Doctor Drivel wrote:

I already gave you an example.
If you look at the (externally verified and tested) specs of many modern boilers, you will note they will run at about 92%+ efficiency into a conventional radiator setup with room stat interlock and TMVs on the non room stat rads. (SEDBUK values typically adjust this down to 90% taking into account seasonal influences)
Note that this is a real efficiency figure calculated using the gross energy content of the gas - none of your "make believe 106% no use to man nor beast" style efficiencies. So any amount of extra complexity you decide to glue between your boiler and radiators, is not going to be able to raise the efficiency by more than 5% at best.
Back in the days of high water content fixed output boilers with dumb controls, the store may have made a notable difference in efficiency, and been well worth having on fuel consumption grounds alone. That is no longer the case.
So by all means use a store if it gets you other facilities that you desire, just don't be mislead into thinking it will save you any significant money
--
Cheers,

John.

/=================================================================\
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Frank Here again,
Most parts seem easy enough to get hold of but there are two items I've little experience of.
Flow switch and blending valve.
Any recommendations of makes that have been found reliable and good value by others?
Many thanks,
Frank
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
snipped-for-privacy@hotmail.co.uk wrote:

http://cpc.farnell.com/jsp/search/browse.jsp?NA1+500001+1002819&Ntk=gensearch_003&Ntt=flow+switch&Ntx (the reed switch versions ought to be very reliable as long as you make sure you don't overload the contacts)

Screwfix and BES both have blending valves. Can't tell you which is better though.
--
Cheers,

John.

/=================================================================\
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Frank again,
Thanks for all that.
Should manage a proper schematic and costing of my proposed system in the next day or two and then bound to have a few more questions. Thanks again for all the above information.
Frank
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Here is how to do a DHW only heat bank and the parts...
Read http://www.heatweb.com for an explanation of how heat banks work.
1. Fit a Surrey type of flange in the top tapping of cylinder. 1" if you can.
2. The plate heat exchanger connects to the Surrey flange port that is immersed in the cylinder water. Drill a few holes in the protruding tube that goes into the water to ensure heat is extracted from cylinders dome, not being pumped to the bottom of the cylinder. The protruding tube has a plate over the end to stop the water heat right to the bottom of the cylinder.
3. The boiler flow is taken from the other connection of the Surrey flange on the top of the cylinder. The return into the old cold feed tapping.
4. From the Surrey to the plate and then to the pump then to a spring loaded check valve and back into the bottom cylinder port. Make a diffuser by inserting 22mm pipe into the bottom cylinder port and drilling holes in and stopping up the end with an internal pipe stop (available from BES). File down the inside of a brass compression fitting that screws to the cylinder port, removing the pipe stop so the pipe can go straight through. This will spread the returning water mainly down, so it will not upset stratification in the cylinder.
5. Two cylinder stats can be used to give a long efficient boiler recovery burn. One stat about half way up and the other about 25% of the way up the cylinder. Set bottom say to 70-80C, set top say to 60-65C. The stats must be latched in with a relay.
6. The cold mains direct from the cold mains stoptap with no tee offs. Take into the flow switch then into the bottom connection of the plate heat exchanger and then to the DHW blending valve.
7. Have thermostatic shower mixers and take the hot supply for these directly off the plate heat exchanger "before the TMV (blending valve). No need to run DHW through two thermostatic mixers.
8. Install a phosphor de-scaler, or other de-scaler, on the incoming mains pipe.
9. Install isolation valves on heavy usage appliances such as the washing machine, and throttle back so it will not rob showers and baths of hot water.
10. Have the F&E tank top up at the bottom of the cylinder and vent at the top. You may want to vent from the boiler flow pipe.
11. Fill with inhibitor - about 1% of total system volume. An average system is approx 100 litres, so a system has one 1 litre can. If say 150 litre cylinder then two cans for the cylinder alone, which is three.
12. Fit a Magnaclean filter on the rads return pipe to the boiler.
The performance is brilliant and you will be delighted with the mains fed showers and no vibrating power shower pump noise. High pressure mixers can be on all appliances.
Gledhill will supply a Plate Heat X. The model for the 145 litre Systemate will do. If you can get another cheaper source then try them. A 100kW plate heat exchanger is needed
<http://www.bes.co.uk or Screwfix will supply most of the fittings. They don't do the plate heat exchangers.
Farnell will supply the flow switch <http://www.farnell.co.uk Farnell number: 1006771 with 22mm compression joints.
Flow Switch, makers site: The FS06 http://www.gentechsensors.com/productTemplate.asp?ProdId 3 This flow switch is about the best - very good.
If the boiler requires to be in a sealed system then have a cylinder with a quick recovery coil, the boiler heats this ASAP. Most boilers can be fitted to an open vented system. Best have open vented.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

The boiler flow/return blending valve? Reliance 28mm. I think onepost gives the model number.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

In short, none at all.

