Help...

I have a double breaker labelled as 50 amps that runs from my house to my garage by two 6 gauge stranded wires. It goes to a box in the garage that has 4 15 amp breakers in it, 2 on each leg. Each of the 6 gauge wires connect to each leg in the box. I have a grounding rod 6 feet in the ground as that is a far as it will go, must be rock below it, and the rod is connected to the neutral / common strip in the box.

Is this setup correct? I can measure 125V on each leg to ground, but once I put a load on one of the legs, the voltage drops to 70V and the other leg reads 180V, what is going on here?

Thanks much,

Sean

Reply to
Sean
Loading thread data ...

Not correct. They left a wire out when they ran the cable to the garage. The "ground" rod is not sufficient to act as a Neutral conductor.

Jim

Reply to
Speedy Jim

Hi, Ground or neutral? How many wired do you see coming into garage? Tony

Reply to
Tony Hwang

There are two 6 guage to the garage. They come directly from the dual breaker in the house. Nothing else, so I assume I will need to run another 6 gauge for neutral?

Reply to
Sean

Hi, And ground. Looks like some one half finished the wiring job. Went to lunch break and forgot to come back and finish? Tony

Reply to
Tony Hwang

You need to add two wires; a ground and a neutral. And they all have to run through the same holes in metal. Good example of a floating neutral.

Reply to
Toller

I'm no electrician, and even I can tell this setup ain't kosher. Sounds like somone had a stone-age 2-wire setup for a 240v circuit (2 hots, one from each side of the house panel, using each other as the 'neutral'), to run a welder or something. They then tried to use it for 2 different branch circuits, which as you found, doesn't really work, especially with unbalanced loads.

My advice, and your insurance agent would agree- turned the 50-amp ganged breaker off, and don't use that circuit, until you rewire it all properly. If previous owner would do hillbilly crap like that, who knows what they did where you haven't looked yet? I'd have a pro go over all the house wiring.

aem sends...

Reply to
ameijers

Agreed.... You have a dangerous situation there. The only applications where a neutral would not be present is in situations where only 240 volt appliances were used. But you would still need a hard-wire ground back to your main panel.

Beachcomber

Reply to
Beachcomber

He forgot to install a transformer.

Reply to
PrecisionMachinisT

2 options: Add neutral. Neutral bar at garage connects to ground rod and panel/ground bar (usually a screw in the ground bar). There can be no continuous metal connections from the house to garage.

Add neutral and ground. Neutral bar at garage does not connect to panel/ground bar. Ground wire from house connects to panel/ground bar and ground rod.

bud--

Reply to
Bud--

Wow, to be completely honest with you - if you don't understand this situation straight away, you should hire an electrician.

Your situation requires a relatively simple fix, but asking a NG, when getting it wrong could mean your house may burn down isn't my idea of very smart.