Emergency generator and automatic transfer switch

As I understand these installations, if the generator capacity is less than the utility company's incoming then the selected circuits are split so only they are fed emergency power.

I would expect then if the capacity of the generator equaled or exceeded the utility incoming then both the generator and the utility drop could be fed to the transfer switch.

What % range of the installation cost might be saved by using a higer capacity generator set?

Reply to
Curtis
Loading thread data ...

The utility drop is not changed , your transfer panel wires to your existig panel

Why would you save anything by using a bigger generator, You wont it will cost more, a heavier unit , more wiring. Maybe a bigger gas line. I assume this is for ocasional power outages

Reply to
m Ransley

Plus a bigger gen means larger conduit, larger wire etc etc.

Reply to
m Ransley

if you have power coming in, the generator should be operating at zero capacity. i.e. off.

you want something that turns on when the power goes off. if you cant handle ANY downtime, put some batteries on it that can power the sytem for however long it takes to get the generator started after a power failure. or just put them on the items that you need. like a computer. the fridge will do fine if the power is gone for a few seconds.

randy

Reply to
xrongor

The gentleman's question is what savings there might be on the installation process for a generator large enough to power the whole house so that circuits to be powered don't have to be split off to a seperate panel as is typically done.

I think if you're going to do it one way or the other, get an electrician out to give you an estimate both ways. I think you'll find that the install cost difference is small compared to the cost of a much larger generator. Plus, you have the other problems like the increased size/weight of a larger unit too.

Reply to
Chet Hayes

The best way is another panel, with 2 watt meters built in

Reply to
m Ransley

see the body

Yes, only certain loads are on the generator. Even in industry the generators only run critical loads, usually.

Yes. But it is common for an 1000 amp service to have a 100 or 200 amp transfer switch. Using this as an example only. It depends on the load of the critical loads. Transfer switches start out at 30 amps and the largest I have ever done was

2000 amps. There are manual ones and automatic ones. The automatic ones have a variant that is a load sharing, similar to a soft start. CH makes this one as well as others. Not small I believe these are 1200 amp.

Savings for a bigger genset, absolutely not. Bigger is more money absolutely. Manual is less than automatic. Remember even with an automatic system your looking at 10-30 cycles minimum before transfer usually much longer. Really expensive to get any faster.

Reply to
SQLit

lets play ping pong.

ok i see it now. and i think you are correct. i would guess the cost of more generator pales in comparason to the cost of a sub panel.

one thing that comes to mind is that if you understand how a panel works, some of the circuits run of one leg of the 220, and some on the other, both using the neutral to get the 110. if you have a 110 generator wouldnt it be possible to wire it into the panel to energize one side of it without the other? then with a little clever wiring you put the things you want on the generator, on that leg of the 220. i dont think any harm will come to the

220 appliences that only have one leg powered, although they wont work either....

im just thinking outloud...

randy

Reply to
xrongor

According to xrongor :

Some random comments:

Any generator large enough to consider wiring into the panel is going to have 240V.

Even if it was 120V, it's not going to make the code-required transfer switching any less expensive.

Indeed, with the cheap generators being discussed, the transfer switching to (partially) energize the panel is going to cost almost as much (or more) than the generator does, so why not get a generator with 240V capability?

If you wire a small generator fully into a panel, even with the proper transfer switching, it'll be a moderately complex cutover process.

Reply to
Chris Lewis

Actualy Generac sells a complete prewired kit with exterior box, cable, plugs, and 2 watt meters on the panel for 200. It was a 4 hr instal complete, the hardest part was drilling through the house. Lowes often has free panels when you buy a generator.

Reply to
m Ransley

HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.