Temp rise on a furnace

Dec 09, 2005 6 Replies

What should the temp rise be on a Ng Lennox Dimension 93% 2 stage furnace from return to just at the AC coil with new filter, clean squirrel cage and all ducts open and on low fire of a 2 stage. Mine is



67 in 137 out a 70f rise. Isn`t that to high indicating it is oversized for the ductwork. I thought 50- 60 was inline. It is a bit oversized and I am looking at less Btus on a replacement. The Lennox supposedly was sized correctly as return and supplies were added.

The temp rise information should be listed in/on the furnace somewhere. Greg

This is Turtle.

Like Grego said the Temp. Rise should be on the furnace.

Also 70 degree temperature rise is very much on the top end of the scale . i would like a 50 Temp. Rise or so for me but other opinions may very.

TURTLE

It says 40-70 on the door but it actualy may be 72 or so depending on the return, I would like it lower, slower more even heat is better.

BUT check the CO reading while and after you do it. Bubba

This is Turtle.

E-mail me at this e-mail addy and talk about this.

TURTLE