depot. Since they're so common, would you provide a link to one at h omedepot.com or lowes.com?
Perhaps the proper term should be dual phase or split phase. Does that work for you? I really didn't expect I'd be waking anyone up by responding to a 7 year old post.
61S11_ch3.pdfk you voted for Hillary, you should use the proper terminology."
Then why didn't you correct Ed's Electric when he said that professionals never call it single phase? Instead you winked at him.
They had single phase and 3 phase. They didn't
Guess the folks at Siemens surge protection, which is part of their power business must be hacks:
You are here: Siemens USA Power Distribution Product Portfolio Surge Protection FirstSurge?
Features & Benefits UL 1449 Listed, Type 2, Surge Protective Device (SPD)
Rated for 120/240 split phase panels up to 400A
Surge Current Capacities:
- 60,000 A
- 100,000 A
- 140,000 A
3-stage commercial grade notificationThese folks who make power conversion products are stupid too?
1.1 Service Entrance Panel For 120 / 240 VAC Split Phase AC Power Distribut ion Fig. 1 below illustrates the residential 120 / 240 VAC, Single Split Phase, 3- Pole, 4 Wire Grounding System, which was inherited from Edison's early DC distribution networks.
120 / 240 VAC Split Phase Electrical power from the utility (called Service )is fed through an electrical power meter to a load center / breaker panel for further distribution. This panel is called the Service Entrance Panel. This panel normally has the following components:The center-tapped configuration of the secondary side of the Distribution T ransformer provides following voltages to the Service Entrance Panel: ? 120 VAC between the Hot Leg L1 (Phase A, Red wire) and the groun ded, center tapped Neutral (White wire). The oscilloscope trace of the voltage waveform between the Hot Leg L1 and Neutral shows the voltage risin g in the Positive direction at the start of the waveform ? 120 VAC between the Hot Leg L2 (Phase B, Black wire) and the gro unded, center tapped Neutral (White wire). Please note that the corresponding oscilloscope trace of the voltage waveform between the Hot Le g L2 and Neutral shows the voltage rising in the Negative direction at the start of the waveform. This indicates that the two 120 VAC voltages are 180 degrees out of phase
I agree the panel makers that I saw all do call it single phase. Which I have no problem with either, because I'm not arguing about what it's called. That it's derived from one phase of what comes out of the power plant, I agree, I'm fine with calling it single phase or split phase. I'm just saying that doesn't mean that it doesn't look and act just like a two phase, 180 system.