evaporator ice formation

Somebody mentioned several days ago that ice formation on an a refrigeration evaporator can be caused by low freon (or perhaps air in the system, I don't recall which). I've been wondering about that for the past few days. Why would low freon or air in the system cause ice formation? I'm just curious as to what the theory behind that is.

Reply to
Vic Dura
Loading thread data ...

When the refrigerant charge is low the evaporator coil gets starved for refrigerant and this results in reduced pressure at the inlet piston or expansion valve, thus allowing the refrigerant to vaporize at a lower temperature - below 32 degrees. At this point the first part of the coil will freeze. Then, since ice is a fairly good insulator the refrigerant will now travel further through the coil before encountering an exposed surface. More ice forms and the process continues. Gradually most or all of the evaporator coil will be covered with ice. This of course blocks air flow through the coil.

Reply to
Travis Jordan

What a concise, helpful answer. Thank you.

Jim

Reply to
Speedy Jim

It does seem paradoxical, but it is true:

formatting link

Reply to
Richard J Kinch

formatting link
But not quite for the reason stated: " With a low charge, you only get a dribble of liquid into the evap, which is at too low a temp because of the too-low suction pressure "

The evaporator temperature is a result of the vaporization of the refrigerant, not "too-low suction pressure".

Reply to
Travis Jordan

Ok, that makes perfect sense to me. Thanks for the clear explanation.

Reply to
Vic Dura

I think another way to look at it is when the compressed freon enters the condenser it is a hot gas. If there is the correct amount of freon, just the right amount of heat will be removed such that it will change to a liquid but still be quite hot. The hot liquid expanded through the evaporator gets the correct amount of cooling.

If the freon is low there may be only a small amount of liquid exiting the condenser and it will be cooler than normal. When it expands in the evaporator it can produce temperatures below freezing.

Reply to
Rich256

If you consider 80 to 110 deg "quite hot".

Not necessarily, it could be hotter than normal. It depends upon how low the charge is.

hvacrmedic

Reply to
RP

It's a result of the vaporization under too-low of a suction pressure. More to the point, it's a result of the coil's skin temperature dropping below freezing, because of the vaporization under too low of a suction pressure.

hvacrmedic

Reply to
RP

No. Vaporization occurs from heat transfer, not temperature. Heat and temperature are two different things, which most people confuse.

Look at the saturation pressure-vs-temperature tables.

Reply to
Richard J Kinch

Many refrigeration systems are designed for the evaporator to run below 32F, so they have a defrost feature.

Reply to
Stormin Mormon

You are correct - and that is what I meant to say.

Reply to
Travis Jordan

Reply to
TURTLE

This is Turtle.

there is a point in the Back pressure and head pressure points where at this one point that the evaperator will freeze up on low freon. In the Louisiana area it is on R-22 at 38 to 42 psi back pressure and other parts of the country up as high as 50 psi back pressure. A system can freeze up on low freon but usely only at one temp it will do it at.

TURTLE

Reply to
TURTLE

This is Turtle.

What you spoke about here has been on my mine for YEARS and ties into the evaperator coils on hvac system up at 38 psi to 42 psi in Louisiana and other lower humidity areas at 50 psi. Do you know any places where a fellow could read up on this freezing of the coil at lower temp and pressures of the evaperator coil.

TURTLE

Reply to
TURTLE