Wireless motorized valve controllers ?

Jan 23, 2006 23 Replies

No, it has never tripped on me.

The setting is at about 9 o'clock on the dial which is pretty low. Even then the boiler cycling is quite bad (off for about 40 seconds, on for about two minutes continuously). When I set the thermostat higher than this the cycling is even worse. It is the cycling that has led me to consider taking action to get the system properly set up.

Thanks. I don't feel sufficiently competent to start messing around at this, but I appreciate being informed about how it should be expected to work :)

Cycling occurs when the rate at which your boiler is producing heat is greater than the rate at which the radiators and HW cylinder coil can dissipate it. It should cycle *less* if you turn up the boiler stat because with the radiators being hotter, they can dissipate more heat. Have you tried increasing the pump speed?

If the boiler *still* cycles excessively when the house is hot enough in the coldest weather, it sounds as if it's too big for the job. You can probably reduce the boiler output a bit by reducing the gas pressure. This will be explained in the installation manual.

Actually, re-reading what you wrote above - indicating that the boiler is firing for 120 seconds in every 160 (i.e. 75% of the time) I wouldn't worry about it if it only does it in steady state conditions. [I would expect the boiler to run continuously for much longer than that when first starting up from cold - does it?]

I haven't tried messing with the pump speed (was concerned that this might cause overflow into the header tank?) but I may experiment based on your advice.

I will have a go at turning the thermostat up and measure the rate at which cycling occurs. To be honest with you, I am not long moved into the house and I'm still trying to find my feet regarding which radiators to leave on or off while the system is running, and how long to run the timer for. I'm in Northern Ireland and we pay stupendous amounts for gas over here, so it's about trying to get a balance between heating the place sufficiently and not getting an insane gas bill ;)

The boiler burns continuously for about 45 minutes from cold before it enters the state where the cycling occurs. After this time I've got a full cylinder of nicely hot water.

That sounds perfectly normal to me - and certainly nothing to worry about.