Ok, now that my furnace was scrubbed and cleaned and a new thermo coupler for the pilot ignition was installed, I got a new filter to install. However, as I pushed the filter into the slot, I accidentally brushed/hit one of the wires on the blower and the flames died out and only the pilot light remained. I replaced the blower lid and the burner door, went upstaris to make coffee, and went downstairs to hear that the furnace was burning full blast . I opened the burner door to look inside, and the flames were burning birghtly, then they died out and only the pilot light was on.

I don't remember this ever happening before. The flames were always burning brightly and never went to pilot status when I had opened the door previously. Now that the burners are cleaned and scrubbed, and all the scale and rust has been vacuumed out of the furnace, is the above normal operating procedure?

Thanks

Reply to
NWM
Loading thread data ...

Yes, that most likely is normal operation. There is usually a door switch that turns the unit off and on. Obviously I can't see it from here, but you can...look for some type of push switch that the door come in contact with around the edges of the cabinet.

Reply to
Brian V

This is Turtle.

Look on the top part of the blower door and you will see a push button switch that will be pushed in when you put the blower door back on and will release the push button switch when you open the door. The switch was problem stuck over the years and the fellow cleaned all the trash out ans a service man will clean and pop the switches to make sure the will pop out when the blower door is removed. This push button switch will kill all the 120 volt power to the furnce when it is released. When it pops out, the burners and all blower motors will stop and only the pilot lite will keep burning.

Now you do know your suppose to turn the furnace off before opening the blower door because you can in some cases pull the flames out of the burner area and out to burn the wires if the blower motor is running with the blower door off while running the burners. This is what the switch is on there for.

TURTLE

Reply to
TURTLE

More like a vertical lid that slides off with great difficulty. With the burner door on and the blower door/lid in, the cycle is 1) pilot light 2) full burn 3)blower on 4) blower off with full burn 5) pilot light. Basing this on sound since everything is closed. I didn't notice any switch where the blower door lid would come int contact with. I wonder if the brand new thermal coupler is responsible for this cycle.

Reply to
NWM

Its called a Thermocouple, and its got nothing to do with your blower door switch now working.

Every gas furnace made in the last 30 years has one...

Reply to
steve

I checked again, still no blower door switch. Must be over 30 years old. Brushing the filter against the wire and the pilot light only coming on was probably a coincidence. The tech had also replaced one other part, no charge. Don't know what it is called, but it is some king of big sliding nut that is connected to a thick silver rod that is next to the pilot knob.

The actual sequence of events is 1)pilot 2)full flames) 3)blower with full flames 4) blower off with full flames 5) pilot light 6) pilot light with blower.......(I guess this is good since there is still enough heat in the furnace to trigger another blast from the blower even though just the pilot light is on. Getting 2 blasts from the blower for the price of one cycle of gas, although the second blast is much quicker in duration.) 7)pilot light without blower. Repeat

When the tech was here and started the burner with the blower door off, full flames came on after he lit the pilot light and turned the knob to on, and the flames continued like that and didn't go back to pilot. Blower worked normally. Maybe it was the thermostat constantly calling for heat....the inside temp was around 55 and the thermostat was set at 70. With all that cleaning, maybe the thermostat now works properly and now that the internal temp now matches the thermostat at

65, it goes through the cycle as described above, and uses much less gas. In the past, always seemed that the burner was constantly on full blast. Thinking out loud.

Also, the thermostat is off by 5-7 degrees, but it's thermometer is accurate. I have to set it at 60 in order to get 65-67 ,etc. I should probably get a new one. An analog, presumably 2 wire, Honeywell is the brand I got. Any recommendations?

Also just noticed that the blower motor area wasn't vacuumed. Slight oversight to a thouroughly excellent job.

Reply to
NWM

Sounds like a pilot tube...but you know...no one can see it from here...and you have yet to give any real information...like..brand of unit, model, serial...cause if you had, not only could we tell how old it was, we could tell you what SHOULD be on it.

That is wrong. And its costing you. IT could be from improper heat rise, caused by improper burn set, it could be from an improperly set fan switch, or a bad fan switch... The second blower run is wrong, and its not a good thing....

I dont know....we bypass the blower door switch while working on units, since there are times you need to have things open to properly check items...like blower fan RPM and such with the tach..

The thermostat is nothing but an on, and off switch...it knows NOTHING about how the furnace is running, or the sequence of operation of the furnace. You keep talking like you have a two stage burn furnace, and I can guarantee IF you do, you have a blower door switch on it.....since they havent been made long..

Is it a T87..the round one? If so, level it. If its not, check level on it. Your furnace guy should have done this as well....

Sounds like he took your money and you feel good about it. How long was he there? 20 minutes? 30? Average time for a gas unit to be properly serviced is over an hour. It takes about 10 to 15 minutes just to check the WC on the manifold and line. Then you have your leak tests and checks, and then the heat exchanger inspection....(and from the sound of your double run on fan, you really needed that..seriously) then there is the spillage check, the CO test, the cleaning, the adjustments, the heat rise check and adjustment, blower cleaning, HE cleaning, thermocouple replacement, thermostat calibration, and level if needed, terminal checks, ductwork checks flue check.....and thats on an older unit...there are still all the roll outs to be checked for operation, proper sequencer operation, door and flue switches, inducer motors on the newer units, gaskets and seals to be checked.......the list go on...

