Copper vs. aluminum electrical supply

We are about to upgrade our panel from 100A to 200A. The run from the electric company drop to the panel is about 15 ft vertical drop followed by 30 feet horizontal run within the house.

- Other than the fact that copper costs much more than aluminum, what are the pros/cons of copper vs. aluminum?

- Is copper worth the added cost?

- Also, the supply will run through the unfinished utility portion of the basement at joist level. Is it worth it to encase the cable in metal (or pvc) conduit?

Reply to
Jeffrey J. Kosowsky
Loading thread data ...

Reply to
w_tom

This is Turtle.

If you ask about the electric service being in conduit between the service entrance and the main service box. I sure hope your going to get a Electrician to do this job. Yes it must be encased.

Aluminum is ok but Copper is better in the long run for joints getting loose or having connection burning off. Al. is called the poor man's wire.

TURTLE

Reply to
TURTLE

That's interesting.... because the current 100A service doesn't appear to be conduit -- it appears to be just a fat (2x1 inch oval), gray flexible wire.

Also, I asked our electrician who said you can always pay extra to put in rigid conduit but it is not necessary. BTW both the electrician who did the original job and the current electrician are licensed. Also, the house passed inspection.

Maybe the wire is in some type of flexible plastic conduit that looks just like wire :)

Reply to
Jeffrey J. Kosowsky

This is Turtle.

It was done by a friend or a None Electician before the codes were inforced in your area.

TURTLE

Reply to
TURTLE

No, house was just inspected. Electrician is licensed and no relationship. Again, I am just stating the facts, not arguing code or not code. Also, maybe this stuff that looks like wire counts as conduit.

Reply to
Jeffrey J. Kosowsky

That's service entrance cable (SE), and it does not need to be run in a conduit -- in fact, I don't think you're allowed to run it in a conduit.

I don't know about the 30 feet run of it inside the house, unless you have a disconnect at the meter (and even then I don't know if you can use SE for that long of a run.)

Bob

Reply to
zxcvbob

Here in New Jersey on a single family residence the 30' of wire does not have to be in conduit, but it must be protected by a circuit breaker or fused switch located just below the meter. On larger services for commercial or industrial buildings it would have to be in conduit encased by

2" of concrete all around.

If aluminum is installed correctly you shouldn't have any problems for a long time, but copper is still a better choice.

There is no reason to use conduit unless you anticipate the cable becoming subject to abuse.

John Grabowski

formatting link

Reply to
John Grabowski

This is Turtle.

This is new to me of using SE cable in a basement to connect the meter pan to the switch box and also going one end of the basement to the other in open air. If you would have a short in the SE cable before getting to the switch box the only breaker you would have is the 1,000+ amp breaker for the transformer to protect it. Like you said , The only way I could see this would be a 200 amp breaker & disconnect at meter pan to protect it before it gets to the switch box. I will have to pass this by my City inspector on SE cable run in open air

30 something feet in a basement and being before the switch box main and after the Meter pan. I would not want this in my house but NEC and city codes do let some funny things go by that I would not want , like Al. Wire for lighting circuits.

TURTLE

Reply to
TURTLE

According to John Grabowski :

Here in Canada, ordinary NMD is perfectly code-acceptable for this, but, yup, you MUST have a breaker/fuse box within 5' of the cable entering the house.

[There are _occasionally_ variations allowed, but you have to get prior permission from the inspector.]

Given costs that I last saw for wire this size, 30' would be about the most I'd go with copper before I'd consider using Al.

Same here.

Reply to
Chris Lewis

I woudn't want it in my house either.

I was just tryin' to help identify what the OP has. If the service conductors run more than 10' inside the house before they get to the panel, there's gotta be an OPD (breaker or fuses) outside the house. I don't think there's a limit to how far you can run the service conductors outside the house without an OPD, but I've never needed to look it up yet.

