Rooftop commerical Lennox AC compressor keeps tripping on the internal breaker

Our office has a rooftop Lennox THA090 AC unit. It comes with 2 compressors. Almost everyday we have to go to the roof to restart the compressors because they often will trigger an internal circuit breaker that protects the compressors. According to the PCB board that is next to the compressors, when it trips the breaker, it says it is because of a High Pressure fault (LED1 will flash, and LED2 will be ON solid). What would cause this fault on a daily basis? Thanks for any tips!

Here are some pictures of the AC unit:

formatting link

Reply to
dchou4u
Loading thread data ...

1) use a clamp on Ammeter to verify that the current is indeed high 2) use a pressure gauge to check the high side pressure to see if is indeed high 3) check that the condenser coils air flow is not blocked or dirty and that the condenser fans are running correctly

Mark

Reply to
Mark

Are there bubbles in the sight glass when the units are up and running after 5 minutes or so? Another problem could be dirty condenser coils. A low charge or dirty coils could cause the compressors to overheat. ?

TDD

Reply to
The Daring Dufas

might be a bad breaker, circuit breakers are designed to get more sensitive at end of life......

Reply to
bob haller

The high limit switch is designed to protect the compressor from burning out, when the amperage or discharge pressure is too high. When it trips, you're supposed to to call a HVAC service company to come out and repair the unit. If you press the reset and do it all over again (the next day), eventually you will have a compressor burn out. And the resulting repair will be several times more expensive than having the unit serviced. Talk to the people in the stores near you, see who they use, and who does a good job. Your cheap approach is going to cost you mega bucks before too long.

Christopher A. Young Learn more about Jesus

formatting link
.

Here are some pictures of the AC unit:

formatting link

Reply to
Stormin Mormon

They totally need to call a service company, and have it repaired. Before the compre$$or burns out. That way, they can have the unit serviced for a couple undred, instead of compre$$or replaced for $$everal thou$$and dollar$$.

Christopher A. Young Learn more about Jesus

formatting link
.

1) use a clamp on Ammeter to verify that the current is indeed high

2) use a pressure gauge to check the high side pressure to see if is indeed high

3) check that the condenser coils air flow is not blocked or dirty and that the condenser fans are running correctly

Mark

Reply to
Stormin Mormon

if the guy didn't already know and had to ask what to do on a newsgroup, then you are probably right.

Mark

Reply to
Mark

Thank you all for the tips. We will call a service tech to come and check it out.. :)

Reply to
dchou4u