"sweaty" cold water supply pipe

Pawlowski is, again, correct. The water on the pipe surface comes from the air. Thus, a well sealed insulation jacket will not allow moisture to fomr on the pipe. TB

Reply to
tbasc
Loading thread data ...

The humid weather is resulting in "sweaty" cold water pipes in our basement.

I have read the suggestion to insulate the pipes just like with hot water pipes. However, I am concerned that while this may reduce the sweating, there still will be some condensation, but now the condensation will be trapped against the pipe.

Should I be worrying about this? If so, what should I do to minimize the potential for mildew and mold in this trapped moisture?

Second, I find that the condensation only occurs on the first few feet of pipe in from the grounde. Is it possible that conduction causes the water in the first few feet of pipe to stay cold all the time leading to heavy condensation while beyond that the water for the most part has warmed up (except when the water is actively running) so that there is much less active condensation?

Reply to
blueman

Not in any measurable way. I assume you are meaning the heat the cold water picks up in the line while waiting for some draw. It is minimum. Even a few degrees rise in a pipe run of 40 ft doesn't add up to a sneeze.

Harry K

Reply to
Harry K

And it may increase the water heating bill.

Nick

Reply to
nicksanspam

Well I heard this insulation was primarily for the cold water pipe, not the hot water pipe.

Reply to
CL (dnoyeB) Gilbert

Reply to
ronm

Insulated properly there will be no condensation to trap.

No

Yes, but if you run a lot of water it will move along the line as it cools down. Depends on your particular use, temperatures, humidity, etc.

Reply to
Edwin Pawlowski

I disagree.

Nick

Reply to
nicksanspam

Care to expound on why? The amount of water contained in a 3/4" pipe say 20 ft long is not very much. About 5 cu in/ft (after heavy rounding off) unless my long ago math is out of whack. Water in the cold intake pipe also doesn't usually sit there long enough to pick up much ambient heat.

Harry K

Reply to
Harry K

In alt.home.repair on Fri, 22 Jul 2005 01:32:04 GMT blueman posted:

If you put it on when the pipe is dry, almost anything will keep the humid air from touching the pipe after that. No humid air, no condensation. If part of the pipe is dry, wipe it off with a towel first.

Personally, I doubt mold or anything will grow on a little dampness on a copper pipe, but this should prevent any.

If youre still not sure, open part up after 6 months and check it out. But you have to look right away. The moment you open it up, humid air might start to condense on the pipe.

Meirman

-- If emailing, please let me know whether or not you are posting the same letter. Change domain to erols.com, if necessary.

Reply to
meirman

How well sealed is "well sealed"? Is it enough to buy the Home Chepot middle-grade stuff that comes with taped edges that you push together?

My sense is that the adhesive tape is enough to keep it on the pipe but not enough to make a real seal. Is there stuff that is better to buy or should I cover the seam with something like duct tape?

Thanks

Reply to
blueman

As long as it holds, yes.

If you have concerns wrap some tape every 12" or so. Duct tape or electrical tape will work. Mine has b een holding for about 20 years, but that does not mean what you buy today will.

Reply to
Edwin Pawlowski

I get 0.19 lb/ft, so 20' would hold 3.8 pounds.

That depends on how fast the heat flows... 20' of 3/4" pipe has about

4 ft^2 of surface. With still air and no condensation, it might have a thermal conductance G = 1.5x4 = 6 Btu/h-F, so the time constant RC = C/G = 1 hour, ie a 3.8 lb slug of water would warm from 50 to about 57 F (1/e th of the way to 70) in 1 hour in a 70 F room.

Recall Charlie Wing's TV show in which he built a tempering tank in a basement, a 20' length of 6" PVC pipe tucked up under the rafters? Well pressure tanks can warm water too.

And condensation might raise G to 1000, so flowing water can warm to the dew point in real time as it moves along the pipe. As I recall, the OP described "a few feet" of condensation near the pipe entrance. I don't recall that the entire pipe had condensation when water was flowing. If not, the pipe warmed flowing cold water to the dew point.

