Hi,
Only two years after my original posting I'm finally getting round to running a supply from the CU (20 amp type B mcb, rcd protected) to the shed. If any of you have long enough memories my current plan is much the same except I'm taking the cable run from the front of the house into the loft, where I'm going to change from 4mm T&E (8m) to 4mm SWA (I was going to use 2 core but could only get three so I'll use the third as an additional earth) using a metal clad socket to join the two.The run then goes down the back of the house and onto the shed (ca 20m swa). The intent is to import the earth from the house to the shed (dry no water pipes etc.) The circuit is longer than I originally said but the disconnect time/voltage drop is still OK.
It occurred to me that I could cut into the swa at the back of the house and install an IP rated outdoor socket (which is plastic). What I'm not sure about is how to utilise the earth tags that come with the gland. From what I can gather they are normaly installed on the outside of the patress/box and a hole drilled into the box, with bolt& crimp ring terminal. In the case of the socket I obtained there isn't actually any room to do this. Is there any reason why I can't bend the tags and put them on the inside of the sockets enclosure? In some respects this question is academic as the armour would be eathed via the 3rd core and the metal clad fcu in the shed, but I doubt good practice.
Also am I correct in assuming that the earth tags don't need to be used with metal clad sockets etc.
Thanks
Jim
Thanks
Jim