I'm having a problem with an electrical circuit in my home. The power goes out only in one section and hours to days later it may come on again for no apparent reason and then off again. I was able to isolate the breaker when power resumed. It's a double 30 amp breaker and it doesn't trip off but still no power. It only controls doorbell and an outlet in the garage. I've checked for loose wires but haven't found anything. I've flipped the breaker on and off and still nothing. I think at one time this was for an electric water heater but have switched to gas over 20 years ago. Could the breaker be bad? I would appreciate any suggestions.

thanks in advance.

Phild

Reply to
Phil
Loading thread data ...

Phil,

Do you own a voltmeter? When the power goes off in that section turn off the main breaker and test continuity across the suspect breaker. It may be bad. A water heater circuit should not have any other connections on it so I'm surprised that this breaker affects anything in your house. If someone took out the water heater and then spliced into the wire and used it to create new circuits the splices may have been done badly. These splices should be in a junction box near the old heater. With the power off check and redo these splices. If the splices are wire nuts without a junction box put them in a junction box.

Dave M.

Reply to
David Martel

Could it be there is a subpanel in your house fed by that 30 amp breaker?

Reply to
Mikepier

I suspect a GFI somewhere. (note the outlet in the garage). It may be almost anywhere including the kitchen and baths. I would also agree that you may well have a sub panel. It would be unusual for a 30 amp double breaker feeing anything other than a sub panel or a single fixed 240V device like an electric stove or water heater.

Reply to
Joseph Meehan

I'm not sure if anyone has mentioned yet how dangerous this situation is? Something is randomly interrupting the current. That causes heat. fortunately its only a small load. Still, when its interrupted you should take the opportunity to check the continuity of the circuit and see where the break is. Shouldn't be that hard.

Reply to
CL (dnoyeB) Gilbert

I had a similiar problem. Use a voltmeter to check to see if the voltage is gone or if it is just low. My power would fluctuate between

60 and 0 (which made the whole circuit garbage). After checking everything I discovered that there was a problem with a neutral wire (it was had all of the power). I ended up having to find a hidden junction box in the cieling where two circuits connected into one and one section of wire needed to be replaced. After rewiring the junction box and replacing the one wire, everything was fine. My water heater too was connected to everything else. Turns out that it had a direct line - someone just wired in the new one wrong and crossed some circuits or something.
Reply to
jeff

NEVER test continuity before testing voltage, especially when dealing with more than 3 volts.

If the breaker is bad, or even if it is just off (as is recommeded in the first two lines above), you'll be putting 110 volts or more across the continuity tester. Only neon bulbs are designed for that. No voltmeter/multimeter is. Some of them may be protected against that, but many are not, and who knows which are which, and I wouldn't want to rely on the protection anyhow.

Test the * voltage* when the breaker is ON. Test at the screw terminal on the left or right. The center is inaccesible and that's ok.

IF the voltage isn't what the voltage is at other circuit breakers (240, 220, 120, 117, 110, or maybe lower during a brown-out) the CB is bad. Turn off the main CB and only then remove this CB.

When it is all the way out of the box, then you can check it for continuity, but even if it passes, don't forget that this circuit works sometimes and doesn't work all the time. That's what you said. Buy a new CB. They are cheap. If you are like me you can save the old bad one for when the next one fails (which may well never happen.) and you can't get to the store. Mark it "BAD". Or you can cut it open and see what is inside. (Not too much, but there will be pitted contacts most likely.)

Also there is some difference between passing a continuity test with

1.5 or 3 or 9 volts DC and minimal current, and actually working with 110 volts AC. I'm thinking there would not likely be in this case, but bear it in mind. Voltage testing of a A) circuit with voltage present is sometimes more reliable than resistance testing of B) individual parts with voltage off. (This situation is neither A nor B, because turning the CB off doesn't disconnect the CB from the power at one end or from the ground at its other end.)

Remove NOPSAM to email me. Please let me know if you have posted also.

Reply to
mm

An intermittant open will not cause heating. You need current flow, and substantial current at that, in house wiring to produce noticable heat. An intermittant short certainly would cause heating but should also trip the breaker.

It is unusual for a double pole breaker to feed a 110V receptacle but not unheard of. If only one side of the double pole breaker tripped and the breaker were not working perfectly, the other pole switch handle could hold the switch in a position making it look on when it is in fact half tripped. One pole should be able to trip the other but an old breaker might be sticky.

Have you tried toggling each breaker off and on. Did that one feel different the first time you switched it as opposed to subsiquent tries?

There is also a good possibility that the wire connection to the back of the receptacle or a wire nut in the doorbell is open. Inspect the connections to eack of these things. If the receptacle has the wires shoved in the back, replace it with one with side screws

Reply to
PipeDown

When I have had intermittent problems like that, it usually turned out to be a bad connection. Sometimes the romex is daisy chained and connections are made with wire nuts. The connections get flaky and heat builds up, causing the wire to expand. This can either open a connection, which will then close again when the wire cools off or something jiggles it. I had to locate it by finding the outlet that was bad, and tracing the romex in the walls or ceiling back, box by box, and checking the connections. It can occur with wire nuts or on receptacles, or in a light fixture --- almost anywhere along the line.

Andy

Reply to
Andy

And not wise considering " It's a double 30 amp breaker" I don't know many 120V receptacles rated for 30 amps. :-)

Reply to
Joseph Meehan

Breakers have been known to go bad like that. You may want to replace it, or at least switch the wire(s) to another breaker to see if the problem goes away. Don't use a 30 amp replacement breaker though, try a 15 amp.