Thanks to John's input I can now find the diagram I drew.

formatting link
The argument was about if the RCDs would trip in a normally functioning circuit.

Add a high resistance on one of the lines and there will be a trip.

I did a circuit simulation model at the time:

formatting link
That took into account the likely circuit lengths and some estimated loads, so that one could probe the current imbalances. Even with a 1m of extra cable and a 12.5A of load spread over the circuits, the setup just about stays sufficiently balanced to not trip:

formatting link
(Note I inverted one curve so it does not obscure the other)

Firstly that's unlikely in practice, and very unlikely for them to run for long.

The cable would run hot, but not hot enough to be a hazard.

15A BS1361 fuses trip in around 20 seconds at 30A, so it probably would. The user wouldn't notice until the other fuse tripped another 20s or so later. Some users might then fit 30A fuse wire or a suitable nail, enabling the thing to run indefinitely. It would.

NT

They might - but that is a bit optimistic - 5 mins sound more likely.

(and in a CU of that era a BS3036 rewireable would be more likely than a cartridge fuse I would have thought)

Yes. The open wire fuse links used in 1930s fuseboxes would have been the most common in the 40s - were they BS3036 compliant?

Ah - if BS 1361/2 came about in '47, 3036 was presumably much later.

Anyway, yes it would blow eventually, but the scenario would not be common & was still safe.

NT

Our House is late 40s Semi (ex local authority) and probably rewired 60s / 70s. We have a lot of circuits compared with most, and most sockets only have one T&E. Most crcuits cover a some or more sockets upstairs and downstairs. I decided as I wasn't sure of the topology of most of the circuits to have them fitted with 20A MCBs rather than 30A when we had a new CU. We've only tripped once tripped a circuit by pulling too much consecutively, and we just moved the cement mixer onto a different circuit for the day. I did do a continuity test in the CU on one of the suspect circuits the other day and it does appear to be some some sort of ring (at least in parts (but I realise this is simple test is no guarantee of anything). I found out the hard (amd painful) way that the circuit previously labelled upstairs Power wasn't! I now also test to make sure things are dead before I stick my screwdriver in!