Can anyone point me to a source of meter tails bigger than 35mm? I'm having a three phase 160amp per phase supply to a workshop, need probably 50mm tails (anyone able to confirm??) but no one seems to stock it. Any pointers gratefully received.

AWEM

Reply to
Andrew Mawson
Loading thread data ...

TLC will supply it in cut lengths - but to order as branches don't stock it.

Reply to
Dave Plowman (News)

Table 4D1A, 70 deg. PVC singles, Ref. method F (free air or perforated tray), 3-phase, cables touching in trefoil formation:

- 35 mm^2 - 137 amps

- 50 mm^2 - 167 amps

- 70 mm^2 - 216 amps.

Try the more industrial orientated wholesalers like Newey & Eyre or CSE

formatting link

Reply to
Andy Wade

perforated

Andy thanks for that. Is there a derating factor as its in 100mm square pvc trunking or does that count as free air?

AWEM

Reply to
Andrew Mawson

You'll be needing 70 mm^2 then...

Table 4D1A, ref. method B (enclosed in conduit or trunking on a non-thermally-insulating wall), 3 or 4 cables 3-ph AC:

- 35 mm^2 - 110 amps

- 50 mm^2 - 134 amps

- 70 mm^2 - 171 amps

- 95 mm^2 - 207 amps

Reply to
Andy Wade

City Electrical Factors.

Reply to
mark

Thanks Mark, TLC have got them for me - should arrive Mon/Tuesday - ended up having to use 70mm

AWEM

Reply to
Andrew Mawson

Good luck bending the buggers ;-)

Reply to
John Rumm

Linesmen used to use extra large ring spanners[1] to get sets into the Henlite[2] cables for connection onto pole transformers.

[1] 3/4 x 7/8 whit from memory [2] Trade name, insulated and sheathed Ali cable, largest size used to be 120mm² I think.
Reply to
The. Wanderer

I've got a piece of 150mm² here (11kV)... It's only 14" long so you can't get much leverage, but might as well be rock solid (overall dia = 31mm).