I understand that a residential service panel requires 2 sources for grounding. I was looking at a newly installed panel the other day and I'm not sure that it was installed correctly.

This panel has a neutral bar on both sides of the panel and ground bar on the right hand side only.

At the electric meter on the side of the house, there are 2 bare copper wires running down the wall into the earth. These wires were existing prior to the installation of the new panel. They look like this:

formatting link

When the new panel was installed, a new ground wire was run from within 5' of the water meter to the neutral bar of the panel. The neutral bar is bonded to the panel with a large green screw next to the incoming service neutral lug. I believe that this part is OK.

However, this is the part that I'm not too sure about:

Above the panel, there a ground wire clamped to a water pipe. This wire was there before the new panel was installed. The wire was pulled into the new panel attached to the ground bar.

Does that wire count as a second grounding point for the panel or is it essentially the same point as the new ground that was run from the water meter to the panel?

Shouldn't I be seeing something that directly connects the ground wires at the electric meter to the panel?

Reply to
DerbyDad03
Loading thread data ...

You really only need 2 electrodes if one of them is the water pipe.

As long as your grounding electrode conductor goes from the neutral bar to the pipe, within 5 feet of where it comes through the wall and there is nothing between that and the dirt (meter, filter or whatever" that is your primary electrode. A water pipe has to be supplemented with another electrode and it sounds like that is a rod or two outside. (they usually get installed in pairs)

I can't see it but it sounds right.

Reply to
gfretwell

Not necessarily. Old services used to only be connected to a metal water service pipe. (Now you need a "supplemental" electrode for new services.)

A house might be built now with plastic water service pipe and a "concrete encased electrode" (Ufer ground) used as the only grounding electrode.

You can connect grounding electrodes anywhere from the connection to an overhead service drop (or at the connection to a service lateral) up to the neutral bus at the service disconnect. But that is irrelevant here

- see below.

That is how connections to a water pipe service is made now. The "supplemental" electrode is presumably 2 ground rods connected at the meter.

I presume the water meter is bonded and that is irrelevant to your questions.

You used to be able to connect to a metal water pipe electrode anywhere on the interior metal water pipe system. This was the grounding electrode connection for the old service. It is not required now, but is a little improvement. It is not a "supplemental" electrode.

Generally you want to connect all the grounding electrodes together and make the connection to the service neutral at one point.

But "supplemental" electrodes can be connected several places, including the meter. Ground rods are a pretty crappy electrode.

Reply to
bud--

The problem is, as far as I can tell, both of them are the same water pipe.

I think this is what I should see, but I'm not sure that I do:

formatting link

What I don't see is a connection from the ground rod(s) to the panel. Please see the images below.

See here:

The first image is of the meter and the ground wires going into the earth:

formatting link

This second image is of the panel. It shows the old bare copper wire that is attached to the water pipe right above the panel. That is the wire that is attached to the grounding bus.

It also shows the new black, insulated ground wire that runs back all the way across the basement to the water meter.

I don't understand how the ground wires at the meter/rods are connected to the panel as shown in the web image above.

formatting link

Reply to
DerbyDad03

In the pic of the panel you have three ground wires identified. One goes to the water service pipe. One goes to the water pipe in the house. Where does the third one go?

Reply to
trader_4

...snip...

Actually, I only have 2 grounds identified, but I can see where the confusion might come from.

If you read the 2 text boxes related to the "bare ground wire" the upper one says that the ground wire that is attached to pipe above the panel "runs behind the joist" and the middle text box says that the bare ground wire "emerges from behind the joist".

That is the same ground wire.

Reply to
DerbyDad03

So you have one grounding electrode, ie the water service pipe that comes directly into the panel. According to Bud, the supplemental electrode(s) can be at the meter and it sounds like that's where they are. The only part I'm confused about is that you appear to have just two hots and a neutral coming into the panel from the meter. So the neutral which is a current carrying conductor would be what ties the grounding system together, ie it connects the water pipe ground at the panel to the supplemental grounds across a distance of 5ft, 10ft? whatever. Is that OK with code? Seems questionable to me. Bud?

Reply to
trader_4

That, my friend, is exactly what I find questionable too.

The homeowner has already called the owner of the company that installed the panel and informed him that the circuit grounds and neutrals should not be on the same lugs (my post from last weekend). The owner will be coming out to fix it. He will order a new ground bus for the left side of the panel and remove the grounds from the neutral bar.

The owner (electrician) told the homeowner that he can't believe that one of his guys actually wired it that way. "He should know better!" Makes you wonder what else this guy has wired that is still in use. If I hadn't of been curious and and wanting to see how the new panel was wired, this one would have gone unnoticed, probably until the homeowner tried to sell the house and the buyer got it inspected.

Now I'm trying to find out if he has to fix the service ground connections also. The homeowner doesn't want to call this guy back more than once.

Reply to
DerbyDad03

You can attach the grounding electrode conductor any place between the service point to the service disconnect enclosure. Connecting in the meter base is pretty common around here.

Reply to
gfretwell

Thanks for the responses.

I'm still confused how the situation we're discussing matches up with this picture. Maybe it doesn't have to?

formatting link

What I don't see is the connection from the ground rod to the panel. Does the connection of the ground rod at the meter eliminate the need to connect the panel to the ground rod?

If that's the case, then does that mean that the short ground wire to the pipe just above the panel is redundant since a new ground wire was run from the panel all the way back to the meter?

Seems to me that the section of pipe above the panel could easily become not grounded if a section of pipe between it and the meter was replaced with PEX, etc. I thought that was why you had to be bonded within 5' feet of the meter now.

Reply to
DerbyDad03

In this case the most useful ground is the water pipe, which is connected at the panel. Other comments below.

In this system there are 2 points of attachment. I don't think that is OK in general, but in this case it is OK to attach the "supplemental" ground rods at a separate place (the meter, if that is what is attached there).

You can have all the grounding electrodes (GEC) attached at the meter (as at g's location). And the N-G bond ("main bonding jumper") is at the service disconnect. That is code compliant, but seems a bit odd to me. Like ferinstance if you had a neutral connection failure on the neutral from the meter to the disconnect it wouldn't be too healthy. Comment?

(I have never seen one done that way, but basements are very common here.)

Minneapolis still has a municipal metal water system. If the GEC (including water pipe) is connected at the panel, and the service neutral opens at any point, the neutral current will be to the water pipe, to other houses, and back to the service neutral. The neutral voltage shouldn't float much.

Reply to
bud--

The NEC can be much more complicated than the picture. For instance in new construction a Ufer ground is usually installed, which replaces the ground rods (which are a POS).

Yes

Yes [to the water meter]

It is. The connection to the water pipe near the panel is likely the connection that was made before the service was upgraded, and was just easily connected to the new panel. Connection at that point used to be kosher. Them pex guys are ruining the world.

>
Reply to
bud--

Thanks, Bud!

I will tell my neighbor that he doesn't have to worry about the service grounding situation. The owner of the company whose worker paired up the circuit grounds and neutrals under the same lugs is coming out next week to fix that situation.

If I have the time, I want to be there when he does the work and have my neighbor ask him about the service ground. I just want to hear what he has to say.

Thanks again.

Reply to
DerbyDad03

HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.