On 3/1/2014 1:42 PM, snipped-for-privacy@snyder.on.ca wrote:

At high limit, the delta T will be higher than spec, so more heat goes into the house. Then, it goes through the cycle. I can't see this being a major loss of efficiency.
--
.
Christopher A. Young
Learn about Jesus
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Saturday, March 1, 2014 6:03:05 PM UTC-5, Stormin Mormon wrote:

You have it backwards. With a lot of the air handler air flow blocked off, you have less air moving, the air in the plenum get *hotter* and the temperature delta across the heat exchanger is lower, ie the plenum temp is closer to the temp of the combustion gases. Hence, you recover less heat and more of it goes out the exhaust.
Also as pointed out previously, if the furnace then kicks off and recycles on and off due to the high limit being hit, during the period it's cooling down, most of that heat is being lost up the vent, or could be lost to an unfinished basement, attic, etc. I think that's largely a moot point, because I believe any modern furnace is going to trip and stay off with a fault code if the high limit is exceeded. But if it does continue to cycle on and off, no question you're taking a hit on energy loss.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Temps below zero F, tonight, with wind chill even below that. Should I leave a faucet dripping?
Should I cover a heat vent or two?
--
.
Christopher A. Young
Learn about Jesus
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Mon, 03 Mar 2014 22:23:10 -0500, Stormin Mormon

"redneck bungalow" You won't need your bunny slippers to go to the john, and you won't freeze your pipes.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 3/4/2014 8:02 PM, snipped-for-privacy@snyder.on.ca wrote:

Rent a heater. Pay for fuel oil. Pay for electric. Heat goes out from the skirting.
So, tell me about savings?
--
.
Christopher A. Young
Learn about Jesus
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

There is no "sweet spot" for the heat exchanger efficiency. Setting the blower on HIGH blowing more air over the heat exchanger will always be more efficient then lass air.
It's only a sweet spot in terms of comfort and not feeling a draft in your home, not in terms of heat exchanger efficiency.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 3/1/2014 6:36 PM, snipped-for-privacy@yahoo.com wrote:

You're not suggesting that Clare is mistaken?
--
.
Christopher A. Young
Learn about Jesus
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Fri, 28 Feb 2014 22:35:34 -0500, Stormin Mormon

Was it before or after you bought them that they converted to Mormonism?

Almost in the same way. I think?, that driving short distances and never letting a car's engine warm up to proper operating temperature. In the case of the furnace, it may get that warm, but because it turns off soon, a higher percentage of the On time is at the lower temperature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 3/1/2014 1:49 AM, micky wrote:

SM: After, sadly we were not able to find Mormon furnaces. So, we gave them lots of natural gas, and now they blow hot air.

SM: With a cold return closed, the furnace would reach operating temp sooner, and spend more of the day at operating temp. Not sure the two can really be compared.
--
.
Christopher A. Young
Learn about Jesus
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sat, 01 Mar 2014 06:48:01 -0500, Stormin Mormon

FTR, I thought we were talking about closing the warm air supply to some rooms, but actually I don't think there is much difference.

But they don't run all day. It might be 10 or 20 minutes. Yeah I see your point that, assuming as was said that they warm faster, they get to operating temp sooner than normal, but they might then zoom though that temp range on to overheated soon thereafter.

