3 phase cable question

The 3 phase cable I have that's still connected up to this rather large lat he I bought has some unfamiliar colours making it up. There's a braided shi eld round the outside which I assume is for grounding purposes. Then four e qual thickness conductors inside: brown, grey, black and blue. I have to so mehow marry these up to the inverter box where the appropriate terminals ar e marked 'U','V' & 'W' which is neither helpful nor meaningful to me. Can a nyone clue me up here? I'm starting to develop a complex over all the flash es and bangs I've experienced recently. Don't want to end up a nervous wrec k. Thanks.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
snipped-for-privacy@virgin.net wrote:

I do not think there is as lot to worry about. The brown, black and grey are the phase wires (U,V &W) the blue is probably used an earth.
You need to look inside the lathe to confirm this.
--
Adam



Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
"ARW" wrote in message wrote:

Surely Adam the Blue is more likely to be Neutral, with the CPC/Earth conductor being the braid that he refers to ? Many machine tools bring in a neutral to allow 240v contactors, lights and the like.
AWEM
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Andrew Mawson wrote:

I did ask the OP to confirm this.
I have seen many more 3 phase only machines than 3 phase and neutral machines.
--
Adam



Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
ARW wrote:

CY cable that I've used is either 4 core - 3 phases + earth + braid or 5 core 3 phases, neutral earth plus braid.
The theory is the the earth must be used for earth continuity to the motor but the braid should only be connected at the inverter end so it can act as a true RF shield to minimise the crap from the inverter interfering with other equipment. If any current passes down the braid (however small) the braid itself turns into an antenna and radiates the RF energy.
Bob
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 04/08/2013 16:44, ARW wrote:

I agree it's best for the OP to confirm, but aren't the harmonised colours for the phases: Brown, Black and Grey, with Blue for Neutral?
The Armour/braid being the CPC?
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Fredxx wrote:

Yes, that is correct.
However what I am saying is that the number of times I have seen 4 core SWA used on a 3 phase supply with the 4th core used as a cpc and not as a neutral far outweighs the number of times I have seen the 4th core used as a neutral.
--
Adam



Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 04/08/2013 18:02, ARW wrote:

I bow to your knowledge. However the core, if non green/yellow, should have a sleeve indicating CPC.
Of course should easy to check on the machine.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 04/08/2013 15:20, snipped-for-privacy@virgin.net wrote:

Those are the "normal" 3ph colours now:
http://wiki.diyfaq.org.uk/index.php?title bles#Conductor_Colours_and_Harmonisation
would have been red/blue/yellow and black in the past.

Sounds like the lathe has connection for the three phases, but no neutral.
--
Cheers,

John.
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sunday, 4 August 2013 16:41:28 UTC+2, John Rumm wrote:

Yeah, I need to change the lathe motor box from star to delta and IIRC, delta doesn't use the neutral.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 04/08/2013 15:44, snipped-for-privacy@virgin.net wrote:

Don't think you *have* to use it in star config either.
--
Cheers,

John.
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
John Rumm wrote:

Most Star -Delta starters have no Magnolia/Swizterland.
--
Adam



Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

It depends if it is a dual voltage motor.
If it is dual voltage it will be delta for 220 volt (Phase/phase) and star for 400 volts (phase /phase). There is not much requirement for this sort of thing now, as we and the EU are similar voltages.
The neutrel is not needed for the motor iself but may be needed for ancilliaries. If it is a dual voltage motor & starter, the starter coil will be the low voltage so you would need a neutral if is were run in high voltage configuration.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
So basically you're saying I can just connect *any* phase wire up to the u, v or w and the order doesn't matter? I mean I don't need to specifically connect a certain colour to a certain lettered connector?
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
snipped-for-privacy@virgin.net wrote:

Depends if direction matters, if it spins the wrong way swap any two wires, if your 3ph converter can reverse direction, even easier.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote in message

So long as you don't mind which way the motors revolve then yes. However if you are running off a static phase converter you need to ensure that your contactor coils are driven by a phase other than the generated phase.
AWEM
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sun, 04 Aug 2013 11:30:23 -0700, orion.osiris wrote:

First. Look in the terminal box at the lathe end of the cable. What are the terminal markings in there, and which cable colours are connected to them?
Usually: Phase 1 is L1 / Red / U / R / Brown Phase 2 is L2 / Yellow or white / V / S / Black Phase 3 is L3 / Blue / W / T / Grey Neutral is N / Black / N / N / Blue
Although variations exist. :)
If a neutral connection is used for the lathe then you will need to source it from the inverter somehow (or make some other arrangement) as it will be used for the control circuit. You can't omit it. Even if the motor is star connected the neutral may not be connected to the star point of the winding (that is very unusual).
As others have said, if you reverse any 2 phases of a 3-phase motor it will run in reverse. So no, you don't have to be specific in colours & markings. If the lathe was properly installed then it will probably have been connected as one of the above sequences.
Unless the lathe was originally fed from an inverter or speed controller it will almost certainly be using the braid as protective earth. The blue (usually neutral for brown/black/grey/blue cable) wire may or may not be connected. You MUST check. You also MUST check whether the braid is used as protective earth and make sure that it is terminated correctly at both ends if it is.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sunday, 4 August 2013 21:40:56 UTC+2, mick wrote:

e
THanks, Mick. I was wondering if I should make the addition of an earth spi ke within the workshop itself to be on the safe side, since there is a run of about 10 meters from the lathe back to the existing earth in the house's distribution board. Any thoughts on the advisability of that and if so, ar e those cheaper, copper plated spikes good enuff for the job? Come to think of it, I've got some 15mm copper pipe laying around that woul d probably do just as well as a spike...
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 04/08/2013 20:40, mick wrote: ...

Most three phase machines I worked with came with three red wires and, sometimes, one black.
...

I think there is some natural law that they will always run the wrong way when you first connect them, ;-)
Colin Bignell
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Mon, 05 Aug 2013 09:09:11 +0100

I know there is some natural law that they will always run the wrong way when you first connect them. Especially if it matters.
--
Davey.