Greetings All!
I am in the process of wiring up a shed in the backyard for use as a workshop. I have a new SquareD load center panel (QO8-16L100S) that I want to use but need some clarification. 1. This particular panel only has one grounding/neutral bar, but I was under the impression the ground and neutral must be separated in a subpanel installed in a stand alone structure. Should I just buy a ground bar and install it in the panel and connect it to a new grounding rod? 2. The panel is rated for 100A, but I was hoping to use a 60A-75A breaker in the main box to feed this subpanel. Is this a problem? The subpanel does not have a main breaker in it. 3. The run from the main panel to the sub will only be about 15 ft. total. What size wire do you suggest I run?
Thanks, Robb
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Check here for guidance on the grounding:
http://www.ecmweb.com/mag/electric_grounding_vs_bonding_5/index.html
I recently called my local building inspector and found him to be very helpful and forthcoming without ever asking for my address.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

I'll defer to others on this one. The conduit should serve as a ground, but some placed might require a separate ground wire.

I did exactly this. It's not a problem since the breaker protects the wire.

Size it to match the breaker you put in the main panel. You'll need something like #8 or #6 for 60 amps. I can't remember what I used. It will be disasterous if you size it too small.
brian
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 19 Apr 2006 08:44:42 -0700, robb snipped-for-privacy@yahoo.com wrote:

Yes and do not install the jumper/green screw that would bond the neutral bar. Run a 4 wire feeder.

That is OK if you have less than 6 breakers in the sub.

4 ga copper is a good choice. That gets you up to 85a The ground wire can be #8 copper up to 100a
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Wed, 19 Apr 2006 12:32:05 -0400, snipped-for-privacy@aol.com wrote:

Should have said 6 or less
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
>That is OK if you have less than 6 breakers in the sub.

How does the number of breakers in the subpanel matter?
brian
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 19 Apr 2006 09:38:44 -0700, brianlanning wrote:

NEC requires a main for more than 6 breakers.
--
Art


Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
snipped-for-privacy@none.invalid wrote:

Cite, please? I thought that was for service entrances, not subpanels.
--
Regards,
Doug Miller (alphageek at milmac dot com)
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Wed, 19 Apr 2006 21:18:15 GMT, Doug Miller wrote:

Hmmm. From my copy of the NEC 2002 Handbook:
230.71(A) "The service disconnecting means for each service permitted by 230.2, or for each set of service-entrance conductors permitted by 230.40, Exception Nos. 1, 3, 4, or 5, shall consist of not more than six switches or sets of circuit breakers ... "
408.16(A) "Each lighting and applicance branch-circuit panelboard shall be individually protected on the supply side by not more than two main circuit breakers or two sets of fuses having a combined rating not greater than that of the panelboard."
"Exception No. 1: Individual protection for a lighting and appliance panelboard shall not be required if the panelboard feeder has overcurrent protection not greater than the rating of the panelboard."
Seems you're correct, Doug.
--
Art


Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Somebody wrote:
>NEC requires a main for more than 6 breakers.
TRUE.
Known in some circles as the "6 hand" rule.
Regardless of whether a panel is a "sub" or a "main", you must be able to disconnect ALL power distributed by that panel in a maximum of 6 motions of the hand.
I seen some very clever schemes used by some contractors in an attempt to avoid a main C/B, but most don't get approved.
Lew
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Coleman 10HP, Contractor type, 5,000 Watt engine-generator located Long Beach.
120/240V output
Boat yard has power so have no further use for it so it's for sale.
Will make a good back up power supply.
SoCal area only.
If interested, contact off list.
Lew
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

FALSE!
I -wanted- a master-cut-off in the main breaker panel in my condo when I was rebuilding the kitchen, and replacing the breaker panel. (went from 14 to 20 circuits, original panel mfr long out of business, had to enclosure, et al.)
City inspector would not allow a 100A breaker at panel feed, because there was 100A breaker (only) panel in utility entry room.
I had, per inspector, choice of: 1) run with *no* 'master-cut-off breaker' in unit. 2) try to find something like a 95A breaker to use as the 'main' in unit. 3) replace (obsolete, mfr out-of-business) breaker at utility entry room with something like 110A,, and use 100A in unit.
"1" was the only 'financially viable' alternative.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Robert Bonomi wrote:
> >>Somebody wrote: >> >> >>>NEC requires a main for more than 6 breakers. >> >> >>TRUE. > > > FALSE! > > >>Known in some circles as the "6 hand" rule. >> >>Regardless of whether a panel is a "sub" or a "main", you must be able >>to disconnect ALL power distributed by that panel in a maximum of 6 >>motions of the hand. > > > I -wanted- a master-cut-off in the main breaker panel in my condo > when I was rebuilding the kitchen, and replacing the breaker panel. > (went from 14 to 20 circuits, original panel mfr long out of business, > had to enclosure, et al.) > > City inspector would not allow a 100A breaker at panel feed, because > there was 100A breaker (only) panel in utility entry room. > > I had, per inspector, choice of: > 1) run with *no* 'master-cut-off breaker' in unit. > 2) try to find something like a 95A breaker to use as the 'main' > in unit. > 3) replace (obsolete, mfr out-of-business) breaker at utility entry > room with something like 110A,, and use 100A in unit. > > "1" was the only 'financially viable' alternative. >
I'm not sure I understand your explanation; however, the "6 hand rule" applies if you are going to comply with NEC.
Got any idea what this "inspector" had for a day job?
Lew
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload


Doing electrical rework, _with_ a city permit, it was specified _by_the_ city_ that I was to use a sub-panel (24 circuit capacity) *WITHOUT* a main breaker in it. Because the main breaker was in the panel in the building utility room.
I _wanted_ a master-cut-off in the sub-panel, but there was no asibleway to do it *and* be code compliant. Since it was _not_ required by code, I ended up going without it.
Note: *NONE* of the 30-plus units in my condo building has a master- cut-off in the 'in unit' sub-panel. All have at least 14 circuits, and it is comparatively 'modern' construction -- circa 35 years old.

