I had my digital volt meter hooked up to two outlets during the day. I noticed that the voltage is normally around 114 volts. When I have my two AC window units on it drops to about 109-112. If I then turn my microwave on it drops to about 102-104. I tested this on two different circuits both on different sides of the breaker panel. This voltage sounds low to me. Is this normal or should I be seeing higher values?
it could be several things. like loose screws in the panel, meter socket, bad connection on the pole,too many services on one transformer,undersized service. try checking your panel connections at the breakers and nuetral bar. then with breakers off check voltage if its still 114v the power company might be willing to up your voltage. i suppose i should recommend you contact an electrician to safely perform some of these things.
Kind of low. The issue now is whether the cause of the voltage drop is inside your house or outside.
Do the test again but this time hook up your meter to the panel on the same phase as the AC and microwave's circuit. It should read 114V. If you can't tell which phase is the right one, then measure both phases.
Then turn on the AC and microwave. What is the voltage? If it also drops to
It sound low to me, and I suspect there is a bad connection somewhere. If you know how to be really careful around high voltage, you could do the following.
Test the voltage at the breaker panel where the wires come in from the meter. Measure on the wires from the meter themselves. If you see the same drop there (Be Cafeful!), call the power company and have them check their lines.
Next, check across the metal buss bars that those wires attach to.
If the last check was OK, but you have drop here, the screws holding the wires coming in probably need to be tightened. If no drop here, check at the output of each breaker, on the metal of the breaker. If you find drop on a breaker, re-seat or replace the breaker.
Then test the wire attached to the breaker, and tighten the wire screw there if this is where the drop occures.
If all the voltages in the breaker box were good, the problem is in one (or more) of the wiring circuits. You need to figure out everything (outlets and lights) on each circuit. Turn off the breaker, and see what doesn't work.
Does every electrical box on the circuit have the problem? If not, you might be able to isolate the problem by guessing what is wired to what. The problem is probably at the last box that tests OK, or the first box that doesn't. Open up each suspect electrical box on the circuit and tighten all connections, then test again..
Maybe. I complained to the power company once. They told me it was impossible to have the variance I was seeing. But it never happened again after that. Coincidence?