Gas Hot Air Furnace / Blower Speed??

Some of us won't use the term "FAG." Nothing personal, mind you....

Oh, your furnace was rated, but the AFUE rating wasn't that well known.

Check your Delta T and see if it can be changed.

Reply to
HeatMan
Loading thread data ...

Heatman - Tell me - Delta T????

Reply to
T.G. Lambach

You will know when you get a mouthful.

Reply to
Oscar_Lives

Tom,

Measure the return air temperature near the furnace with an accurate thermometer. Your thermometer should read degrees and tenths of degrees. Take at least 2 readings and get the average. Write it down.

Measure the supply air temperature near the furnace the same way, Take at least 4 readings and get the average. Make sure all readings are out of direct sight of the heat exchanger. Write that temperature down.

Subtract the return air temperature from the supply air temperature. That is the Temperature Rise or Temperature Difference (TD). Write it down. Get theBTU per hour OUTPUT rating from the furnace data plate. Write it down. Put these numbers in the following formula:

BTUs Output / (1.08 * TD) = CFM

This is the ACTUAL CFM of air flow. Note that each fan speed has a range of air flows. This is called a fan curve. It is usually shown as a graph or a table. For every pressure difference across the furnace, there will be a different air flow even though the blower speed connection has not changet. Each speed connection has a different fan curve. If you use all the fan speed connections and measure the air flows as shown above and plot them over the fan curves, you will get the system curve. The air flow will always be where the system curve crosses the current fan curve. A duct system with a higher resistance will result in a lower air flow. When you increase the resistance, the blower amps will go down! Try measuring the blower amps and partly covering the return with cardboard to demonstrate that.

If you cannot make the measurements and tests I outlined above, DO NOT try changing the blower speed connections. You should be able to measure the results of your efforts if you are going to make any changes.

Hope this helps.

Stretch

Reply to
Stretch

I looked on the ANSI table for the Delta sign, but couldn't find it.

Delta T and Delta P have one thing in common. It (Delta) means difference. Delta T is difference in tmp, Delta P means difference in pressure.

Kinda a head-slap, Homer Simpson "Doh!", huh?

Reply to
HeatMan

Thanks Stretch!

Reply to
T.G. Lambach

HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.