To insulate or not to insulate, under tiles that is the question!

Situation: Basement floor, 175mm reinforced concrete over hardcore on clay but ~2m underground. I want to put travertine tiles (12mm) over electric underfloor heating for comfort in the winter and primary heating in the summer when the rest of the house is warm anyway.

The U-value calculator say's given the area and perimeter that U-value excluding floor coverings is 0.67. Manufacturers of insulated tile backing board (marmox etc.) say that even with 6mm of insulation under the heating elements I will feel the benefit of quicker warm-up and lower running costs. The U-value calculator says that with 6mm of insulation the overall U-value is ~0.63 i.e. not very different.

Since the heat-loss from the room is largely unchanged I can't believe the argument about reduced running costs is true? Certainly a gain of

0=2E04 in U-value doesn't justify the =A3400 cost of the insulation. Is there something I'm missing?

On warm-up time surely 12mm thick tiles will still heat up faster than the 175mm concrete so even in the warm-up phase the effect of the 6mm insulation will be pretty much nothing. Again am I missing something, apart from the desire to get the cost down?

I accept that if I had 50mm of insulation it would make a difference, but this is a basement with finished headroom of 6'6" so I don't have space to play with.

Should I spend less money (since it's cheaper) on a bit more wall insulation to keep the overall heat loss down?

Advice welcomed.

Fash

Reply to
Fash
Loading thread data ...

Personally, I'm not sure you really have space to install it as is. You definitely need the 6mm, and you really need the 50mm. Would it be possible to dig out the floor and reinstall something more suitable with DPM (you don't mention one) and 50mm of kingspan? You could even install wet underfloor, then, which will be much more efficient.

Remember that because the heating is buried in the floor, you get direct conduction of that expensive and environmentally unfriendly electric heat right into the ground, so the u-Value is much more significant than a standard floor, which is unlikely to be excessively problematic even uninsulated.

Christian.

Reply to
Christian McArdle

Sopudns about rioght. You don';t want 6mm of exep-snice crap, you want

60mm of expensive insulation. Polystyrene, or best of all Celotex or kingspan.

The rugs that you pit down on the tiles for one..the sofa that you sit on for another..I've got UFH and UNDER THE SOFA its about 10 degrees warmer than UNDER THE RUG which is 5 degrees warmer than OVER THE LAMINATE which is 5 degrees cooler than the tiled parts...

The amount of energy that goies down3wards relative to the amount that gies uopwards and is useful, is entirely down to the relative U values in each direction. A big sofa on a rug is a pretty good insulator. To get te heat to sone up you have to stop it going down.

Then get digging. For my money, putting in UFH with any less is a waste of your time and your money.

With building regs forcing the walls to be about 0.1-0.3 U valuse, 0.63 is going to soak away about 70% of the heat before it even gets into the room.

And with electricity at 13p a unit or whatever, thats a damned expensive way of making the earthworms cosy.

No. Either do the job properly and excavate and fit 50mm+ insulation, or scrap the idea of UFH and tiles, and fit a THICK carpet and some radiators.

I am the biggest fan of UFH there is, but the underfloor insulation on a ground touching floor is MANDATORY - its not an option, its part of the whole job.

Reply to
The Natural Philosopher

We are definitely singing from the same hymn sheet here, Christian.

I've got 50mm polystyrene, and if I did it again I'd use 70mm celotex.

My problem is a suspended concrete floor with an icy draught underneath... I may block up the vents once the BCO has buggered off - well some of them anyway.;-)

Reply to
The Natural Philosopher

The message from The Natural Philosopher contains these words:

I'd agree. I honestly think the whole idea of UHF without a really thick layer of insulation is misguided. I've used 100mm poly under the conservatory floor.

Reply to
Guy King

Digging down further is NOT an option. Not because I'm lazy (I already dug it down 500mm over a 25m2 area. It's an old house and the cellar walls don't reach floor level. The structural engineer proposed a reinforced bath-tub as earth retaining but didn't want me to dig down more than absolutely necessary due to the undermining effect on the house (which didn't fall down so that was good!).

