Hello, 'bout a year or so ago found a method for calculating required SH. (WB*3-80-ambient)/2. WB was at the evap. intake; ambient was outside. Found at hvactalk.com; site is totally revamped and can't research it anymore. Any thoughts??? TIA, Barrie
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Fri, 11 Mar 2005 14:18:01 -0800, "Barrie Hiern"

    Happy floodback :-)
    BTW, I see NO WAY that theory can work. It makes NO allowance for system capacity, loads, what refer is in use, SHR, and a host of other things.
    To start with, you're mixing apples and oranges right off the top - RA WB vs OA DB. The relationship between the two is very complex, very building-specific, very load-specific, very system specific, and can not be assumed in any simplistic formulae.
    You make no allowance for envelope insulation or internal loads, even is we assume that you're trying to effectively derive 'load' from the ambient, which is impossible.
    Then, we must assume you propose to vary SH as a means of reacting to load. But you don't have load data in the equatino ( you can not simply assume it from WB ! )
    Unless you propose an electrically variable TXV or HGB, then this can not be a control strategy, only a charging strategy. As such, it don't work. In fact, as ANYTHING, it don't work.
    Basically, you have the SH equivalent of '1 ton per 400 sq ft' in load calcs, if even that much.
<Trump Moment>
    You're fired.
< /Trump Moment >
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Barrie I have superheat charts for Trane, Heil, Carrier, Goodman. All but Goodman use ID wet bulb & outdoor dry bulb. Goodman uses ID & OD drybulb. I also have a program on my calculator for Carrier & Trane. Your formula matches my Trane program, at least on the first few tries. I will try to dig the formulas out of the calculator and post them. email me at sixfoot7 @ sccoast . net with a fax # & I will fax the charts to you. Remove spaces from email address. you can call me at 843-385-2220.
Stretch
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

    I'd be interested to see a post of those. Is that ALL they consider, OA DB and RA WB ? Nothing else ?
    I understand how a manufacturer, for a piece of equipment they designed, can have such charts / formulae ** for that piece of equipment **, but I don't see how there can be 'one formula' for ALL equipment.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
'scuse me but you might want to check the Rheem/RUUD charts..... ID dry bulb within a degree or 2 of comfort level, SP converted to ST vs actual ST should = a 15 - 20 degree deltaT Just keep the SP above 58 PSI or you will freeze.

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Found
Yea, why not research 'superheat' and learn the correct proceedures?
kjpro
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Fri, 11 Mar 2005 14:18:01 -0800, "Barrie Hiern"

RA 72 DB / 50 RH , WB = 60 , OA 95 ( hot normal day ) (60 * 3) = 180 180 - 80 - 95 = 5 5 / 2 = 2.5 degree SH ???? I don't think so !!!!! You're gonna have floodback !!!
RA 72 DB / 80 RH , WB = 67 , OA 70 ( cool rainy day, lots of building leakage ) ( 67 * 3) = 201 201 - 80 - 70 = 51 51 / 2 = 25.5 SH ???? I don't think so !!!!! ( this implies running a MUCH warmer coil, which is the WORST thing to do in this condition ! )
RA 72 DB / 30 RH , WB = 54 , OA 80 ( warm dry day ) ( 54 * 3) = 162 162 - 80 - 80 = 2 2 / 2 = 1 SH ???? I don't think so !!!!!
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Fri, 11 Mar 2005 23:48:16 GMT, pjm@see_my_sig_for_address.com wrote:

Take this same day, assume the power has been off and it's mid afternoon. So, the DB inside is up, but specific humidity hasn't changed, @ 58.6 grains ( same as it was in the above )
DB 90, grains 58.6, WB = 66 ( RH 28 % ) ( OA still 95, as above )
66 * 3 = 198
198 - 80 - 95 = 23
23 / 2 = 11.5 degrees of SH, under this max-load hot-startup extreme condition ??? Sorry, no way. That's like half or less of the SH you would expect.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
The charts I have are manufacturer data. Carrier is different than trane, york, heil etc. stese superheat charts work only for charging systems with pistons or cap tubes, not TXVs. Before you put them down, contact the manufacturer and ask for their charging charts. That is what these are, charts for verifying correct charge in COOLING. Won't work for heat. Carrier & Trane have slide rules with data on them. Others use tabular data that can be graphed The Trane data can be worked into a formula. What do you guys do when you service a unit? Pull all the refrigerant out every time and weigh in a new charge? If you do that on every tuneup - Ho Boy!!! Expensive and time consuming!
Stretch sixfoot7 @ sccoast . net remove spaces to email
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

    Yep.
    I wasn't putting them down, I was just saying there is no 'universal formula'. And the one posted here before doesn't work, IMO.

