My home A/C was turned on yesterday, and we realized that it blows warm air instead of cold. I did a little bit of investigation and also changed the filter.

  • The outside unit fan is running, but the compressor itself seems to be not running. I measured amps going to it, it is about 1.4 amps 220v, consistent with only the fan running.

  • The cold refrigerant line (with thermal insulation) is not actually cold but warm.

  • I just changed a filter. The evaporator coil was not easy to see so I did not look at it.

Would you have any troubleshooting suggestions. The outside unit is relatively new. Thanks

Reply to
Ignoramus18130
Loading thread data ...

If it's fairly new , it may still be under warranty

Reply to
philo

See if main contactor is energizing and check it's contacts to see if they are badly pitted. Beyond that OP knows how to charge the refrigerant?

Reply to
Tony Hwang

Is the compressor going? If not starting cap good? Contactor contacts in good shape? Or need more refrigerant after checking leak.

Reply to
Tony Hwang

The first thing you check is to be sure there's 220v to the relay . Then that the relay closes when you call for cooling - and that 220 is getting out of the motor side of the contactor . Next is the start cap , if the top is bulged it's for sure dead . If not , I'm sure you have a meter that measures capacitance . You might want to disconnect the fan power temporarily to see if the compressor hums when first energized then quits trying . No hum probably means it's dead or not getting power for some reason , hum then click and stop indicates a high probability it's the cap . If the compressor runs but no cooling , check the lines for an oil stain , which indicates a leak at that spot . Do be sure to shut off power to the unit while you've got your fingers in there unless you're actually checking voltage or performing tests . But you knew that .

Reply to
Terry Coombs

A few possibilities. Low refrigerant, bad capacitor, bad relay. Do you have the ability to check that stuff? If not, time to call a pro. Best to call now instead of July when it is 105 degrees.

Reply to
Ed Pawlowski

Warranty, check first.

Motor run cap is second thing to check. Then, overload and windings.

- . Christopher A. Young learn more about Jesus .

formatting link
. .

Reply to
Stormin Mormon

Reading comprehension not firstly set turn reversely backward?

- . Christopher A. Young learn more about Jesus .

formatting link
. .

Reply to
Stormin Mormon

Guys, thanks a lot for your help.

I have a business buying and selling industrial parts and doing some industrial scrap metal. So I think that I can troubleshoot this. I do not have any experience working with refrigerant.

My understanding is, the compressor has a single phase motor with external capacitor and resettable overload relay, right?

So, I would check, first, if there is 220v coming in (there likely is since the fan runs), secondly whether there is 24v coming into the coil of the contactor. If yes, I would check the overload relay. Maybe after this, turn off the system for 30 minutes and turn it back on to see if there is any humming or running compressor motor.

Then I should have a good idea if the problem is in the boards, power coming in, relays, or capacitor, right?

i
Reply to
Ignoramus18130

Leave the system off a while so the thermal has time to reset if it tripped. Turn it on while someone is out by the condenser and listen for a loud hum that stops in 15-20 seconds.. If you are getting that, then try the start cap. Bear in mind these things usually have a time delay on the compressor and if the power was off, it may not start right away although the fan will be running. Give it 5 minutes or so before you give up.

Reply to
gfretwell

The transistorised timer in my ancient Carrier A/C was intermittant. It would sometimes not turn on and sometimes turn off for no reason If it turned off then later came on again another 3 minutes elapsed befor the compressor came on. Having a long expierince in electronic problem solveing I had 2 A/C techs look at it before I decided to observe very carefully myself. Some judicious banging on the case and watching revealed the above. New timer works like a dream. :-)

Reply to
John G

CY: What does buying scrap have to do with troubleshooting an AC system?

I do

CY: Bummer.

CY: Not the ones I've worked with.

CY: Yes,likely.

secondly whether there is 24v coming into the

CY: Using some deductive logic, you can tell if there is 24 VAC without a meter. Just from your posts.

If yes, I would check the overload relay. Maybe

CY: Not what I'd have done.

CY: From what you write, you'd have some data, but not much idea.

Reply to
Stormin Mormon

If there wasn't 24V going to the contactor, the fan wouldn't be running. That would seem to suggest that the contactor/relay is OK too and supplying 240V to the output side which goes to the fan and compressor.

Reply to
trader_4

Ignoramus18130 posted for all of us...

Yes, call the installing/servicing co and get them out now before the temperature rises. It may still be under warranty...

Reply to
Tekkie®

Two things:

1) Where are you located? The reason that I ask is that I am located in an area where my gas and electric utility provider has a deal where they will come out and look at a broken item such as HVAC, figure out what is wrong, and give a price to fix it. If I don't use them to fix it, there is no charge for the visit. So, it's a free diagnosis. If you are lucky enough to have a utility company that provides that free service, let them check it out for you. I sometimes pay them to do the work if it is something basic and not too expensive. Their repair prices are high in general, but sometimes they can just fix what's wrong while they are there and I'm done with it.

2) Since the condenser fan is running, this may not be applicable, but two times recently when my AC was just blowing hot air it was because the lawn company accidentally weed-whacked the 24-volt wire running to the condenser (two different properties).

Reply to
TomR

OK, guys, thanks to those who encouraged me to look further.

Again, what was happening before was that the fan was running, but the compressor was not running.

I turned off the thermostat altogether, for several days, due to cool weather. Today, the weather was warm enough to try looking into my AC again.

I turned the thermostat to COOL and nothing at all is happening. The furnace fan is not blowing and the outside compressor and fan are not running at all.

This is a change from 4 days ago, when at least something was running, now nothing is running.

I spent some time today investigating this. This is what I found:

*) There is 120 volts coming into the furnace from the circuit breaker

*) There is 120 volts on the input of the 24 VAC transformer

*) There is no 24 VAC on the output of the transformer, the output is 0 volts AC.

*) The secondary (low voltage) winding has resistance appx. 1 ohm

*) The primary (high voltage) winding has infinite resistance, in other words it is broken.

So, on its face the answer is that my air conditioner is not working because the control transformer is not functioning. It should be easy to replace.

What I am not sure is why it failed. Did it happen simply due to age, or there was perhaps overdraw of current or a short in the 24v system that caused it to fail? Any thoughts on this?

I can easily find a 120->24v transformer, but I am not sure if I found the root cause or not.

i
Reply to
Ignoramus18857

OK, I think that I understand what happened, the root cause.

The cause was that the contactor for the outside compressor was not closing properly. That is why the compressor was not running originally.

Because the contactor would not close, the contactor coil used excessive current. After a while of this, the control transformer burned out.

I actually figured this out just by sitting and thinking.

Then I went outside, opened the control area of the compressor unit, and found the following confirming evidence:

1) The compressor motor works just fine when I push the contactor to close, by hand 2) The contactor coil stinks and looks blackened/browned, instead of wholesome gold like color. 3) The coil also stinks, like burned out coils are wont to do.

So, I think, that I am looking at replacing both the contactor unit, as well as the transformer.

I
Reply to
Ignoramus18857

I'd check the contctor in the ODU. Check the coil.

Reply to
Tony Hwang

Tony, it was exactly as you said, as I find out. Looks like I need to replace both the contactor and now the transformer.