With no cold water pipe insulation, we have 4 potential savings in water heating: the small warm slug of still water before flow begins, the large flowing gain to the dew point, the small flowing gain from the dew point to room air, and the effect of having warmer cold water at a sink or a shower, which can allow using less hot water in a mix to achieve a certain temperature. The latter may come from a lot more cold water pipe in the house, unrelated to the pipe that goes into the water heater. Harvard physicist William Shurcliff has written about these savings.

Nick

Reply to
nicksanspam

Good discussion of the -theorectical- savings. Just how much savings dollar wise do you think it comes down to in practical life? You won't see it on your power bill. Most of your warming is coming from having water stand still in the pipe for long periods. That doesn't happen in an active house. The tempering tank could have some small advantage. I wonder about the well tank (basically same as tempering tank). Think I will test my incoming water temp as opposed to the tank out temp after sitting all night.

Harry K

Harry K

Reply to
Harry K

The biggest might be from condensation on active pipes. If we spend (say) 50K Btu/day warming 1000 pounds of 60 F well water to 110 in a water heater, and insulating the cold water pipes lowers the 60 to 50, we have to spend 1000(110-50) = 60K Btu/day, ie 20% more, eg

10K/3412 = 2.93 kWh/day or 1070 kWh/year, eg $107 at 10 cents/kWh.

I disagree.

Nick

Reply to
nicksanspam

Nick, according to my calculations, there 5.3 cubic inches of water in a foot of pipe, that is equal to .0229 gallons. At 8.33 pounds per gallon, that is .191 pounds of water per foot of pipe. Assume 10 feet of 3/4" pipe that sweats that is 1.91 pounds of water. To warm that from 40 degrees incoming temperature to 70 degrees, at 1 BTU times 30 degrees times 1.91 pounds = 57.3 BTUs. At 8 cents per therm (100,000 BTUs) the cost savings gained by leaving the insulation off is.0045 cents every time you have to warm the water in the pipe. If the people in the house use the water 40 times each day, the total savings per day is .183 cents per day. Times 30 days per month is 5.49 cents (per month). Nick, that is not enough to worry about. Even if you allow for inefficiencies, it is still less than 10 cents per month. Nick, that is not worth the time I just spent on it. Or do I need to write that into a BASIC program to get the point across to you?

Stretch

Reply to
Stretch

Thanks. My last physics was in HS 50 years ago. I was beginning to think I'd have to do some real research to make the point. I was running off of common sense and practical application. There are a lot of things out there that look good in theory but don't work out in practical application. Of course Nick can argue that any savings is worth it but to me dripping pipes trumps that one.

Harry K

Reply to
Harry K

Common sense and practical application don't seem to apply with Nick. His math may be correct, but his assumptions often go awry. He has some interesting points, but if he had customers that had to live with his assumptions, he would soon go broke.

Stretch

Reply to
Stretch

We all seem to agree on that.

And that...

Yes...

You can buy oil for 8 cents a gallon? :-)

I make this 0.115 cents at $2/gallon.

And 4.6 cents/day.

And $1.37/month.

You might check your math for glaring errors and read more carefully. I said this savings is small compared to warming an active pipe with condensation, which might save 20% on a water heating bill.

And you might modify your arrogant attitude and be more polite. Apologizing is optional.

Nick

Reply to
nicksanspam

Nick, You assumed oil heating the water, I assumed gas. Although my gas rates may be off a bit, he did not say what he is heating the water with. Also the calculations assume the water is completely warmed to room temperature each time, which is not likely. There are a lot of suppositions involved here, most of them are overblown. The daily savings are likely exagerated to the extreme. Also, pipe insulation slows down the rate of heat transfer and increases the area of surface area exposed to ambient conditions. It does not stop heat transfer. As well, as the temperature in the pipe approaches room temperature of the basement, heat transfer slows down, so it will take too long for all this heat transfer to tane place. Certainly each complete temperature change is not likely to take place in in 36 minutes. So an apology is not likely. Still not enough cost to worry about.