Can anyone confirm this meets wiring regs please?...

I have rewired my house, and have ran a 4mm earth cable from kitchen sink to fuse board, 4mm from cloakroom sink to fuseboard, 4mm from bathroom taps to fuseboard, and 6mm form boiler to fuseboard. I have also used 10mm from gas supply to fuseboard.

Are these cable sizes ok (they are indepentantly wired, i.e. they do not loop into each other). Also is it ok to do it this way?

Thanks in advance,

Toby.

Reply to
mkkbb
Loading thread data ...

Not required. Actually a bad idea if the pipework is plastic.

Not required. Actually a bad idea if the pipework is plastic.

Not required.

You need to bond all the metal pipework and fittings and earth conductors of circuits in the bathroom together. This is normally done with 4mm cable, but you can use 2.5mm if it is protected from damage. This bonding doesn't need separately connecting back to the main earth terminal and must not be connected back to the main earth terminal instead of connecting to the earth conductors in the circuits locally.

Not required (over and above the earthing in the boiler supply).

However, you should earth the associated pipework unless it's plastic.

That's good. You need to do this with all metalic services into the house (e.g. water, oil) too.

Service bonding should be 10mm. Most of the other bonding you did wasn't required so there is no relevant cable size.

Reply to
Andrew Gabriel

In message , Andrew Gabriel writes

Er.. What is the thinking behind this? Assuming the gas supply to an external meter box is plastic and the consumer side is copper. Are we protecting the meter reader from shock or is there some other purpose?

regards

Reply to
Tim Lamb

Thanks for your reply, however i'm a bit more confused. How should I earth the kitchen and bathroom sink taps. Bond the hot and cold together then run one cable back to fuseboard? I have copper all round the house (only plastic, the blue MDPE pipe, from street). I'm just finding it hard to visualise the actual cable runs.

Toby.

Reply to
mkkbb

On 18 Apr 2007 01:34:45 -0700, mkkbb mused:

Kitchen taps don't need any bonding, as you've been told once already.

You don't appear to understand the basics of supplementary earth bonding, it's not about earthing everything, it's about keeping various zones at the same potential by connecting local pipework together, not to connect every bit of pipe in the whole house together. Maybe buy a book, or actually look into what you're doing

*before* starting a job, especially one where you can end up injuring people, by killing them.
Reply to
Lurch

In article , Lurch writes

You might find this interesting reading....

formatting link

Reply to
tony sayer

On Wed, 18 Apr 2007 10:04:24 +0100, tony sayer mused:

Reply to
Lurch

In article , Lurch writes

No suggestion of getting anything wrong ..just given for general advice and reading!......

Reply to
tony sayer

Clarification here might help the OP (& me too). Oil supply pipe(s) coming into the house are usually 10mm outside diameter.

Standard bonding clamps with the proper regulation stamped tag do not fit pipes

Reply to
jim

On 18 Apr 2007 01:34:45 -0700 someone who may be mkkbb wrote this:-

To add to what the others have said. Copper pipe generally conducts electricity just as well, if not better, than copper cable, as it has a similar, or larger, cross sectional area compared to copper cable.

If there is reliable metal to metal contact along the length of a metal pipe then running a bit of copper covered in green and yellow plastic alongside it adds almost nothing to electrical safety.

Of far more importance is to bridge plastic inserts. For example a plastic water tank may mean some pipes are not earthed properly. This is easily solved by a few clamps and a short length of earth cable.

In rooms containing a bath and shower the aim is to ensure that all pipes and metalwork that may introduce a potential into the room are at the same potential. It doesn't particularly matter what this potential is, so long as there is not a difference between the potential of different pipes. That is what supplementary bonding is for.

This is explained well in the usual books on the subject, which may be borrowed from your local library before starting to do some work.

Reply to
David Hansen

On Wed, 18 Apr 2007 11:18:29 +0100, tony sayer mused:

Right, it's just that as you replied to my post I assumed you were telling me I should read the guide.

Reply to
Lurch

On 18 Apr 2007 05:49:39 -0700, jim mused:

Although I've never looked into small pipe clamp sizes I have found that the cheap clamps are useless on most pipes. I tend to stick to the Tenby clamps as you don't have to tighten the screw up with a huge amount of force to tighten the strap up as you do with the cheap ones.

Reply to
Lurch

One thing not mentioned in terms of bonding is the bonding of the three pipes at the boiler. We had to do that with ours, and I guess it's a general requirement.

Reply to
Bob Eager

On 18 Apr 2007 15:42:35 GMT, "Bob Eager" mused:

Well, I think it was, but that may have been in one of the other 56 bonding threads from this week. I will generally only bond all the pipes at a boiler if it's close to a bathroom or if the existing supplementary and\or equipotential bonding is a bit suspect.

Reply to
Lurch

There is no such rule that I am aware of. As long as the main equipotential bonding is done correctly along with the supplementary bonding in bath/shower rooms why would the boiler need x-bonding? A lot of plumbers ask for this to be done and say CORGI ask fot it doing, but many other CORGI plumbers do not ask for this doing.

Adam

Reply to
ARWadsworth

Fair enough. Our WB 24Ri installation manual explicitly states that it should be so bonded. So I did!

Reply to
Bob Eager

Would be worth doing if the boiler was in the bathroom... ;-)

Reply to
John Rumm

On Wed, 18 Apr 2007 16:09:39 GMT someone who may be "ARWadsworth" wrote this:-

The flow and return pipes of heating systems are amongst those the relevant books indicate should be bonded, along with metal ductwork and a number of other things.

Reply to
David Hansen

In message , tony sayer writes

The reason I am interested is that a recent gas meter change for my Aunt was accompanied by a warning that the installation might not meet the regulations in respect of electrical bonding.

A local electrician has quoted for running 10mm earth cable from the service earth to the gas supply entry point. I have only heard my wife's version of the proposed route so may easily have misunderstood but, with continuous copper gas piping to the meter and plastic beyond: underground, I could not see any benefit to carrying the earth beyond the nearest convenient bonding point (at the boiler).

regards

Reply to
Tim Lamb

Which "relevant books" are those? Or is this like Whitfield claiming that sinks should be bonded?

BS7671 only mentions bonding of CH flow and return pipes in relation to locations containing a bath or shower [601-04-01]

Reply to
John Rumm

HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.