Could one estimate their heat load by clocking the meter and adjusting the gas valve on the furnace?

I turn down the gas valve reducing flame size until the furnace runs continuously on a design temp day, then clock the meter to determine the input btu's. Multiply the input btu by the AFUE factor should provide the output btu.

ie: existing furnace input btu 100k, output 80k

Turn flame down and read meter clocked at 60k (furnace running continuously and maintaining temp)

Effective heat loss would be 60k * .8 = 48k

Would this not be more accurate than a mathematical model assuming the in/out relationship of the existing furnace is still 80%.

Reply to
Fred
Loading thread data ...

Get a self-regulating digital thermostat and let the technology do this for you. Honeywell makes a good one--their technology is called "adaptive recovery".

You may need to run the ground wire loop to the "G" terminal--better read the manual that comes with the stat to see for sure.

Reply to