I think they can but maybe there is no general rule. Maybe each similar furnace setup is the same but ....
Well I don't know what the but is, but I've been bothered since yesterday, per my previous post, wondering if that was why my furnace was turning off. In the short period between replacing the igniton transformer and having the next problem, I was sitting at my computer in the room next to the furnace and for about an hour I logged when it started, when the blower started, when the fire stopped, and when the blower stopped. The notes are somewhere in my Agent outbox so I have to find them and read them.
The rest of this post is about my 1979 furnace and may not interest most people, but though many things have changed over the years, I doubt the final actions described here of the control panel, etc. have changed.
I've also been trying some more to understand the furance wiring. There are a couple omissions to the wiring diagram (2 resistors), and one or two more things** I haven't figured out yet, but most I do understand and when the heat limit switch opens, that interrupts the 120 volt black wire to the furnace. which will turn off the burner motor, the ignition transformer, and the control board power transformer (which powers the furnace relay so that too turns off the furnace) . The fan wiring I find complicated but I don't think the fan turns off because it's needed to cool off the plenum etc. which we just said had overheated. Anyhow, after the house reached 168, the furnace never ran for more than 20 minutes iirc and that started to worry me.
Since I've had trouble with the control panel, what I've been doing is turning the furnace on by hand (with a stick*** holding down the relay armature) for 2 or 3 hours when I wake up in the morning, and for 2 or 3 hours just before I got to bed. (Less time during the couple days it was warmer out) I get the second floor of the house up to 178 or even 180 before I got to bed (where I often listen to the radio for a couple hours and then sleep 8 hours) and it's 164 to 168 in the morning. Under the covers it's always warm enough, but a couple days, I've had to dress quickly and go turn the furnace on.
If my furnace could overheat in 20 minutes, surely it would overheat in 3 hours and the high limit swtich would turn off the whole furnace. But it doesn't. I have to turn it off by taking the stick out. So it must not be overheating.
***The stick was originally used to post an illegal advertising poster on public land. Baltimore County law now allows anyone to remove such signs. Many are held up by wire things, but when it's wood, I save the wood. About 2 feet long by 1 by 1/2" with a point at one end.
**Things I don't yet understand about the schematic. The switch that turns the furnace off when there is no flame (or maybe too much black smoke??) has four wires going into it, but the schematic shows nothing about how they are connected inside -- it's a black box -- and that makes it hard to understnd the main relay's operation, since two of those four wires are connected straight to the main relay coil. Also the fan relay, which is in the fan & limit control enclosure, I think, I have just started to figure out. The schematic does not use the same exact symbols that radio and tv schematics do. I think I've found a double throw switch but I'm not sure. (Maybe I'll post the diagrams) It also doesn't match my own fan, which has 3 speeds but only one is connected, the same fan speed for everything. This one from the web for my model may have high speed for AC and low or medium for heat.
It also appears that 24 volts are provided to close the main relay, when the thermostat calls for heat, but maybe that's lowered to 12 volts to keep the relay closed once it has closed. Can't tell because of the black box.
I have also found that sometimes when the house is cold enough that the thermostat should call for heat, when I start to close the relay by hand, when the armature is half-way there, it's pulled shut magnetically****. But it didn't shut without my help. That goes with something I think you said, that there's a problem with the main relay coil. So I've decided to replace the control board (including the main relay coil) first and worry about the thermostat later.
****Other times when the house is cold, there is no magnetism in the relay. How can that be? Maybe that's a problem with the thermostat or maybe it's gremlins.
(ONE DAY WHEN I GUESS I HAD THE STICK just right, the furnace went on and off by itself for 24 hours or so, and the house was always 68. I guess the stick wasn't holding the armature closed but it was holding it close enough to the relay coil that the coil could pull it the rest of the way. Nothing else makes sense.)
I also remembered that my thermostat is electronic or semi-electronic, not like the round honeywell thermostat that was used initially in 1979 and is in the schematic, and disconnecting the stat and expecting to find zero ohms across the red and white wires when the house is cold might be wrong. Maybe it needs its 24 volts to work right.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Fri, 28 Feb 2014 21:16:31 -0500, snipped-for-privacy@snyder.on.ca wrote:

Hmmm. That's a serious concern. Thank you. How short do you think too short an ON portion of the cycle would be?
Also there should be some way to know if the furnace is turning off because the thermostat reached the desired temp, OR becaues the high limit switch turned it off. I realize now that I don't know why my furnace turns off.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

If the furnace shuts down while the thermostat is still calling for heat, you have a problem, and it is short cycling.

usually has an indicator telling when it is calling for heat.
Mine ( a 2 stage furnace - high stage really too big for the house) will occaisionally short cycle if it goes on high.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sat, 01 Mar 2014 13:16:42 -0500, snipped-for-privacy@snyder.on.ca wrote:

Well, right now I'm not using the thermostat, but now that this issue has come up, I'm going to up the priority of the control board replacement and I should know soon.
Although with a day to think about it, it seems to me from theory and looking at the wiring diagram for my furnace installation that if the high limit switch opens, the furnace would shut down, except for the blower needed to cool it off, and it never shuts down until I do it manually, even after 3 hours. That's certainly not a short cycle.

I have maybe the first residential setback thermostat sold, from 1984 maybe. It's electronic or semielectronic, The clock is digital but the time and temp settings are mechanical switches. Anyhow, no indicator.
But when I replace the control board on the furnace, I'll put in a couple wires that extend beyond the furnace, so I'll be able to use a voltmeter to check without having to get my hands in among hot wires.

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 2/27/2014 11:24 PM, micky wrote:

In my case, the return air vent is in the hall. If I close a vent in one of the two small bedrooms, there will be no air flow.
--
.
Christopher A. Young
Learn about Jesus
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 2/27/2014 10:31 PM, micky wrote:

The evidence of it working, is that rooms are colder, and heat bill goes down. Hard to compare heat bill, but got to figure it's doing some thing.
--
.
Christopher A. Young
Learn about Jesus
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Fri, 28 Feb 2014 07:36:32 -0500, Stormin Mormon

I said at the top that I assume I'm saving money.

For just this reason.

I too can't really tell if the cost has gone down because I didnt' keep records before I closed the vents, and I'd have to keep track of degree days from one year to the next and gallons of oil delivered and it's too much effort.
When I say at the end I don't think it will change anything, I mean I don't think it will change the character of an oil (or gas) fire to either make the air in the house dirtier or make more carbon monoxide, or something else I wouldn't like. DD3 says the same thing, iiuc. But someone here in the last 15 years once said it would, and iirc no one posted a disagreement.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
...snip...

Just for the record, I don't recall making any comments related to dirty air or carbon monoxide.

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sat, 1 Mar 2014 00:03:01 +0000 (UTC), DerbyDad03

I think I missed one word that changes everything. Sorry. People, forget that I mentioned DD's name here.

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

if you put a box, and it would be quite a big box, over the living room you wouldn't be able to get in or out

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Hah. You Yanks really are in the dark ages,like a hundred years behind the rest of civilisation. My house needs no heating most of the Winter I have two feet of insulation in the walls. The TV and freezers keep the place warm
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Related Threads