I have an older house in which the electric cables to all the switches and receptacles have only 2 wires: one black (hot) and one white (neutral). I would like to upgrade the receptacles to the newer type that have a third opening in them for a ground. I would like to avoid running new cable with three wires (black, white, ground) as this would be a fairly tough job to fish new cable through the walls. The new cable is also pretty expensive.

Is it acceptable to just run a ground wire (either bare or green) from the ground bar in by service panel to the receptacles. In many locations this would be easier than fishing a whole new cable as well as less expensive.

Thanks in advance for any guidance.

Herb

Reply to
Herb S
Loading thread data ...

"install a GFCI receptacle. The ground lug should not be connected to anything, but the GFCI protection itself will serve instead. The GFCI will also protect downstream (possibly also two prong outlets). If you do this to protect downstream outlets, the grounds must not be connected together. Since it wouldn't be connected to a real ground, a wiring fault could energize the cases of 3 prong devices connected to other outlets. Be sure, though, that there aren't indirect ground plug connections, such as via the sheath on BX cable.

The CEC permits you to replace a two prong receptacle with a three prong if you fill the U ground with a non-conducting goop. Like caulking compound. This is not permitted in the NEC.

The NEC requires that three prong receptacles without ground that are protected by GFCI must be labelled as such." this and more at:

formatting link

Reply to
buffalobill

Yes, they are non-metallic.

Reply to
Herb S

Yes, they are non-metallic.

Reply to
Herb S

I haven't got a current code book handy, but unless something has changed.

250-130 (C) (5) says you can

Reply to
RBM

Then, IIRC, you can do as you propose since the cable is nonmetallic. Use Tyraps to secure the equipment grounding wire to the existing cables as much as possible. It's a lot of work. Using GFCI receptacles at the first outlet in each circuit would be a lot easier. All downstream receptacle outlets could then be 3 prong.

Reply to
volts500

You can probably be selective about which ones really need a ground. If you don't use 3 prong plugs there, don't bother. Computers, fridges, washing machines, disposals and microwaves should get the ground.

Reply to
gfretwell

But, that won't do anything for providing an earth connection for computers, surge protectors, etc. although it certainly DOES add in the safety factor for the GFCI lines.