Anyway I don't expect there's many volunteers to come and dig up 175mm concrete with A142 mesh in it.

I'm still not convinced by the figures. Google it and you'll see that large concrete floors don't require under slab insulation as perimeter effects dominate heat loss. I accept mine's not big enough for that to be the case but if you do the calculations adding 50mm of underslab heating reduces U value to 0.3, which given the loss through the walls isn't significant. I'm not subect to building regs part L a) it's existing and b) it's listed and they accept that part L standards can't always be achieved in a manner sympathetic to the aesthetics of the building and can cause real damage to the fabric by messing around with moisture equilibrium levels.

To be honest compared to the rest of the house it's the best insulated room because the ground has an effective insulation value particularly in cold weather as it's always at ~12C once you get more than a meter below. The u-value calculator I used had special settings for basement floors and walls including data on average ground temperatures across the UK. I accept that warm-up is based on relative u-value above and below the heating, but that's why I don't think 6mm insulation makes any difference since it doesn't significantly shift the u-value below the heating elements

I also stick with the argument that when the room is at a steady temperature the heat-loss calculations are valid for underfloor heating as for rads, if not why not?

If we take the finances. If you believe (and feel free to argue, but I want to know your theory not just an insulation is good mantra!) that heat loss is the same, and it's just warm-up time, let's work it out:

Additional cost for insulating (excluding the social effect of reduced headroom) is =A3400 if I use 6mm Marmox. At the quoted 13p/kWh (incidentally I'm paying 10p) this represents 3076kWh. Total heat loss from the room is 1700W (assuming no additional wall insulation) and output from UFH is 2000W. If it takes an extra hour to warm-up then this is 1500 days running, which is a minimum 5 yr payback time based on expected usage. However since heatloss is unaffected and the floor acts as a better storage heater without the insulation I should be able to turn the heating off 0.5 hrs earlier increasing the payback time to

10 yrs MINIMUM.

By the way I have radiators in the room anyway as I said in the first post as primary heating in the winter, the UFH is just to stop the little ones from getting cold toes since it's their playroom. For the radiators I'm absolutely convinced that the only consideration is the total U-value of the surfaces, floor and walls.

What I really want you all to explain is how the extra heat gets out given that the U-value doesn't change with the addition of the 6mm insulation.

Come on take up the challenge show (not tell) me how I'm wrong because I don't see it in the posts so far.

Fash

Reply to
Fash

Oh yes, of course there's a DPM, what do you think I am?

Fash

Reply to
Fash

For those interested in facts not hearsay take a look at . This states clearly in the intro that insulation is NOT required for all ground contact floors. For my basement at 2m depth 0.8 perimeter/area ratio, floor value from the table is 0.56 and walls are

0.58 (R=0.5) for no insulation. This is pretty close to what the u-value calculator said.

Fash

Reply to
Fash

I know all that..been there dome that etc. However for that to be effective - using soil as an insulator effectively - you need a LONG time to build up temps.

Because the UFH is not *at* room temp., Its a lot higher..say 30Deg C. so more heat gets lost before the room even gets warm. Your heating element is always ABOVE room temp and the colder walls are always below. You are placing the heating element directly against the cold wall..with no air between. Now if transfer from floor to room is good, thats not such a big issue, but if the floor is actually masked from the room by insulation - carpets/sofas even a dog lying on the floor - its like having a heating element halfway outside the house. The temp locally rises, so heatloss to te outdie imncreases..but the heat transfer into the room falls.

IN terms of heat output inside the house, to heat output inside the house, teh ratio is simply the localised U values. Any obstructions on the floor make UFH worse. whereas in a conventional system they make it better. UFH under a carpet is like hanging curtains over your radiators. They get hot and most of the heat goes outwards.

Look, in the end its your choice, but don't be misled by a simplistic interpreation of the maths.

