ACL-Drayton mid-position valve

Apr 04, 2012 5 Replies
Saved reading
Jump to replies (5)

Our CH has an original (1996-ish) ACL-Drayton Lifestyle mid-position valve p/n 679H340-30LO, which, unlike later ones, does not have a click-off actuator head.



The head has now failed.



I'd rather not drain down and remove the pipework to replace the 22mm tee + head, so I'm tempted to force the head off one way or another and try to fit a newer-style head which is available separately.



Has anyone tried this?


Never mind - looks like a drain-down and complete replace:-

formatting link

For anyone with an acl-drayton 679H340-30LO valve, ie the old type without the removable actuator, it IS possible to completely disassemble it as follows;

TURN OFF ALL POWER TO THE CENTRAL HEATING IF YOUR NOT SURE HOW TO DO THIS YOU SHOULD NOT READ ANY FURTHER. CONTINUE AT YOUR OWN RISK.

  1. Undo the screw and take off the cover.

  1. to remove the motor there are two screws, ones probably hiding behind the orange wires. remove the screws and pull the motor away from the body with the earth plate and heatsink/cover then carefully unplug the connectors from the circuit board. If you need to replace the motor just plug and screw in your new one.

  2. to remove the circuit board, slide off the white cover, and undo the two small screws that go through the micro switches. You can now remove the circuit board. (If you havent already you'll also need to remove the cable clip).

  1. if you want to go any further, (I didnt), you can remove the actuator bits and springs and there are two screws to remove the actuator body from the valve body. And thats pretty much it.

I replaced the valve motor with one from screw fix and had the exact same problem. So I took the circuit board out to see if anything had burned out. And discovered that both micro switches were faulty.

They both had very dirty contacts and one of them had a bent contact causing it to arc when energised. I cleaned them both up resoldered them to the circuit board plugged it all back together and its all working again.

I tried to repair it, but it was still unreliable. In the end I replaced the entire assembly, which was surprisingly easy, even with the partial drain down. I say replace the whole thing.

In message , Reentrant writes

They do not need forcing,

Many people have

>

Heed the wise words of brother agile

Join the Discussion

Have something to add? Share your thoughts — no account required.

Didn't find your answer?

Ask the community — no account required