Is it possible/sensible to use 'standard' mains DIN rail MCBs as protective devices on 12 volt DC systems or would the voltage drop across them be too great?

A small[ish] consumer unit would be a neat solution to use as a distribution box for the 12 volt wiring on our new (to us) boat, much cheaper and easier than a custom solution.

Reply to
tinnews
Loading thread data ...

Generally not a good idea unless the manufacturer specifically says it's OK.

An MCB (as you'll know if you've ever taken one apart) is a complex device and has two operating principles. There is a magnetic part which responds quickly to short circuits and there is a thermal part which responds to small and moderate overloads.

The thermal part will not care whether the current is a.c. or d.c. (which is why thermal circuit breakers are pretty much universally rated rated for both a.c. and d.c.), but the magnetic part is optimised for a.c. short circuits (in particular in respect of arc-quenching) and may not be deemed suitable for d.c.

Consequently, if any given manufacturer does not rate the MCBs for d.c. supplies, I would not recommend that you use them.

===

MK Sentry data sheet does not mention use on d.c. supplies:

formatting link
short link
formatting link
Whereas, ABB are suitable for d.c.:

formatting link
Moeller standard FAZ-type MCB's are good for 48V d.c. Moeller make special MCBs for d.c. upto 250V d.c.

formatting link
(catalogue page 12/13) (actual page 10)

See also catalogue page 12/58 (actual page 54)

===

Hager 10kA-class MCBs don't mention d.c.

formatting link
Merlin Gerin C60-type are suitable for d.c. and give a little treatise on the subject here: (cat. page 166, actual page 6)

formatting link

Reply to
Dave Osborne

You need to check manufacturer's datasheets. Generally, they have a different range of MCB's for DC operation, and both the AC and DC breakers have a minimum operating voltage for reliable tripping.

Reply to
Andrew Gabriel

I've used Polyswitches (polymeric positive temperature coefficient devices) for circuit protection on boats in the past.

Reply to
Peter Parry

Dave Osborne wrote: [snip]

Thanks for the links, so I need to choose manufacturer, no problem there.

No indication of voltage drop though that I can see.

Reply to
tinnews

Shouldn't be a problem. There isn't much voltage drop as the magnetic trip uses a heavy wire coil. The DC current rating will almost certainly stay the same up to 30V. Above that and you get problems as there can be insufficient air gap to break the arc. Check your mcb spec though, you may have to use type D, especially if you have inductive loads.

There are some breakers intended for DC applications though, these are usually thermal releases only and don't give good short circuit protection. Usually low current ratings only.