We charge over $175 for that...what did you pay? $35, $50? $100 even?

Sorry to say, sounds like you got what we call a hit and run....if you have a legitimate contractor, he should be willing to return and check your thermostat free of charge....if not...well..you get what you pay for most of the time.... Any furnace company that claims a check can be had for $50 is actually not lying....they check to see if you HAVE a furnace..and thats about it.

Reply to
steve

What is the proper sequence ? I assume from the above that the furnace should be fully burning at all times and I should not see only the pilot light at any point. Is the second blower run dangerous?

First guy I called didn't even clean or change anything. He was pushing hard to install a 5000 dollar furnace. He claimed it would take 5 hours to remove the burners. The second guy took an hour to take out the burners and scrub and clean them and check the limit , replace the thermo couple. Unfortunately, he didn't check the blower. Probably becaue at the time it was working properly , the pilot light did not come on just by itself. The furnace was burning fully.

You have to understand, I am completely new at this so every experience I am learning more and learning more from the responses I get . The second guy was a big improvement over the first. At least the second guy got the furnace working and the auto setting on the limit to work. BUt not good enough according to you. First guy was 140 bucks for pretty much showing up, and the seond guy charged 186 for labor and one part for an hour. Maybe the third time will be the charm. Is there a checklist for things I should ask for? Your industry is full of crooks so it seems.

Thanks

Reply to
NWM

Chrysler Airtemp model number 4212-30

Reply to
NWM

Proper burn..standing pilot furnace:

Thermostat calls for heat Gas valve thermocouple detects pilot flame, (constant, since the thermocouple generates a tiny voltage amount) and opens allowing burners to light, or fire... Heat exchanger warms air around it, causing fan limit switch to start climb towards fan start At around no more than 150F air temp at fan limit, fan switch turns on blower home is heated Thermostat is satisfied, ends call for heat Gas valve shuts Blower runs until fan limit switch cools to shut of temp, set on dial. Unit sits with pilot lit until next call for heat.

Not unless you have a cracked heat exchanger that is allowing the fan limit switch to become overheated.

Five grand for a furnace....damn...I am not charging enough....

The industry IS full of crooks, as is every one. By the same token, Usenet is not always where you will find the right answer to every issue..:)

No, your service was NOT good enough, or else you would not be having what we call a run on condition. While it MIGHT be a simple adjustment to the fan limit, I would be more concerned with the heat rise, and if its too high. If it is, due to your previous techs failure to check it after cleaning the unit, the blower will continue to cycle as it is until the burn is corrected and the heat rise is lowered. hell, if you are in my area, (central NC) Ill come by and check it for you and if its an adjustment, fix it for a hell of a lot less than they did...no service fees.... Educated consumers, help us that are legit, and trying to do the right thing for everyone, run the bad guys out. i dont mind charging what I do...most people agree, they will pay more for competent and correct service, than for half assed hack work that costs more in the long term than in the short.

Good luck there.

Reply to
steve

Holy mother of God...that things still running? Good going...seriously. I worked on many a Pentastar...tanks...absoulute tanks. Make DAMN sure someone runs a CO check on that unit....90% of the replacements we have done on those are due to cracks in the exchangers. They are good units for the age, but like everything else, they will fail over time. Not trying to sell you anything, but in all seriousness, they also are fuel hogs...a new 95% unit will about pay for itself in very short order in savings compared to that one...but 5 grands a bit steep, altho I cant see it from here but I assume its in a location thats not hard to get to.

Reply to
steve

This is Turtle.

I would not be so quick to call a third company out when you have not called the second guy back and explained the problem. If you called me back and said it was still not working properly. I would come back for NOTHING to see about it. Call him back and see what happens .

Now watch out here lumbing the second guy with the crooks out there. I have cleaned a burn and replace the thermocouple and see nothing wrong with it and leave and get called back to a Fan / Limit switch start to acting up . A fan / Limit can work good one minute and when you leave it will start screwing up.

TURTLE

Reply to
TURTLE

"Steve@carolinabreezehvac" wrote in message news:yB2od.192$ snipped-for-privacy@eagle.america.net...

This is Turtle.

I think your lumping in the second guy who worked on it in the crook area when he did what he come to do and not spend another 1 to 6 hours checking the complete system out from one end to the other. The customer called him to come fix it and not give him a complete system check out which would take atleast another 3 hours at $70.00 a hour. $187.00 for the fix and a another $210.00 to check the whole system out. = Just short of $400.00. Just reading here.

TURTLE

Reply to
TURTLE

Ok, I had thought when you stated heat rise, you meant the heat didn't rise up through the flue and ducts. SOunds like you mean the heat has risen too much in the furnace , thus the second blower run when the burner is off as a result of too much heat still inside. The first blower run didn't force enough hot air through the ducts?

Can the heat rise be a problem of the limit switch setting? The tech showed me that the limit was set between 100 and 150 with emergency shut off at 210. However, I just read on the furnace that the switch is supposed to be set at 70 and 100, unless I misread what was labelled.

SO you are saying that the second blower run could correct itself eventually?

Thanks again for all the helpful responses

Reply to
NWM

70 and 100 is too low. 100 and 150 is apparently too high. I would take it to 90 and 140. If that doesn't take care of the double run, I would go to 80 and 140.

The proper setting varies from system to system. Also, its entirely possible that the fan switch just doesn't hold its settings anymore and needs to be replaced.