I have added a room to my home and the A/C tech connected a new 7" flex duct to the plenum. Off of that he SAID(??) he connected a 7" wye with 6" reducers. And then off of that he connected a 5" duct dropping into a 64 sq ft. room and a 5" duct dropping into a 77 sq. ft. room This does not add up for me if a 7" carries about 170 CFM and 2, 5" ducts carrying about 70 CFM each. Thats 140 CFM. What happens to the other 30???

Please let me know if this is correct duct design.

Thank You!!!!!!!!

Reply to
barisco
Loading thread data ...

Flow limited by smallest point just like a water hose -- flow will balance to an equilibrium point. The flow ratings of a open-ended duct are based on just that -- add a restriction and the pressure will rise and the flow go down.

If you have adequate but not too much in the new room and still adequate but not too little in the remainng house, it's good enough...

Reply to
dpb

Reply to
barisco

Also, is connecting a 5" duct to a 7" wye with 6" reducer the correct design?

Thanks

dpb wrote:

Reply to
barisco

Sounds fine to me.

Oversize pipe reduce the drag produced by the walls, they don't cause any other problems that I would be concerned with.

Reply to
EXT

What "extra" 30 cfm? There's a fan from the furnace of some capacity

-- larger duct implies lower pressure/velocity. Larger duct size is typical for branch runs to minimize drag loss and possible wind noise but don't want a huge outlet into a small space.

The only real problem as I noted previously I would foresee would be the new duct is sufficiently large as to allow for an excessive diversion from the rest of the house into the new area. You'll soon find out that if the rest of the house isn't getting sufficient cooling. A real pro could measure flows and balance but unless you have a problem in practice is undoubtedly overkill.

Reply to
dpb

If you want your system to work properly, size it according to ACCA Manual D. (Short version below)

Take a measurement of all your fittings and layout on your duct system, then on the back of most ductolator is ?an equivalent length of all the fittings,? to use for figuring the total length of the system.

If using an older gas furnace you have .50 external static available. With newer furnaces look at blower performance chart. Minus the A-Coil, filter, etc.,, and all the other external component pressure drops to your furnace blower performance rating.

Use the formula: Friction = leftover available static X?s 100, divided by total equivalent length, and that is the friction rate for sizing the ductwork.

Depending on a lot of existing, at this point unknown factors, there could be some CFM delivery problem shortfalls in many if not all of the rooms. The ductwork and/or the blower may need upgrading to deliver the proper CFMs.

formatting link

- udarrell

Reply to
udarrell

Why do you suppose a 7" with a 6" reducer was used to connect a 5" duct instead of a 7" with a 5" reducer?