That means very few bathroom would ever have them fitted.

Reply to
Doctor Drivel
Loading thread data ...

What are you saying?

Reply to
Doctor Drivel

That RCBOs are not well suited to protecting lighting circuits anyway for obvious reasons.

Reply to
Andy Hall

And these obvious reasons are ... [not obvious to me]?

Reply to
Andy Wade

Gasp! an echo!

Reply to
Doctor Drivel

State it twice and it becomes obvious.

Reply to
Doctor Drivel

The smallest trip current RCBOs commonly available are 16A ones. This exceeds the current carrying capacity of 1mm^2 T&E, and also the rating of many lamp fittings. Hence you would needs additional fusing etc. THis kind of defeats the point of the RCBO.

A 30mA trip RCD spur on a conventionally protected 6A lighting circuit is a more elegant solution at little (say £15 - £20) extra cost. As someone else highlighted you will save that on not needing to EQ bond the bathroom.

For bathrooms that have other higher current using appliances (wall heaters etc), then the RCBO solution may be workable with a RCBO protecting the higher capacity circuit and a FCU used to feed the lighting circuits.

Reply to
John Rumm

The 17th will say that RCD on all bathroom lights, unless way high. So just having the lights on an FCU will not comply.

Reply to
Doctor Drivel

? - There's no problem finding 6 A and 10 A RCBOs. E.g. MK Sentry range

6932s: RCBO B6 / 30 mA, 230 V, single pole, solid neutral, M6, Cat 3.
Reply to
Andy Wade

Which is why I said *commonly* available. Most places don't seem to carry anything below 10A, and even those are not always available (16A often being the smallest that many offer). Even TLC only have a couple of 10A choices and no 6A ones.

(RS do them, if you don't mind taking out a second mortgage to buy them!)

Obviously this will change with demand, but compared to the half cost option of a local RCD spur without the need for a dedicated cable run, I can't see the RCBO option catching on for installations that just require one room with RCD protected lighting.

Reply to
John Rumm

Yes it would, if the circuit has a RCBO at the head end.

e.g. Bathroom has a 16A radial circuit to feed a wall mounted fan heater. This could be protected at the CU with a 16A type B/30mA trip RCBO, and then the bathroom lighting could be powered via a 5A FCU on the same radial.

Reply to
John Rumm

The 17th. The bathroom is easy enough, have RCD protection on all electrical fitting in the bathroom and equipotent bonding is not required. How does the 17th address equipotential bonding/RCD in the kitchen?

Reply to
Doctor Drivel

It's easy when you say it properly isn't it?

Reply to
Doctor Drivel

Which is fine if you have a MK CU.

Most people have what the electrician fitted.

Adam

Reply to
ARWadsworth

What are you on about?

Reply to
John Rumm

yes, we were discussing the detail of implementation, not the broad concepts.

Same as 16th mostly. EQ bonding is not required in a kitchen as before.

RCD protection on general purpose socket circuits. Any non protected sockets need to be specifically labelled.

(with the 16th edition the RCD protection of the sockets was not a requirement unless there was a likelihood they may be used to power portable equipment outside. However it was common practice to protect them thus anyway, and in many cases there was a good probability they would be used for powering appliances outside so it was often a requirement)

Reply to
John Rumm

RS also list a few other makes like Siemens and Merlin Gerin which do not seem to be that commonly used. There was a Hager one mind you (still at £65 though!)

Reply to
John Rumm

This is not just an RCBO. This is a Hager RCBO sold by RS ...

Owain

Reply to
Owain

That's what he said! There something wrong with the Jocks today.

Reply to
Doctor Drivel

Individually selected for freshness, and hand wrapped in an organic box by nubile virgins....

(which when you compare to the bog standard Hager RCDs at £12, and MCBs at £6 (admittedly lobbed into a box by a bloke called Dave in Basidon) does make you wonder).