voltage drop in circuit

I run a standard duty washing machine on a 15 amp circuit. The circuit also has basement lights on it and measures approx. 119 volts with the washer off. This is in line with the other home circuits at 119-120 volts. With the the washer running, certain cycles will cause a slight flicker in the lights and a drop in circuit voltage to 116.5 volts. Other circuits are unaffected.

I'm guessing the washer pulls 4-5 amps and it seems like this shouldn't strain the circuit. Is the small voltage drop normal? Also, would electronics possibly be damaged by the slightly lower voltage if they were on this circuit?

Thanks in advance........

Reply to
JC
Loading thread data ...

Check all the places on the circuit where the line is cut. Like outlets etc. Make sure the contacts are solid.

If you find any aluminum wire.. BINGO. Have a professional check out all the wiring in your home.

It may just be normal for the washer.

Reply to
Joseph Meehan

All the neutrals in your main tight?

Reply to
CBhvac

First off, you should have a 20A circuit for your washer. My washer pulls 11.1Amps (according to the nameplate). And it was made in October or November 2003. It's probably OK to put both the washer and dryer (if it's a gas dryer) on the same 20A circuit, but not recommended. Also not recommended is the putting the lights on the same circuit as the washer. Lighting curcuits should always be separate from non lighting so when you trip a breaker your lights don't go out also.

Now as to your specific problem, you are most likelly getting voltage drop either because of a bad connection or maybe because you are taxing the circuit to it's limit.

Reply to
Childfree Scott

Do the lights flicker the whole time, or do they flicker when the motor comes on, and then stabilize? If its the whole time, you have a problem; if just when the motor comes on, probably not. (I am making an assumption you have florescent lights; incandescent should never flicker, though they might dim.)

You are seeing a voltage drop of 2.5v with the washer on. That is little more than 2% and nothing to worry about. If you actually have 5a and it is a 14 gauge cable, it means you have a 90' circuit. That is a bit on the long side, and you should avoid putting anything really heavy on it; but 5a is fine.

Reply to
Toller

Has anyone looked at the length of run on the wire and wire diameter. for

14 AWG wire. you're looking at .25 ohms / 100 feet. Consider the loop length (from the breaker box to the washer and back) is 100 feet (easy in a house) then the voltage drop will be 10 amps (assumed) * .25 ohms = 2.5 volts. That drop will get you a ~116 volts readout at the washer (or near). Also consider that splices in junction boxes are not zero ohm and can add to the voltage drop.

I would say this is normal. Any decent electronics should be able the handle this. I would put a surge suppressor just to be safe though since you have a motor (source of noise and spikes) on the same line.

Reply to
mook johnson

HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.