I have a problem with my boiler (Potterton Kingfisher boiler CF40 from
1992)... The hot water in the tank does not seem to warm up very much, even when I increase the thermostat on the boiler to MAX. It fires up for about 1 minute then goes off for 10 minutes. I can hear the boiler thermostat "click" at between 1 and 2 but increasing the thermostat to above the click does not make the boiler fire up as I would expect it to (hot water setting is turned to "constant" on the controller).
However, if I turn the heating to "constant" too, the boiler does fire up and stays on. The radiators get very hot (I increased the thermostat on the boiler to MAX) but the water from the tank is still lukewarm. There is no thermostat in any room for central heating by the way. The thermostat on the boiler then clicks between 4 and MAX.
Is there usually one thermostat for the hot water tank and another for the heating? If so, maybe the thermostat for the hot water tank may be dodgy...?
How many water pipes (not to be confused with the gas feed pipe) are connected to your boiler?
Do you have any motorised valves anywhere (such as in the airing cupboard)? If so, how many, and how many water connections does each have?
Answers to these questions will help to establish whether you have a gravity hot water or fully pumped system. The cause of your problem is different, depending on what type of system you have.
The boiler is in a single floor flat at the same height as the cylinder. There are 2 pipes going to the cylinder and 2 other pipes which I assume to be the central heating circuit.
There looks to be one motorised valve inside the boiler cabinet itself
- placed on one pipe after the output from the pump splits into 2. It's on the central heating pipe.
I investigated the cylinder further and found the thermostat there, set to 60
The hot water tap was a bit spluttery. So I'm thinking now of air lock rather than dodgy thermostat...?
I tried to take some photos but apart from one of the boiler front, showing no pipes, the cupboard was too cramped to get the camera to focus.
I did follow wires from the controller junction box and found that there is actually another motorised valve on the hot water pipe at the back of the boiler. I wouldn't fancy changing that, it is quite inaccessible.
Which aspect of the system sounds odd? - I might be able to clarify.
Is it worth testing the tank thermostat? That's the easiest bit to remove! I don't think that the motorised valve has shut totally because the water in the cylinder does warm up a bit.
It sounded odd when you said that there was only one motorised valve - on the CH circuit. I would expect either two 2-port valves - one on each circuit - (S-Plan) or one 3-port valve at the point where the circuits divide after the pump (Y-Plan).
Now that you have found the second valve, it sounds less odd! It sounds as if you have a fairly conventional S-Plan system. You can see how it is supposed to work by looking at the schematic and wiring diagram for S-Plan in
formatting link
In essence, the HW valve is driven by the programmer and tank stat. The CH valve is driven by the programmer and room stat. Both valves have a set of auxilliary contacts which close when the valve opens. These contacts are used to switch on the boiler and pump.
If your hot water isn't getting hot enough, it could be due to:
programmer not turning it on for long enough
faulty cylinder stat (or incorrect setting) closing the valve too early
I'm using the programmer on Constant setting for testing. I did open up the wiring centre junction box and tested some terminals with neon screwdriver. There seemed to be a voltage to the HW ON terminal regardless of the setting (Const/OFF) of the hot water on the controller, which seemed a bit odd to me. The CH ON terminal switched as I would have expected, when CH was moved between Const and Off on the controller.
Tested the cylinder stat and it is working fine, so I've ruled that out.
Tried activating the manual lever on the HW valve when HW had been on for its 2 minutes and then switched itself off. The boiler and pump came on for 1 second and then off again, even when I locked the lever in manual position.
Is the auxiliiary switch a feedback from the valve to the controller to turn on the pump and boiler? Would moving the lever to manual trigger that switch?
I was thinking of swapping the heads on the 2 valves since the CH is behaving fine and the HW is not. The HW valve has 6 connections but the CH one has 5 (no white).
Does it sound like the valve is at fault? Is there any voltage test I could do on the terminals that would help diagnose the problem?
Can I repeat the plea made in other threads - when replying to someone's message, PLEASE, PLEASE quote at least some of it so that people can see the context. I had to pull up the whole thread to remind myself what had already been said. A lot of people - quite understandably - wouldn't bother, so you wouldn't get a reply.