Bob

Reply to
zxcvbob

From the 2002 NEC handbook No maximum distance is specified from the point of entrance of service conductors to a readily accessible location for the installation of a service disconnecting means. The authority enforcing this Code has the responsibility for, and is charged with, making the decision as to how far inside the building the service-entrance conductors are allowed to travel to the main disconnecting means. The length of service-entrance conductors should be kept to a minimum inside buildings, because power utilities provide limited overcurrent protection and, in the event of a fault, the service conductors could ignite nearby combustible materials. Some local jurisdictions have ordinances that allow service-entrance conductors to run within the building up to a specified length to terminate at the disconnecting means. The authority having jurisdiction may permit service conductors to bypass fuel storage tanks or gas meters and the like, permitting the service disconnecting means to be located in a readily accessible location. However, if the authority judges the distance as being excessive, the disconnecting means may be required to be located on the outside of the building or near the building at a readily accessible location that is not necessarily nearest the point of entrance of the conductors. See also 230.6 and Exhibit 230.15 for conductors considered to be outside a building.

Reply to
Greg

i'm curious why you are running the 200a SE cable so far inside the house. my guess is that you are doing the new entrance in a different location than where the old service was, and you will be putting the new panel where the old one was, in order to reconnect branch circuits. if so, you might consider putting the new panel just inside the building (like normal), and then make a feeder run of #2 or 0, whatever, over to the old panel. You don't necessarily need 100a ampacity on this run, as long as the breaker size protects the feeder wire. Depending on what's in use on the old branch circuits, you may be able to feed with quite a bit less than

100a. Then feed new branch circuits out of the new panel. Just a thought. Bill
Reply to
bill a

Well, this is the way the old feed went. It enters the house at one end, goes through a 100A main breaker and then goes about 30 feet to the other end of the house where the main 100A panel is.

We thought of various alternatives for the upgrade including:

  1. Placing panel at entrance and moving all circuits to this new panel -- however, then we would need to rewire all the branch circuits or have some type of nasty junction box replacing the old panel

  1. Placing a new 200A panel at the entrance and converting the old panel into a 100A subpanel -- however, we thought this might confusing and a PITA having the two panels separated by the length of the house. Especially, since given the mix of old and new wiring two circuits feeding the same room could end up in different panels 30 ft away from each other.

Therefore, we are planning instead to consolidate all the circuits at the location of the old panel. In doing this we considered two options:

A. Place new large 200A panel next to the old panel and convert the old 100A panel into a subpanel of the new panel. This would mean leaving the bulk of the circuits in the old panel and keeping the new main panel mostly unpopulated (but likely to fill in over time). -- we chose not to do this since this seems a little kludgey with the subpanel having more circuits than our new main panel

B. Instead, we are planning to replace the old 30 circuit 100A panel with a new 42 circuit 200A panel in place which requires a bit more effort to move over the breakers and reattach neutrals and grounds. Then, we will move the old 100A panel to a location next to the new 200A panel to hold any circuits after we run out of space in the new panel.

Finally, rather than having a meter outside, then a main breaker just inside, and then a 30 ft run over to the panels, we are thinking about placing a combo meter/breaker unit outside replacing our old meter and then entering the house and running 30 feet directly over to the new panel. This has the benefit: - Reducing costs (since no need for separate main breaker just inside the house) - Eliminating "extra" box inside the house - Allowing fire dept easy access to electrical shutoff in case of emergency

Does this thinking make sense??

Jeff

Reply to
Jeffrey J. Kosowsky

My understanding is that by having an exterior main breaker (shutoff), the interior panel is considered a subpanel, and so the conductors leading to it are feeders, not service conductors. I have a similar situated, I elected to use 1/0 Al SER cable as my feeder cable; it is stapled to the underside of the joists in my crawl space.

Cheers, Wayne

Reply to
Wayne Whitney

I believe you are correct technically -- sorry for my misleading "lay" use of the word "supply" when feeder (and subpanel) were more technically correct.

Reply to
Jeffrey J. Kosowsky

Reply to
Joe Fabeitz

This is Turtle.

I know it is a problem for NEC and the International Mechnical Code would not allow this without a breaker before the switch box. All 50 use these codes and stick by them. Now he could be in Mexico or Canada and i could be wrong.

TURTLE

Reply to
TURTLE

Makes sense. Or you could get a w/p outdoor main disconnect which holds not only a 200a main but also at least one additional 2-pole breaker for an outdoor hottub or pool panel.

In my jurisdiction, outdoor tubs and pools can not be fed from subpanels due to proper grounding and bonding issues.

Reply to
HA HA Budys Here

Jeffrey J. Kosowsky posted for all of us....

Hey Jeffy, going to the warehouse to get some cable and connectors cheap? Say volts, amps, shorts and you will impress them with your knowledge and they will drop their drawers, er prices to suit you.

Reply to
Tekkie