I am confused about this. I have a 2kW heater wired in to a timer. I want to add a frost protection thermostat, which will (obviously) have to get its live supply before the (fused, isolateble) timer. The chosen 1.5mm cable for the thermostat only adds about 300mOhms so is ok for fault protection. But, looking at overload current, does it have to be rated for the full MCB current of 16A, or only for the heater current of about 6A?
Given this is a dedicated hard wired installation by the sounds of it, then you while you *must* have fault protection, you could argue you don't have to have overload protection at all since there is no way an unskilled user can plug in extra load to make overload a realistic possibility[1]. (and you can assume that an installer changing a hard wired heater would do the necessary checks to make sure they will not overload the supply cables and switchgear etc).
To answer the specific question, overload protection needs to be set at a level higher than the nominal circuit demand, but low enough to protect the circuit (inc cables and switches etc). Generally if the appliance itself needs tighter protection it will include it internally itself[2], or its installation manual will include explicit instructions on supply protection.
[1] you would also need some assessment of if there a realistic failure mode of the appliance that could make and overload possible, before deciding whether to omit overload protection.
[2] For example, many fan heaters will include a thermal fuse to cut the supply in situations where the fan fails or stalls and the internal temp rises too far.
Apparently 1.5mm is ok for 10A if it is going through insulation (which it might be, I am pulling the new cable fthrough an existing route which might be in cavity wall insulation if there is any). So that seems ok to me subject to your footnotes
Using an oil filled radiator, I assume any realistic high current (but below MCB rapid trip levels) fault would be an earth fault and trip the RCD.
I've seen fan heater elements droop and short circuit part of the element, creating a short-lived IR emitter.
The reason for my question is that I don't want to use two 2.5mm T & E cables, as some of this has to be surface wiring through nearly full mini-trunking.
Is there any scenario where the unit could need to dissipate the whole lot and more to the point will you fuse the lower current bit accordingly. Brian
That will only switch on when the frost stat switches on. Then the timer will run and the heater may not switch on at all if the timer is set to on. It needs to be wired in parallel across the timer so either can turn it on.
If the machine requires an FCU, then you have a problem, you can't simply bypass it with the thermostat. That might be solvable by reducing the MCB/RCBO to 10A, if the mfr says that's ok. But you still need an effective isolating switch.
For historical reasons (not unconnected with Economy 7) the heater is on its own circuit not available on the side of the room the thermostat needs to go. And the thermostat needs a neutral for the anti-hysteresis heater. The sockets in the room and a much used outside socket are on another radial circuit and I hesitate to put the heater on this circuit for maximum load reasons. Though that would be by far the easiest solution!
Roger, you do know that without an extra fused spur or DP switch in front of the frost stat and the heater you are bending the electrical regs by about 90 deg.
But it would be fine if I used the timer and 'stat provided by the heater and plugged it all in to a socket. I was slowly beginning to recognise this. Without the frost thermostat the timer does the isolation and fusing job! Does anyone make a timer with a 'live when not isolated' output? I am fairly sure it would be a bad plan to modify the itmer to get at the switch o/p. An additional FSU does solve all my other problems though! It just looks messy on the wall. I will have to put it below the timer and loop back, for neatness.
HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here.
All logos and trade names are the property of their respective owners.