Once again no figures given. You must stop making things up.
If making a heat bank it is rather foolish not to take the CH off the store as it gives a great CH buffer and the befits have been explained in other posts. It is clear you can't see this, so please be quiet as a person here wants sound advice, not the ramblings of an amateur whose only experience is fitting a combi.
As to the efficiencies of these boilers that directly heat the rads. The system is balanced properly and by-pass valve set correctly (few are set correctly). At the weekend I was in a friends house - a big house. He said the system warms up evenly enough around the house then one side of the house is hotter than the other as the rads on one side are hotter.
I looked and found that the by-pass valve opened too early (all too common) and much of the flow went back to the boiler. The flow which never went to the rads on one side of the house. This reduced the condensing efficiency of the boiler and efficiency went right down. I adjusted the by-pass and all was well. With many boilers the by-pass has to open early as they require a minimum flow through the boiler which may be quite high.
Take SEDBUK with a pinch of salt - a guide only. Efficiencies can be bettered by engineering the system.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Doctor Drivel wrote:

The sums are quite easy to do. Even for you.

Well if you can explain how you can pay for all this out of a maximum of 5% efficiency gain then be my guest.

I can't see it because it is wrong. Alas you can't see it as it is too firmly entrenched in your mind along with various other old wife's tales.

Woa there boy, you seem to have a bit of a fixation on bypass valves. Are these like plastic plumbing were you claim the whole system does not work properly based on your hacksaw escapades?
With room stat controlled zones, that have rad without a TMV there is no need for a bypass valve within any of the zones. The only time you may need a bypass outside of the zones is to allow pump overrun (which occurs when the burner is not firing and hence loses no efficiency).
If you are paranoid about your ability to set this correctly, then place your bypass on a three way diversion valve such that the flow path only exists where there is no call for heat from any zone.

They let you out at weekends do they?

Agreed, but not by enough to make all the titting about cost effective.
--
Cheers,

John.

/=================================================================\
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

"Big House" being a slang term (principally American I believe) for prison........
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Matt, have you been a big house?
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Frank here again.
Glad to sat Gledhill very co-operative. GT017 PHE for 74 plus vat and carriage.
The flow switch looks fine too.
I was wondering about a compromise system. Please tell me what you think.
What led me to thinking about heat banks in the first place was the slow flow rate of DHW from 28-30kw combis and the desire to get a long life out of a boiler by using a HB for the CH.
Instead of HB for both DHW and CH I wonder if a reasonable alternative might be to slightly preheat the incoming mains water (7C at the moment) to say 20-25 degrees by running it through a PHE connected to a suitable part of the CH heatbank cylinder and then putting it through a combi.
What would the result be of putting this through a combi rated to give, lets say 12lts per minute at a rise of 35C if we expected it only to give a rise of 25 or 30 degrees.
Would this be a good way of getting 15ltrs/min plus of water at 50-55C out of a modest sized Combi?
Or one could take the whole 35C rise at slower rate and mix it down to a safer temp with a blender.
When the CH is off the incoming mains water is warmer. At the moment the flow rate from anything but a really big combi is going to be little more than a dribble. Anything 13ltrs/min and up of 50 - 55C water is fine for me . Mixes down to about 44 for a nice shower and hot enough to give a hot shot into a cooling bath to re-invigourate it.
We don't use much DHW but it would be good to have decent delivery when we do. I know the full HB thing will do that but this is a kind of Lite version.
Just wondering what the drawbacks of this idea are and how it might by improved or why it should be discarded.
Thanks again,
Frank
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
snipped-for-privacy@hotmail.co.uk wrote:

You can, with provisos. You would need to check the specs on the combi carefully to see if it has a maximum input water temperature - some don't like hot water up em.
You might be able to get enough preheating without a PHE - just by using a indirect cylinder and running the cold feed through the coil. A bog standard indirect cylinder may add 5kW that way - a fast recovery could add 20+.
Having said that, you are throwing away the best advantage of the heatbank - i.e. the ability to get decent flow rates of mains pressure water.

Well take the given spec and convert that to energy terms:
12 x 4200 x 35 = 1.764MJ / min
So, lets say you want water at 40, and the incoming main is preheated to 20:
1.764x10^3 New flow rate = ----------------- 4200 x (40 - 20)
= 21 lpm of 40 degree water.

Not especially unless you have the PHE and heatbank do most of the heavy lifting. In which case why bother with the combi.
(its a workable way of making use of low grade heat from other sources like solar thermal etc)

Or just take the preheated water into the cold side of a blending valve and the combi output into the hot.

So you need about 45.5kW of heating power available to archive this in the winter.

If you want the lite version just leave the rads off the HB and use it just for HW.

<cue dribble's two combis suggestion>
;-)
--
Cheers,

John.

/=================================================================\
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Frank here again.

Good price. The Swep is great plate Heat exchanger for DHW as it is long and thin, rather than short and fat.

What is the point of this when the Heat bank can deliver high flowrates all by itself and uses a cheaper simpler boiler that will not cycle? You will gain nothing.