    Hell no.

    Unit charging chart, of course, if available. Otherwise, you gotta pick a SH that seems reasonable and do it.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

TXV systems superheat is only a cursory check just to make sure the TXV is working. The correct charging method for a TXV system is sub-cooling.

ANd still others have a charging chart for heating mode

Not hardley

Superheat and sub-cooling is so much easier

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Method for charging cap tube or piston metering device systems using suction superheat (Phew! What a title!)
Enter the chart (or formula) with indoor wet bulb and outdoor dry bulb temperatures. The formula or the intersection on the chart or will yield a superheat in degrees. Allow the system to run at least 10 minutes for conditions to stabilize. Measure the suction superheat at the suction service port using charging gauges and an accurate thermometer. If the measured superheat is above the value on the chart (or formula), add refrigerant. If the measured superheat is below the value on the chart (or formula), remove refrigerant. If the required superheat is below five degrees, add refrigerant if needed till the superheat is exactly five degrees, then stop. This is to prevent flood back. NOTE: in extreme conditions, required superheat will be zero degrees. See previous sentences.
Indoor wet bulb converts to enthalpy, or total heat in the air. As wet bulb increases, load increases and superheat goes up. Outdoor dry bulb determines head pressure to a large extent. As outdoor dry bulb increases, head pressure goes up & pushes more refrigerant through fixed restrictor; superheat goes down. These conditions create relationships that interact in predictable ways. This information can be used by the manufacturers to create charging charts and tables.
I have been using this method since I first heard about it at a Trane training class. It really works! I developed the formula by reverse engineering the graph Trane provided.
Note: Wy minus Indoor Wet Bulb Temperature
Formula for 10 SEER & Below Trane: (-1*(.4+(W*0.0178))* OD Dry Bulb) + 72 = suction superheat
Formula for 11 SEER & Above Trane: (-1*(.3166+(W*0.016))* OD Dry Bulb) + 62.5 = suction superheat
Formula for Trane Packaged Units: (-1*(.4+(W*0.0176))* OD Dry Bulb) + 71 = suction superheat
I will try to dig out the Carrier formula. It is not as accurate, but is mostly within 1 degree of Carrier's tables. I have these formulas programmed into my graphing calculators to make checking charge easier. Note that I have to use charts or tables for Rheem/Ruud, York, Goodman & Heil. I have no formulas for those brands. I don't know how to post the charts, I can only FAX them & some of them are slightly smudged.
Stretch
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Buy Gary Lloyds books and through all those charts away.
Rich

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
wrote:

    If you have them in a computer format, email them to me, I can online put them :-)
    Writing I may not know good, but online putting I am well at :-)
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
I printed them using a DOS CAD program called Generic CADD. It does not work on my new machines and printers. I will try to send you a scanned JPEG.
Stretch
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

    Tks, I look forward to them. Yeh, G-CADD was cool, in its day, for sure :-) I think it's still around, but costs an arm and a ball, and won't read old files anyway, probably.
    I still can't swallow that 'charge a system to 1 SH when the return air is 90' one. I think there have got to be limits stated on the charts having to do with 'when system is settled down to normal operating range.'
    IMO, if you crank a 1 SH when the return is 90, you will guaranteed flood from over charge when it's 72.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
I need your email address to send a .JPG file with one of the superheat charts. If it works, I will send the rest.
Stretch Kevin O'Neill 843-385-2220 O'Neill Bagwell Cooling & Heating sixfoot7 @ sccoast . net
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

     snipped-for-privacy@pobox.com
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
For some reason tht beginning of your address shows up as p...@ - if you put spaces around the @ and the dot I can read the address, otherwise I can't. Please send it again, Thanks. Or call me at 843-385-2220. Kevin O'Neill (stretch)
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

p j m at pobox dot com
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Related Threads

    HomeOwnersHub.com is a website for homeowners and building and maintenance pros. It is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.