Number of wires in conduit

Installing dishwasher. New install. Need to run electic-separate 15amp circuit. Would like to feed wires through nearby conduit run. How many conductors and neutrals can run in a 1/2 or 3/8 conduit ?

Reply to
Teo2006
Loading thread data ...

The limit is on the total number of wires. The capacity of those wires may need to be derated if there are more than three current carrying conductors in the conduit. Conductors that are functioning as actual neutral conductors are not counted for that purpose but grounded current carrying conductors other than true neutrals are. To answer your question about the total number of wires permitted in the conduit I would need to know the actual type and nominal size of conduit or at least it's actual internal diameter. Conduits carrying three or more wires may only be filled to 40% of their cross sectional area.

Reply to
Member, Takoma Park Volunteer

Short answer 9 #12 THHN

Reply to
gfretwell

I created a Conduit Calculator application that is available for free at

formatting link

Reply to
Calvin Henry-Cotnam

I think its safe to say you can install (3) #12 thhn wires in a 1/2 conduit. 40% fill. Assuming your dishwasher is 120v ac

Reply to
Tazz