Just replaced an ancient 30KW Kingfisher II floor-standing lump with a shiny new GlowWorm HXI 30KW condensor (credit due to IMM believe it or not for
The house is a large, Edwardian detached job with four big bedrooms. Before replacing the boiler I did an approx size of all the rads and came up with 27KW needed if you allow ~3.3KW for the HW cylinder, and therefore went for a 30KW boiler. I also had the pump and S-Plan control valves replaced as they were rather old, and took the oppurtuinity to put the conservatory on a separate zone. The new pump is an Alpha 15/60 (currently set to constant head setting as there is a bypass).
The conservatory has two 3.3KW Double-panel convectors, and a 600W single-panel convector. There is also 500W single-panel convector in the bog adjacent to the conservatory, which will eventually be moved back to the main rad zone (couldn't move it without ripping floor up so it will have to wait a while).
One thing I've found is that it seems impossible to get a 20 degree C drop across the conservatory rads when only that zone is calling for heat. If you shut down the lockshields the boiler seems to get insufficient flow, heats up really quickly in a couple of mins then shuts down. Opening up the lockshields fully to increase flow seems to suit the boiler more, and you do seem to get a bit more of a temperature drop across the two big rads (approx 10 degrees). Closing down the smaller rads doesn't really seem to acheive much as the flow across the boiler drops and the temperature drop across the big rads actually drops to virtually nothing, without actually increasing the temp drop on the smaller rads.
One advantage of the low temp drop in this zone is the conservatory heats up pretty quickly; I would guess the downside is less efficiency in the boiler due to the high return temperature. Once the circuit has heated up the boiler cuts out at about 70 degrees, drops to about 60 degrees then cuts in again for a couple of mins or so.
Can you confirm this behaviour is to be expected? Any comments/observations?
TIA,
MH