I certainly agree that 6mm insulation is a total waste of money..What concerns me is that the whole UFH without the underfloor insulation - down to 0.1- 0.2 U value - that is what I think is ideal, may also be a waste of money.

Which will vary depending on the wind, the draughts, the ventilation, the curtains, the carpets and the furniture.

We have single glazing. With a room temp of about 22C the curtains - doubled lined with thermal lining - allow frost to form inside teh windows at -5C outside..the air space is about 7-8C estimated behind the curtains...so U value of window from building regs book about 3-4..u value of curtains with airspace behind, about .8...?

Drawing the curtains probably halves the heat loss from the rooms with the french windows in.

However, if all you want to do is shove in a bit of warm to stop a tiled floor feeling icy, then none of this is relevant. Just don't expect the heatloss calcs to actually be the complete picture.

We have an aga running in a slated floor kitchen. Its enough - because we have 50mm insulation under - without the UFH being on - to make the floor warm.

Think on't....

I never said that. I said that less than 50mm was useless, and that UFH as a primary heat source without insulation of at least that underneath was hugely uneconomic.

Why does the FLOOR feel cold right NOW with the room being warm?

Because its at a lower temp then the room?

If now its at a higher temp than the room, is it not concievable that MORE heat will be lost through it than is currently the case?

Reply to
The Natural Philosopher

Why not just sheet the entire floor with 25mm of jablite (p-styrene) which is cheap as chips, then lay a thin sheet of plywood prior to installing UFH? - if you doubt the efficiacy of just one inch of insulation, I can safely say that I now own two 4ft glass aquariums with cracks running along the bottom of both (6mm glass BTW) from putting 20W heatmats on top of 25mm jablite with the aquariums on top, prior to this they were sat on solid timber with the heatmats below the glass and got barely warm, with the jablite I could fry eggs on them, and the snakes were none too pleased neither.

Reply to
Phil L

If it's for little ones maybe you could afford to lose some height :-)

Obviously this won't work if you do have underfloor heating, but it would be quite easy to provide a raised insulated "decking" area to play on; with balustrades and walls it would convert into a "wendy" house / den / fort / whatever.

Cork tiles/sheet is fairly warm to the touch even when laid on unheated concrete, and is also fairly resilient. Plates bounce off it, so I daresay heads would too.

Owain

Reply to
Owain

Because my tallest friend is 6'5.5" so he'd smack his head on the ceiling if I lower it an inch!

I'm going to stick with no insulation since duty cycle on the UFH will be low given that the rads are the primary heat source anyway.

Good explanations from the Natural Philosopher. There won't be too much furniture to soak up heat since it's a playroom so that won't be too much of an issue. There is of course the issue of cashflow to consider, which comes down to the fact that I haven't got the money for it anyway!

Fash

Reply to
Fash

What you haven't calculated, and for which there are no tables that you can use is that cold strikes upwards from the floor, and being in a cellar, the walls too, you seem to have talked yourself into having no insulation despite everyone here telling you that you'll need it....no one is going to agree with you because I think everyone here knows that come December, this basement is going to be uninhabitable at night time, and certainly most of the daytime too if we get a cold spell but it's up to you in the long run

Reply to
Phil L

Believe what you want.

If you aren't going to listen, why bother posting here at all?

Reply to
The Natural Philosopher

The only comments that I could add is that the earth should be somewhat warmer at 2m depth anyway. I now that some caves are a constant temp all year round due to there depth and mass. Certainely in the past we were workig on some old cottages in the winter. We could not find a room anywhere that we could heat a little for breaks. We uncovered an old cellar and cleared it out. That would warm up quicker than any room in the house but the moisture from the kettle wouldn't go anywhere!

Regards Legin

Reply to
legin

It wasn't clear if the floor was new or old when I asked the question.

Christian.

