Disadvantages of two furnaces in series?

and a motorized bypass damper. In the series configuration the heat generated by the wood stove after it's door damper has closed won't present a problem, and there would be

no short cycling unless perhaps your backup resistance heat were also engaged.

Do you still mean to use the blower in the electric furnace, which is upstream from the wood? The motorized bypass damper that you mentioned

- what is that bypassing? Sorry I'm confused about this point. Do you have a telephone number and 10 free minutes? :)

-Dean

Reply to
dean
Loading thread data ...

The bypass is just a duct that runs parallel to the wood furnace. The main air stream is split as it leaves the fan coil, some of that air is fed through the wood furnace and the rest is fed through a duct that skirts around (bypasses) the wood furnace. These air streams are tied back together on the other side of the wood furnace. It's actually a series-parallel configuration. Yes, we're still talking about removing the blower from the wood furnace.

Just think about a stream that splits in two and then rejoins downstream. Now put your wood heater in one branch of that stream and your evaporator coil in the other, with your air handler located upstream of this split.

Richard Perry

Reply to
RP

Ok, but that doesn't help push air through the wood furnace. In fact it would reduce the air going through the wood furnace, some of it would bypass the wood furnace (we are relying on the electric furnace's blower). I think its quite important to have maximum air flow around the firebox.

Reply to
dean

According to your description the air handler has a bigger blower motor than the wood furnace has. I would think that the air handler blower should be capable of pushing sufficient air through the wood furnace. In fact, some of it would have to be bypassed around the wood furnace in order to prevent too much airflow through the wood furnace. At the same time this bypassing of air will reduce the static pressure in the plenum, allowing the blower to run more efficiently, and it will reduce noise at the return as well. The purpose of the bypass damper is to control the volume of air through the wood furnace or alternately through the evap coil, as necessary. The damper will allow air to bypass the wood furnace when the heat pump is energized, and will allow air to bypass the heat pump evaporator coil when the wood furnace is heating. You won't have a call for both units simultaneously. An interlock circuit will prevent both from calling at the same time.

When the fire dies down in the wood stove and it is no longer supplying sufficient heat to the space, and when you aren't there to add more wood or perhaps don't want to add more wood, then the heat pump stat will energize the compressor, modulate the bypass damper open to the evap coil, and at the same time the door damper will be closed on the wood furnace. A small portion of the airflow will still be allowed to flow through the wood furnace, just enough to prevent it from overheating and from rising enough to lock out the heat pump again. I forgot to mention that you'd have a temperature controller on the wood furnace that would lock out the heat pump at a given temp. It is the drop in temp of the wood furnace that would cause this same control to allow the heat pump to take over. Now where was I?

Once the fire is completely out the damper modulates full open to the evap coil, allowing full required airflow through it. There are several other ways to control airflow beside this one. One is to have a second damper, another is to place the coil downstream and have a normal series installation. The bypass system is definitely more complicated than the normal series installation, but it would provide an ability to supply the correct airflow to both the coil and to the wood furnace as necessary. Normally the wood furnace doesn't offer enough restriction to pose a problem. The only reason that I suggested the bypass in your case is that you had some reservations about getting all the air through the wood furnace without it producing an excessive restriction to airflow. Normally this isn't a problem, and the series installation is rather straightforward. If you want a less complicated system, then I suggest you either forget about it, or make that hole bigger. :)

Richard Perry

Reply to
RP

Right:) I am convinced. Once again - thank you!

So, in the normal series installation (assuming 1HP is enough), would I still need a lock-out to stop the heat pump running when the wood furnace is hot? I've read sometimes that you have 2 thermostats, and set the electric 5 degrees below the wood. However, I assume that someone can fiddle with these, so I either get the interlock, or a dedicated single thermostat designed for this type of system.

What would happen if the heat pump came on and fed warm air into the wood furnace jacket? Would it not just turn down the door damper because it doesn't need so much fuel? Would this be a hazardous situation?

-Dean

Reply to
dean

The heat pump air won't harm a thing, it's in the summer when you're running the AC that you don't want the evaporator upstream. The wood furnace would quickly rust out. HTH.

Richard Perry

Reply to
RP

I was telling someone about this idea, That I would love to do something like this in my next house I have custom built. I was ask why not have a wood fuel boiler that used water circulated to a coil as a second unit on the heat pump, then would just need to have the circulator pump shut off when temp was not high enough and the heat pump take over.

Is this doable?

I think back to coal fueled boilers supplying steam to radiators, Just the radiator would be in line with the heat pump.