Most smaller combis deliver 10 to 12 litres/min. Middle range 13 to 16, top end 15 litres plus. There are the odd tiny 9 litres/min jobs still about, however combi performance has increased dramatically in the past 5 years, to the point they must be the first consideration in the average British home. They are highly cost effective, even the top end quality models.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Thank you very much for those comments.
Of course combis don't do vented as far as I know for the CH so if I used a HB off a combi for the CH presumably it would need to be heated via indirect coil or another PHE. Is that correct?
Thanks again,
Frank.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Frank, I think you mean a CH buffer heated via the combi and use the combi for DHW only. Yes, you would need a fast recovery indirect cylinder or a pump and plate heat exchanger to heat the CH buffer cylinder.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

If using a combi and a CH buffer, then the cylinder size must be the total system volume plus 25%. This means in the morning a full cylinder of hot water is waiting to be dumped into the rads giving instant CH heat up. If the combi is used for DHW the 25% extra will buffer the heating untill the combi reverts to re-heating the cylidner.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Thanks for that.
I can't find any ready reckoner for radiator volume. Without doing a drain down at this stage. If we take an average radiator of 600x1000 double convector multiply by 13 and add the volume in the combi and a bit for pipe work what sort of figure will I end up with?
Now they really tricky bit. Which boiler?
Given that I want this thing to last for as long as possible I suppose the best thing is to be prepared to pay a bit of a premium to get a make with a good track record, decent reputation for spares supply and ease of service and repair.
Boderus looks a possible or should I avoid the non SS heat exchanger?
Any thoughts?
Thanks again,
Frank Particular makes to avoid?
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

The average modern system is 80 to 100 litres

If heating a heat bank "directly" then I would go for SS - and use a Glow Worm HXi or Vaillant equivalent open vented boiler. If indirectly, I then any open vented, SS or alum'. If having CH off the cylinder then have a Magnaclean filter on the CH return to the cylinder.
The Buderus 600 range is v good. Buderus is owned by Bosch and Worcester-Bosch service people attend, so no problems there. Buderus is a large outfit on the Continent, much larger than Worcester. Eventually the name Bosch may replace Worcester and Buderus.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Thanks for the info.
I'm attracted by Buderus because they look well made and as if id would be straightforward to replace components. S you say, a big outfit so parts should be okay to fnd at reasonable prices. For instance I think I read somewhere that the HX was about 125 and came out on releasing some screw-clips. You mentioned the 600 range but assume your comments go for the 500 range as well.
On another tack: I've fitted half a dozen boilers and CH systems in the last decade to my own properties. I've done everything myself and got a chap to certify the gas.
Never had any problems (Vokera mostly) but have always assumed that because I'm not Corgi somehow my workmanship would magically be deemed defective and no warranty honoured.
Am I right in continuing to assume this or do you have a cunning work- round?
If you've time:
I've never had reason to use blending valves before so don't know what to expect. One possible (ironic) problem with my proposed system for pre-heating the cold (often 6-8C) mains water going to the combi - to, say, 20C - is that it might easily heat much higher. Are blending valves reliable enough to set one down stream of the PHE on the mains supply to the boiler to mix in more cold and always send the water to the combi @ 20C +/- a degree or two?
Not sure what it would do to the combi long term to send it anything much above what it might have to cope with on a hot day in Spain for instance - say, 25C or a bit more. My expectation is that the combi won't like just topping the heat up say 15 degrees (If it comes in from the PHE at 35C) without waste or perhaps damage.
If it won't mind then all well and good. Very flexible system.
Comments much appreciated as usual.
Thanks again,
Frank
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Thanks for the info.
I'm attracted by Buderus because they look well made and as if id would be straightforward to replace components. S you say, a big outfit so parts should be okay to fnd at reasonable prices. For instance I think I read somewhere that the HX was about 125 and came out on releasing some screw-clips. You mentioned the 600 range but assume your comments go for the 500 range as well. <<<
Yep a clip in Heat exchanger. Brilliant. The 600 range is better. I think they do an open vent model;. Check.

On another tack: I've fitted half a dozen boilers and CH systems in the last decade to my own properties. I've done everything myself and got a chap to certify the gas.
Never had any problems (Vokera mostly) but have always assumed that because I'm not Corgi somehow my workmanship would magically be deemed defective and no warranty honoured.
Am I right in continuing to assume this or do you have a cunning work- round? <<<<
It is legal to DIY. The makers need to honour the guarantee, as it is legal if fitted properly. A way around is fit it and get a landlords certificate.

I've never had reason to use blending valves before so don't know what to expect. One possible (ironic) problem with my proposed system for pre-heating the cold (often 6-8C) mains water going to the combi - to, say, 20C - is that it might easily heat much higher. Are blending valves reliable enough to set one down stream of the PHE on the mains supply to the boiler to mix in more cold and always send the water to the combi @ 20C +/- a degree or two? <<<<<
Should be fine. But I can't see the reason to pre-heat when the heat bank doing DHW will do it far better than a combi. By pre-heating you are not getting anything for nothing, as you still have to pay for the heat that pre-heats.

Not sure what it would do to the combi long term to send it anything much above what it might have to cope with on a hot day in Spain for instance - say, 25C or a bit more. My expectation is that the combi won't like just topping the heat up say 15 degrees (If it comes in from the PHE at 35C) without waste or perhaps damage. <<<<
Some combis can accept pre-heated water at 60C and above.