Code question for 240V line

I currently have a receptacle that has two 125V lines (both connect to the same breaker). I would like to convert this to 240V. My plan is to replace the single pole breaker with a 240V breaker and replace the receptacle with the proper 240V one. My questions are:

1) Does NEC allow 240V and 120V in the same conduit? The current conduit is fed from a sub panel. The existing wire feeds a single receptacle located on a dock.

2) The current wire is 12 awg (black, red, white, ground). I know code allows for 20 amps at 120V. Am I correct that I can use this for 20 amp at 240V.

Thanks.

Reply to
noname87
Loading thread data ...

Yes and Yes, In fact you could split this out in a multiwire circuit and have two 120s and a 240 out there. You just need to put GFCIs on the 120s after you split them out.

Reply to
gfretwell

How do you think you get 240 V? It is two 120 V circuits with the

120V in one circuit 180 degrees out of phase with the 120V in the other circuit. Look at it as a 240 V circuit center-tapped, with the center tap being the neutral/at ground potential.
Reply to
hrhofmann

I have 240V at the sub panel. By using the right breaker, I can access both 120V lines to get 240V.

Reply to
noname87