Sanity check - single core unsheathed in conduit, ref methods...

Just a quick sanity check - would be grateful if anyone is able to concur as the result is borderline... Ignoring voltdrop considerations and looking only at cable sizing for current - I have been through the regs, Amendment 1 (Green) and concluded, for

2 (plus earth/CPC) unsheathed PVC (70C) single core conductors in conduit, NOT T+E:

1) In a brick wall (in brick skin, under plaster, no surface insulation to room, but cavity insulation behind brick leaf) assuming thermal resistivity of brick (inverse-k value) is < 2Km/W:

is Reference Method B, from number 42, page 319

2) In conduit in free air clipped to side of basket tray or laying on joists:

Also Reference method B, number 4, page 317.

Basically I'm trying to work out if I can "get away" with 6mm2 rather than 10mm2 for some 40A circuits (cooker, water heater).

To be honest, Ref B gives me 41A at 30C, but I should probably apply a derating factor of 0.87 for 40C as it's a roof space. Then again, it's now an insulated roof so... (Wish I'd put a min/max thermometer in last summer!)

10mm2 is possible (I have 25mm conduit drops) but no sense in pulling heavier cable than I need.

The cooker will be a 900mm induction+ovens so 32A is cutting it a bit fine, 40 probably better.

Cheers :)

Tim

Reply to
Tim Watts
Loading thread data ...

You need to read up on Diversity Factor. All the parts of the oven will never be in simultaneous use.

formatting link

Reply to
harryagain