I have a honeywill furnance, about 20 years old with electonic igniter. When I turn the thermostat up, the igniter works and lights the pilot light, but it does not stop sparking, as it should. The main burners do not turn on, I presume because the igniter has not stopped firing. The pilot flame is on the thermocouple as it is supposed to be. Any suggestions on what the problems is and how to fix it?

TIA Denis

Reply to
denisclegg
Loading thread data ...

It hasn't sensed that the pilot is lit, so continues to try to light it and doesn't turn on the main gas flow. The thermocouple is probably bad.

Reply to
CJT

Your intro is ok but your conclusion doesn't follow. Try again.

OP, listen to what Paul said.

Reply to
Richard

Sounds like its broken and you need to call a tech

Reply to
Noon-Air

I thought thermocouples were for standing pilot furnaces. Do you mean flame sensor of some kind?

Reply to
Stormin Mormon

It has electronic ignition and you want to change the thermocouple? You're an idiot CJT Bubba

Reply to
Bubba

It is not continuing the start up sequence. Normally the flame sensor tells the control board that the pilot has lit and it opens the main gas valve. Unless you can troubleshoot further you're probably better off calling someone as most of the parts are expensive and non-returnable. You could try a little steel wool on the flame sensor.

Reply to
jamesgangnc

When did *Honeywell* start making furances?

Reply to
Zyp

Zyp posted for all of us...

Ok Zyp, let's get this straight... It's not Honeywell - it's Honeywill - like in Honeywill ya please light this time...

Reply to
Tekkie®

LOL

Reply to
Zyp

HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.