Most of my work has been new construction and very little service tech so forgive me if this is too simple. My ex-wife called me a few days ago and said her heat pump wasn't cooling. She said someone replaced the compressor, which made it much better, but it's still not cooling like it should. So I thought that unless I want to give her even more of my hard earned money, I better load up the truck and head over.
Here's what I found. It's a 3 ton 10 seer HEIL split system heat pump with a TXV. New copeland recip compressor and new dual cap. Coils are clean, filter is clean. I put the guages on and that's when I got a little confused.
outside air temp - 81 inside air temp = 78 Outdoor humidity: ~70%
Suc Pressure - 64 Suc temp - 80
Liq Pressure - 200 Liq temp - 87
Condenser TD - 13 Evaporator TD - 14
My handy Trane charging chart shows it being slightly overcharged.... but shouldn't be enough to give me such a low TD across the evap. Rather than just start fiddling with the charge I thought I might want to actually try to figure out what's wrong with it.
The only other thing out of the ordinary is the condenser fan was replaced with one that's 75 rpm faster. It calls for a 1075 rpm and has a 1150. In my brief experience I believe that won't have a big effect.
any ideas?