House Wiring NM Wire Gage For 30 Amp Breaker Quest. ?

Hello:

For the standard Copper NM interior house wiring:

Am I correct than for (any) circuit breaker labeled 30 amps, the minimum gage of wire going to it should be # 10 AWG ?

Thanks, B.

Reply to
Robert11
Loading thread data ...

You are indeed (correct).

[Now let's see who will trot out Art. 240-3 exceptions...]

Jim

Reply to
Speedy Jim

Per 2002NEC 240.4(d), YES. 10# for non 240.4(e-g) applications, 10 AWG can be used on 30 amp circuits.

Now just summerizing what the NEC says, so read for yourself if you are serious about learning more.

hth,

tom

Reply to
The Real Tom

Oops, forgot to say copper. If you have alumium, then t310.16 says

8#.

hth,

tom

Reply to
The Real Tom

This is Turtle.

Yes as to looking at any wire guage chart but you could possibly find a no if you researched hard enough of the NEC code to find a flaw in your application. So Yes if you don't like to arguee.

TURTLE

Reply to
TURTLE

HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.