Help wiring switched double gang receptacle at end of circuit

We are in the processing of completely rewiring a screened-in freestanding outdoor pool house. We have 14/2 outdoor rated wire coming into the structure. We'll have 2 runs of wire from the entry point into the back of the building - one run to each side of the building. One will go to a ceiling fan and a series of single gang receptacles, and the other will go to a couple of single gang receptacles, and at the end of that run, we want to put a double gang combination that includes a combo switch receptacle and 2 more receptacles, followed by a double gang receptacle to finish that half of the circuit. Here's a rough idea of what it will look like:

|--------| |--------| end | R R |_____| S R |______

Reply to
NJLauri
Loading thread data ...

Reply to
NJLauri

In the next to last box connect all of your nuetrals (white) together with the nuetral feeding the last box. The hot (black) feeding the last box goes to one side of the switch (load side) and the hot from the power line goes to the other side of the switch (line side) and the outlets in the next to last box. All of the grounds get connected to each other and the boxes if they are metal boxes.

Your combo-switch may only needs one hot connection from the power line to power both the switch and receptacle. You will need to check this out on the diagram that comes with the fixture. See figure 1-25 on this page (last one):

formatting link
Your last box would take the place of the light fixture in the diagram.

Reply to
RayV

formatting link

Thanks very much for your help. We'll try it out!

Reply to
NJLauri

I didn't see any reference to GFCI protection.

Has it been provided upstream of the pool house?

Jim

Reply to
Speedy Jim

Hi Jim!

Thanks for your question. Our plan was to install a GFCI immediately after the circuit enters the pool house, run the line from the GFCI into a work box, and split it there to run to both sides of the pool house. We figured that way the GFCI will protect the entire 15 amp circuit.

Does that sound like a reasonable plan?

~Lauri

Speedy Jim wrote:

Reply to
NJLauri

Sounds like a plan :-) Jim

Reply to
Speedy Jim