As has been said many times before, a neon screwdriver is just about the
*least* reliable way of testing for 'liveness' - and can often give misleading results. [Just copping hold of the wire is more accurate! ] Seriously, though, you need a 250v AC voltmeter referenced to neutral to determine what is truly live - and preferably a lowish impedance analog one at that.
How did you test it?
Not if it's a conventional S-Plan system. Did you look at the schematic and circuit diagram which I referenced earlier? Did you understand it? If you did, you will realise that the auxilliary switches are provided with a permanent live - so that when they switch, they turn the boiler and pump on regardless of what the programmer and stats are doing. [This can sometimes lead to a different sort of fault where a valve sticks open, and the system runs even when everything is turned off!]
I would expect it to, but am not 100% sure.
Again, if it's conventional S-Plan, the white wire is not needed - and won't be doing anything on the valve which has it - so you should be able to swap heads.
Well, it could be interesting to swap heads, and see whether the HW then works ok but the CH doesn't. My hunch is that it won't make any difference.
Looking at your initial post, I suspect that there is *some* flow from the boiler to the coil in the hot water cylinder, but not very much - which might explain why the boiler only fires for a small percentage of the time when trying to heat the HW. Are you *sure* that when the boiler stops, the pump also stops? My hunch is that the boiler's own thermostat is turning that off, but the pump is still running. Are the pipes which go the HW cylinder hot under these circumstances? Is there a manual balancing valve in the HW circuit which may be almost closed, preventing the necessary amount of flow? Is there a bi-pass valve which could be stuck open, short-circuiting the HW coil?
Finally, is it a vented system, or a sealed (pressurised) one?
Summary so far: Honeywell S-Plan system. The problem started on its own, not following any modifications or maintenance to the system. CH works fine. When HW switched on alone without CH, boiler ignites and pumps for a couple of mins only before turning off. It sometimes comes back on after about 10 mins but only for 1 minute.
Switching on the CH and HW together and moving the HW motor valve to Manual sometimes gets a full tank of water. But, sometimes when I try this, the lever on the HW valve moves back to about half way across and the valve is shut.
When HW only is on and the boiler is not doing anything, the pump is not running. Tested with multimeter that the brown wire to the HW valve is 240V with respect to neutral. The orange from the microswitch is not live at this point. Moving the lever to manual makes the boiler and pump active but literally for 1 second, before dying.
Tested tank thermostat with multimeter. It switched fine between terminals 1 and 2. Tank thermostat is set to 60 degrees, the boiler stat is set to MAX. Can't see a manual balancing valve. The pipe on the cylinder side of the motor valve is not hot when the HW is not working. It's a flat so I can't be sure where all the vertical pipes are actually going. Apart from the coil in and out, there are only 2 pipes to/from the cylinder fill at bottom and outgoing out from the top of the cylinder - does that alone mean a sealed system?
We've been away from the house but the wife is now getting fed up with using the immersion heater so I need to do something! :-)
One more plea! You've mastered quoting what you're replying to - but will you now please put your response *below* the previous message, *not* above it!
I suspect that the problem is down to the actuator on the HW valve. It sounds as if the valve isn't opening properly under its own steam, and that the manual lever doesn't open the valve far enough to operate the microswitch reliably.
Have you tried swapping the heads? If you do that, and the HW then works but the CH doesn't, it points fairly conclusively at the actuator.
If you don't want to do that, try this instead. Remove the HW actuator from the valve. Turn the valve spindle manually to the open position. Check that the spindle can be turned fairly easily. [If it is very stiff, the problem may be that the 'wet' part of the valve is partially seized, and the actuator is stalling before it's fully open]. At the point where the HW actuator connects to the wiring centre, temporarily bridge the orange and grey wires. If the boiler and pump then run properly and heat the hot water, it proves that:
the water circuit is not blocked or airlocked
the boiler is ok when powered properly - so there must be a problem with the actuator [Don't leave it bridged while unattended, otherwise the HW may get *too* hot].
Don't worry at this stage about whether it's a sealed or vented system. If what I've suggested doesn't work, we may need to re-visit that in order to investigate airlocks or low water level - but that's probably not necessary.