Goodman GMP075-3 Furnace.. LP ..

What consumption rate should this thing have in terms of GPH or similar?

What should the hot air output temp be?

Thanks

Reply to
mpdsville1
Loading thread data ...

What are you trying to do? LOL

It uses 75 Cubic Feet of gas per hour...75,000 btu's Where do you live? Is this thing converted to propane?

Measure your supply temp apprx 6' away from the furnace in the supply plenum.

130F or lower is normal. The temp rise should be roughly 40-70f difference between supply and return air temp. 70f coming in 130f leaving = 60f temp rise.

-Canadian Heat

--

--------------------------------- --- -- - Posted with NewsLeecher v3.8 Final Web @

formatting link
----- ---- -- -

Reply to
Anonymous

One gallon of propane=approx 91,000 btu. Your furnace, if the orifices and gas pressure are correct, will burn 75,000btu/hr. Therefore, it should burn approx .82 gal/hr, or run about 1.2 hr (72minutes) on a gallon. Larry

Reply to
lp13-30

A gallon of LP is 91,500 btu

75, 000 will burn .8196 of a gallon/hr.

This is assuming that the unit is operating under the correct specifications.

The temperature rise should be around 50-55 degrees with a clean filter.

Reply to
<kjpro

hanks to all for the info on burn rate. I learned :

1- Potential Energy for LP is 91k btu/gal. 2- Divide Btu/Hr rating of unit by PE and you get gals/hr 3- Output temp of a furnace isn&#39;t a fixed temp, its the delta between input air temp and output air temp, and that delta should be in the 40

-70 degree range. Output air temp should be measured appx 6&#39; downwind from the unit.

4- Paul hasn&#39;t gotten any. Now, Yet, Likely Ever. Middle-age case of acne driving really BIG pickup. F-350 or Ram3500 I&#39;d bet. A new roll of duct- tape in the glove box awaiting that "special someone".

MPDsville

Reply to
mpdsville1

Thanks to all for the info on burn rate and output temp.

I learned :

0- Oil furnaces have nozzles rated by Gph. With an LP furnace, you do the math. (same for Nat Gas measured CuFt?) 1- Potential Energy for LP is 91k btu/gal. 2- Divide Btu/Hr rating of unit by PE and you get gals/hr 3- Output temp of a furnace isn&#39;t a fixed temp, its the delta between input air temp and output air temp, and that delta should be in the 40 -70 degree range. Output air temp should be measured appx 6&#39; downwind from the unit. 4- Paul hasn&#39;t gotten any. Now, Yet, Likely Ever. Middle age case of acne driving really BIG pickup. F-350 or Ram3500 I&#39;d bet. A new roll of duct-tape in the glove box awaiting that "special someone" no doubt... (Don&#39;t worry Paul, that special someone is out there for you. Just look past the short leg and the harelip. )

Thanks to all for the information, MPDsville

Reply to
mpdsville1

Thanks to all for the info on burn rate and output temp.

I learned :

0- Oil furnaces have nozzles rated by Gph. With an LP furnace, you do the math. (same for Nat Gas measured CuFt?) 1- Potential Energy for LP is 91k btu/gal. 2- Divide Btu/Hr rating of unit by PE and you get gals/hr 3- Output temp of a furnace isn&#39;t a fixed temp, its the delta between input air temp and output air temp, and that delta should be in the 40 -70 degree range. Output air temp should be measured appx 6&#39; downwind from the unit. 4- Paul hasn&#39;t gotten any. Now, Yet, Likely Ever.... (Don&#39;t worry Paul, that special someone is out there for you. Just look past the short leg and the harelip. )

Thanks to all for the > Goodman GMP075-3 Furnace.. LP ..

Reply to
mpdsville1

Not when dealing with Natural gas.

Not on ALL units, some are in the 20-50 degree range. It&#39;s best to check the manufactures specifications!

Reply to
<kjpro

The ratings are required to be on the appliance per AGA.. look near the burner area for the rating plate. The plate will list the allowable air temperature rise, the bonnet capacity, etc.

Reply to