Looking for help from HVAC experts.

Hi,

I have recently purchased a Honeywell wireless thermostat (YTH6320R1015). Manual is here, page 4 is key:

formatting link

I have split setup: A gas boiler in the basement (2-conductor thermostat wire). My relatively modern Bryant AC unit is in the attic. I therefore have two transformers. (For what it's worth, I've made sure they have the same phase.)

I would like to control both systems with my thermostat. Honeywell tech reps all agree that this must be possible, but give me contradictory instructions. After several exchanges they seem to come to an agreement that I might need a third transformer just to power the unit independently from the transformers in my systems.

Does that make sense or could there be an easier solution!

Many many thanks in advance!

Sam

Reply to
Sam Takoy
Loading thread data ...

Remove the jumper from Rc, Rh and R. Rc for cool transformer. Rh for heat transformer. Then simply jumper off ONE of those to power the stat itself.

-Brian

Reply to
Brian V

Remove the jumper from Rc, Rh and R. Rc for cool transformer. Rh for heat transformer. Then simply jumper off ONE of those to power the stat itself.

-Brian

Reply to
Brian V

formatting link

I don't see an issue. The "EIM" needs power (24 volt). It could be powered by either transformer. Choose one. If you locate the EIM in the attic, power the R and RC and C, from the air handler. Remove the existing jumper, which is between R-RH-RC, from RH, which will be powered from the heating system. The two wires go to RH and W O/B. If you want to install the EIM in the basement, you can power the device from that transformer by removing the RC from the jumper.

Reply to
RBM

formatting link
>

Gug? I thought Tc is R common, Rh is R for humidifier.

Reply to
Tony Hwang

formatting link
>

Hi, I have a Honeywell wireless set up. Like wise needs only one 24V source because it is present all the time. Just hook up control leads from both neating/cooling properly. My unit is about 5 years old never was any trouble other than replacing batteries on the 'stat/xmtr.

Reply to
Tony Hwang

formatting link
>>

** In this case: R-C feed the control, RC is cooling, RH is heating
Reply to
RBM

formatting link
>

**My mistake, you do have to power the unit from the cooling system. C and R, with jumper to RC, powers the unit and the cooling. Remove the jumper from RH. connect the Y and G from your cooling system as well. Then the 2 wires from the heating system just go to RH and W o/b, and it doesn't matter what order these two go in >
Reply to
RBM

Thank you for all the responses.

May I confirm that I understand something correctly? The reason why I CAN'T power the unit via the heating system is because it doesn't provide a hot. The two present conductors are responsible for the relay only.

Thanks

Reply to
Sam Takoy

Exactly, typical heating system series 80, two wire, consists of a hot and a return, but no common.It isn't so much that you can't do it using the heating system's transformer, it's just that finding and accessing the "common" for the 24 volt power supply can be difficult on the heating system, where as on the cooling system it should be clearly defined