"Cite please". It was established in another sub-thread that that 6-breaker max w/o a main cut-off applied to a 'service entrance' panel only. They even quoted the relevant NEC section. Now, the question is, can you back up -your- claim.`
Note: the person posting the NEC section showing 'service entrance' only was someone who had made the same assentation you did, and was admitting he had been wrong.

Yeah, he was the CHIEF ELECTRICAL INSPECTOR for the city, and department head. 25+ years on the job.
He was a 'good guy' -- out of six 'somewhat unconventional' things I wanted to do, he found code interpretations (and provided 'chapter and verse' just- ifications) that let me DO five of them. (Just one of which saved me the cost of at least 2 electricians for a full day, and, incidentally, around $200 in parts.) It was only the master-cut-off that didn't fly. to be 'code compliant', I could go _without_ a master-cut-off in the sub-panel, or I could use one that had to be _smaller_ than the main breaker downstairs. (this required either a 'nonstandard' capacity breaker upstairs, or replacing the one downstairs with a bigger standard value. Neither of those options was financially viable, albeit for different reasons.)
To this day, I don't understand the 'smaller breaker' requirement. If I've got a 100A breaker on each end of a 100+A-capable wire, "at least" one will trip on an overload. There's no safety issue. The inspector agreed with my logic, but said that, nonetheless, the code didn't allow it. So, I went the 'code compliant' -- no main breaker in the sub-panel way. 22 circuits.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Robert Bonomi wrote:
> "Cite please". It was established in another sub-thread that that 6-breaker > max w/o a main cut-off applied to a 'service entrance' panel only. They > even quoted the relevant NEC section. Now, the question is, can you back > up -your- claim.` > > Note: the person posting the NEC section showing 'service entrance' only > was someone who had made the same assentation you did, and was admitting > he had been wrong.
No longer have access to a current code book.
My comment was based on being bloodied from having to work with local inspectors and contractors as a distribution equipment supplier for about 15 years.
Your description of your experience is certainly strange.
Just curious, was the main C/B visible from the distribution pnl in question?
Lew
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Well, if you could see out the door or the condo, across the hall, down three flights of stairs, through the laundry room and into the utility room, then yeah, you could claim it was visible. <grin> Now, I was straight across the hall from the stairwell, the folks at the far end of the floor had a somewhat more obscured line of sight.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
I suspect he is being impacted by local rules. I have used main breaker panels as sub panels when they are located a long ways from the main. I don't usually as cost of a 3 phase 208 volt 200 amp breaker adds quite an expense. Also since we usually have to protect according to available fault current fuses get a lot more practicle. I don't think NEC prohibits it. Feeders have to be protected where they are powered from unless using the tap rules. Mike M
On Sat, 22 Apr 2006 22:10:41 GMT, Lew Hodgett

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

There was hardly anything in the municipal code that modified in any way the National code.
There was an addition that _any_ new (addition or replacement) panel had to be inspected by the city, and something else equally earth-shaking. :)

Yup. And there is apparently a requirement that _if_ there is a breaker at the 'downstream' End of the feeder, it must be smaller than the one at the 'powered from' end. which meant if I wanted to use a 100A 2-pole in the in-unit panel, I had to have 'something bigger' at the feed end. But, the building was built (1960s) using "Federal" breakers/panels, etc. finding 'standard' replacements is an exercise in futility -- let alone trying to find, say, a 125A one. the other option was to put something 'a little smaller' than 100A in the in-unit panel. It's amazing how scarce 'residential style' breakers are with ratings above 60A, and below 100A. and how _expensive_ something like a 95A breaker of that ilk is.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On Sun, 23 Apr 2006 16:19:53 -0000, snipped-for-privacy@host122.r-bonomi.com (Robert Bonomi) wrote:

Where I am we have NEC, state, and then local rules, not to mention sometimes building code or fire marshalls. Arguing with inspectors is a little like wallowing in the mud with pigs. Eventually you figure out they like it. LOL, and usually they can cite the code section. Mike
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Ah well, I rarely argue with inspectors. Except when they're out-and-out wrong, and I can prove it, that is. At another place, I crossed swords with a City of Chicago electrical inspector -- over the City of Chicago Electrical code. (The Chicago Code is _not_ based on the NEC, in fact it predates it. It is much stricter than the NEC about some things, and more lax about others. It is also written such that it is _very_ difficult to figure out exactly what is, or is -not-, allowed in any given situation. Methinks that this is deliberate, to enhance inspector revenues.)
Anyway, this inspector didn't like the way something had been done. And cited the code section that it was in violation of. And I cited the section that said _his_ section "didn't apply" if conditions X, Y and Z were met, and that =this= installation have conditions X, Y, and Z. He countered with a section that said condition Y had this other requirement under "these" circumstances, and that we did fall under that. Whereupon I pointed out that section thus-and-such said his section applied only when condition W existed, which did not exist here. This went on for a while, but eventually he "went away mad" -- *without* writing a violation, *or* getting a bribe. He was _not_ a happy camper. :)
The next week the fire inspectors came calling. *sigh*