Reply to
Christian McArdle

The problem is not with having the floor insulated for general u-Value reasons. As you have found out, floor insulation is rarely that critical. The problem is burying the underfloor heating in it. Because the floor is now hot, rather than the 21C to about 10C temperature difference, it is coping with something like 30 or 40C to 10C, so the heat loss could be three times as much. Coupled with the fact that it is electric, I would say that underfloor heating is not appropriate. Have you considered a different heating method?

Christian.

Reply to
Christian McArdle

Which cold is this that STRIKES from the floor. Average temperature

1.7m below ground in the UK varies between 10C and 16C. So in the coldest month which is January not December the situation is that you have a room where the equivalent outside temperature is 10C and there are no windchill factors (since it's not very windy underground), so in fact there's very little difference in the temperature in the basement all year round. Which has the great advantage that it stays cool in the hottest days of summer and is NOT uninhabitable in the coldest days of winter.

Anyway I'm not talking about no insulation, I'm talking about doing it where practical so I will be putting some insulation behind the dry-lining but not so much that I generate lots of condensation.

Reconsider the comparison to the rest of the house. Uninsulated u-values for the basement are ~0.6 all round. Elsewhere given solid stone walls the average wall u-value is >2 so it's there where I'm pouring heat out of the house to try and warm the town (and of course the planet). If you're right about the basement being uninhabitable in winter (which of course you aren't) then I should probably abandon the whole house to the rats since you clearly think it's not a viable proposition!

This group is really good on practical issues but seems to fall over at least a little (don't want to be too rude) when it comes to theoretical analysis. Maybe I should try alt.climatechange or something like that, maybe theres even an alt.thermodynamics group!

Fash

Reply to
Fash

Insulation helps prevent condensation. It doesn't cause it.

If you propose an ELECTRIC underfloor heating system with no insulation in alt.climatechange, if such a group exists, you are likely to be firebombed by environmental activists.

Remember in your calculations that your basement floor is (a) at a much elevated temperature and (b) loses two airsolid interfaces. It is solid throughout, enabling straight conduction all the way through without having to swap from solid to air, which provides considerable insulation in its own right. Typically in an uninsulated floor situation, the floor surface temperature itself is significantly lower than the room temperature, further reducing actual heat loss.

Christian.

Reply to
Christian McArdle

You're probably right about alt.climatechange! So with your sensible advice Christian can I make a summary of the sensible points.

  1. For efficient heating of the space overall I should stick with radiators since these are running on gas anyway, therefore I'm producing less carbon if I run uninsulated on rads rather than pretty well insulated on the electric UFH.

---This is OK and what I plan to do anyway

  1. If I stick with putting in the UFH for comfort heating then I am wasting my money with the 6mm insulation, since most heat comes from the rads so payback on the insulation is somewhere well over the horizon, probably beyond the lifetime of the installation.

---This is OK since I don't have the money or the headroom.

  1. For control of the UFH I should use the floor temperature sensor and set it as low as possible (say 20C) to keep the duy cycle to minimum so it just does the job of keeping the floor at a comfortable temperature.

Are there any other points I'm missing.

One more area of interest.

The issue with insulating the walls is that it moves the point where the condensation is generated. Basically uninsulated any condensation forms on the inside walls of the basement. If I insulate it then forms on the inside surface of the wall membrane. This is why I didn't follow the installation advice for the cavity membrane installation. The floor membrane laps up the walls inside the wall membrane to ensure that water from the walls (and there is some) drains behind the floor membrane and ends up in my sub-floor drainage which is pumped away. They recommend sealing the floor wall joint with waterproof tape. I couldn't see the point since the top of the membrane is unsealed and so water vapour can escape at the top anyway (dealt with by heat-recovery ventilation and dehumidifier if necessary). My thinking was that if I don't seal the joint then any condensation which forms on the inside of the wall membrane should (on the whole) run down the gap between the wall and floor membrane and so end up in the drainage system rather than on the floor or at the base of dry-lining.

Does this seem sensible. If I'm going to seal the joint now would be the time as I've put up the stud framework (inside the membrane) but haven't boarded it yet.

It's been a fun thread!

Fash