I've got to sister five 17' long ceiling joists, due to removing a bearing wall. I've done the engineering, and given the existing roof construction, I've got two options that work:

1) Use double 2x6 select struct at 16" o.c.

2) Use 2x8 select struct at 16" o.c. with a 3.5" long by 1.75" deep top edge end notch.

The selection is deflection controlled, as 2x6 select struct at 16" o.c. meets bending and shear.

Which option is better? The material cost for the 2x6s is about $50 more. I'm mostly working alone, so the 2x6s will be somewhat easier to wrangle into place. Otherwise, it is notching the 2x8s versus the extra nailing to double the 2x6s.

Thanks, Wayne

Reply to
Wayne Whitney
Loading thread data ...

I would go with single 2x8 sisters, less wood to buy, haul, and wrangle with. Besides, 2x8's tend to run straighter than 2x6's. Nailing a single sister will also involve fewer intrusions into the original rafters, not to mention hammer strokes. Given that you are sistering existing, presumably bone dry, rafters, I would also go with KD stuff. Then again, I cannot even figure out my window sizes...

Reply to
Rima Neas

Wayne-

Does the notch start at the end of the joist & only run 3.5"?

IMO this isn't really much of a notch ....more of a depth reduction in the joist shear / bearing zone?

I assume it needs to be there for clearance issues?

You might consider a taper cut rather than a sharp cut out.

Timber is happier if you avoid abrupt section changes but in this case the local stress state appears to "compress" :notch rather than wanting to split it open.

If you don't have a copy you might consider getting one

Design of Wood Structures ASD/LRFD Sixth Edition by Donald E. Breyer

or a older addition (cheaper) ....always great for timber design concepts but newer editions conform to newer codes.

& this guy is a real timber expert.

cheers Bob

Reply to
Bobk207

Wayne-

I must have missed this thread plus I didn't specifically answer your question....

I'd go with the 2x8's and taper cut them.

cheers Bob

Reply to
Bobk207

Yes, everything you say is right, it is a depth reduction needed for clearance. The reduction from 7.25" to 5.5" is just under 25%, the code maximum.

An immediate taper cut is not possible. The roof is constructed with a 1x4 bearing on top of the 2x6 ceiling joists, and the 2x4 rafters bear on the 1x4. Crazy 1908 construction. So I have to actually reduce the depth to 5.5" where it is under the 1x4, hence the 3.5" long end notch. I don't want to modify the roof construction, as that would open a whole other can of worms.

So after the notch clears the 1x4 obstruction, I should do a taper to increase the depth from 5.5" to 7.25" more gradually? Is a 45 degree taper OK or should it be shallower?

Thanks, Wayne

Reply to
Wayne Whitney

Wayne-

I was thinking of cutting a taper that did the job of the notch but sounds like the taper at the joist end would result in a rather shallow joist end?

But as you mention you are deflection critical , shear or bending stress not an issue. So I think that the taper would work....check the shear for the reduced depth. I doubt that a 12" or 16" taper would reduce the beam stiffness much.

We're really discussing stuff that is pretty much second (or third order) effects.

If you can't use a taper cut to do the whole job...I'd use a large paddle bit or hole saw to define the end of the clearance relief & just jig saw to it.

Cutting a taper out of the relief cut is really overkill.

cheers Bob

Reply to
Bobk207

The notch on the upper side isn't nearly as critical as a notch on the bottom of the joist. There's also the possibility of sistering on a

3/4" plywood scab to help distribute the stress at the reduced cross section - whether notched or tapered. R
Reply to
RicodJour

If I do the minimum taper possible over a length of about 17", I have an end depth of 5". Does that seem sane with a 2 x 8 x 17'?

Well, I assume the shear should be checked at the face of the support, since going into the support the shear stresses are decreasing as the bearing comes in. In that case, if I maintain the 5.5" section depth at the face of the support, there is nothing to check, as I already know a 2x6 passes bending and shear.

Thanks, Wayne

Reply to
Wayne Whitney

I'm still wondering about your sanity! ;) What sort of deflection are you getting with a 2x8 sistered on?

Right. And you're doubling the cross section.

R
Reply to
RicodJour

From the awc.org calculator, the span rating for a 2x8 SS DF with a

20psf live load and L/360 deflection is 17' 2" and is deflection controlled. So ignoring any end taper, the deflection at 16' 5" will be L/360 * (16'5/17'2)^3 = L/412, or 0.47".

I'm ignoring the existing joists when doing this calculation, since they are 2x4s. Most of the house has 2x6 ceiling joists, so I was quite surprised to find the 2x4s in the area I'm working on.

Cheers, Wayne

Reply to
Wayne Whitney

You might be ahead to explain what it is you are doing. I don't think I would mess around sistering a bunch of joists. If the existing 2x4 have worked fore years, I would spend the time designing a beam to carry the load for the wall you are yanking. It would seem much more simple to me to install one beam and the carrying ties. By the time you sister the joists in question, you will have the existing ceiling on the ground.

Just where were you going to special order those 17 foot 2x8/s?

Reply to
DanG

Dan's got a great point - it was bound to happen eventually! ;) A flush beam supporting the joists with joist hangers would be much simpler and cheaper. There's usually some surgery to create the beam pocket and you have to plan the assembly (possibly installing beam, then installing supporting studs), but it's a preferable way to go in almost all aspects. You mentioned five joists needed sistering, so that's about a 8' span. You wouldn't need much in the way of a beam since it's only a ceiling load - you were surprised that the CJs were

2x4s so it's safe to assume that you hadn't been up in any attic space. A couple of 9.25" LVL's would be more than enough.

They're not special order around here. Generally, depending on the yard, they stock 18' or 20' 2x stuff.

R
Reply to
RicodJour

Yes, nothing special about the long 2x8's where i live either. my local lumber yard has them up to 24' in 2' increments.

s

Reply to
S. Barker

Rico-

If he's got the ceiling plaster down, wouldn't throwing five long

2x8's up there & nailing them in place be quicker than creating beam pockets, cutting the joists, installing a beam with hangers?

cheers Bob

Reply to
Bobk207

Wayne-

As Rico mentioned, he does sometimes question our sanity on these design issues.

The taper or the end relief would work (IMO) with or without a plywood side plate.

Does a joist edge depth of 5" vs 5.5" really make that much different?

I'd cut the taper & be done.

Rico-

I think Wayne's thinking about using single (notched) 2x8's OR doubled 2x6's.

cheers Bob

Reply to
Bobk207

Reply to
RicodJour

Damn send button! Sorry about that.

Without pictures it's tough to tell what's the quickest solution. There's room above the CJs, and the OP mentioned having to notch, but he didn't say whether it was one or both ends. There might be room to put the beam above the existing CJs without cutting them and hang 'em.

The sistering option seems to be throwing a lot of extra expense and weight at the problem and getting a fairly large deflection as a result. Sistering may be a bit faster, but I don't think a 1/2" deflection is acceptable. It's definitely not necessary. Doesn't seem like a great solution.

R
Reply to
RicodJour

Thanks, that's what I've settled on with the group's feedback. :-)

Right, that was the original question.

Thanks, Wayne

Reply to
Wayne Whitney

OK, here comes. The house is one story over crawlspace/basement, with a hip roof. Here is some ASCII art that shows the plan dimensions and the original location of bearing walls (B):

43' !--------------------------- ! ! 8' ! ------ 26' !BBBBBBBBBBBBBBBBBBBBBBBBBBN ! ! NBBBB! 17' ! N ! !-------------------------------- 51'

The 26' wide by 43' long part of the house has continuous full thickness 2x6 ceiling joists. The rear 8' of the house has 2x4 ceiling joists. In this rear 8' area, I have removed the ceiling and the bearing wall for the ceiling joists. I have also removed the non-bearing wall (N).

Well, since the wall N is also gone, I'd have to design and install a

17' long beam as well as the 8' long beam over the former bearing wall. That seems like a lot more work than installing 5 new ceiling joists. I'm pretty happy with the solution of using 2x8s with end tapers.

As others suggested, in my neck of the woods 20' is a stock length.

Cheers, Wayne

Reply to
Wayne Whitney

Well, I was surprised because the rest of the ceiling joists are 2x6s, just the five where I'm working are 2x4s. C'est la vie.

As to the load, according to the 2006 IBC, if the clear space between the joist and the rafter is under 42", I can call the space "attic without storage" and use a 10psf live load. Otherwise it is "attic with limited storage" and I need to use a 20psf live load. That's not much less than the 30psf for bedrooms.

Now the outermost 3 of the 5 joists do have the restricted clearance because of the hip roof, so I could use only 10psf live load there. However, for a 16.5' span with joists 16" o.c., a 200lb point load in the middle of a single joist gives the same deflection as 14.5 psf does. So I'm going to stick with 20psf live load everywhere.

I'm curious as to why you say that. This is the deflection due to live load only, so it is just while someone is walking around up there. The IBC requirement for ceiling joists supporting a plaster ceiling is L/360, and 1/2" is L/412. So do you believe L/360 is inadequate?

Thanks, Wayne