I'm installing AFCI breakers but have one that trips immediately. After investigating I have found one GFCI outlet that is responsible. However when I check the outlet with a GFCI tester, it is correctly wired. Tesing the GFCI trips the AFCI.

Is it still possible to have a common neutral or other fault that trips the AFCI, while being correctly wired for the GFCI?

Many thanks

Reply to
scbody
Loading thread data ...

It's possible that you have a bad receptacle.

Reply to
Bob

Can you determine if there's shared wiring anywhere? If it's only the one GFCI try changing it out for a new one and see if the problem persists. Is the AFCI in the breaker box? If so inspect the wiring in the box to make sure it's done correctly. Especially as regards both circuits. If you aren't confident in the box hire a pro. Richard

Reply to
spudnuty

An AFCI combines parallel arc detection with ground fault protection of equipment for protection against series arcs which often devolve into arcing ground faults that will generate enough heat to kindle a fire. The presently available AFCIs are not suitable for use on multiwire branch circuits so if the circuit you are trying to protect is run in three wire plus ground wiring method the AFCI will trip because the load on the neutral will be different from the load on the ungrounded conductor by more than the thirty milliampere threshold of the AFCI's circuit. The AFCI will trip on a ground fault of 30 milliamperes or more. The AFCI injects a detection current into the neutral to detect ground faults. If it is tripping as soon as you close it there is a short circuit or a ground fault on the wiring it supplies. Disconnect both the neutral and the ungrounded current carrying conductor from the GFCI breaker. If the neutral for that circuit is not connected to the breaker you have found your problem. Both current carrying conductors of the circuit must be connected through the AFCI breaker. Test those two conductors to ground with a continuity tester or a ohm meter. There should be no connection between those two conductors and ground once they are disconnected from the AFCI breaker. If you measure the presence of a connection to ground you must find the fault and clear it.

Reply to
Thomas D. Horne, FF EMT

GFCIs do that and will detect a neutral-ground connection downstream with no load being drawn (and can't be set with that condition). My understanding is that AFCIs don't and require an applied load to detect downstream neutral-ground connections.

bud--

Reply to
Bud--

Bud Do you have a source for a defintive answer on that? I would really like to know.

Reply to
Tom Horne, Electrician

I was afraid you were going to ask that - I probably would have asked the same thing. I need to include source info in the notes I keep.

The answer was originally based on an article from Mike Holt

formatting link
s~20030301.htm

In the section "Does a GFCI circuit breaker offer equal or greater performance ...." Holt says UL943 devices include current injeciton and will detect G-N connections with no load but that UL1053 devices only detect G-N connecitons with a load applied. I took this to be a distinction between GFCIs and AFCIs but that apparently isn't what Holt said.

Holt talks about UL489/943/1699 and UL489/1053/1699 devices. UL943 is for GFCIs. UL1053 is for "Ground-Fault Sensing and Relaying Equipment". AFCIs are under UL standard 1699. The statement of scope of 1699 at the UL web site is the sandard doesn't include GFI functions and they are covered by other UL standards, presumably 943 or 1053. (UL489 is for molded case circuit breakers.)

A very interesting technical paper on AFCIs is from the Comsumer Product Safety Commission (AFCIs resulted from work initiated by the CPSC).

formatting link
paper insludes info on why circuit breakers don't reliably detect arcs and on what AFCIs shouldn't detect.

From page 15 describing the possible addition of GFCI protection to an AFCI (that is 6 ma trip instead of 30 ma trip) "also the grounded neutral protection is required per UL 943". I would take that to indicate that AFCIs don't include current injection and it has to be added. From the combination of articles I think what I said is right. It would be easy to test.

--------------------------- Relating to another thread I ran across a paper on grounding with coupled rods I thought was interesting:

formatting link
bud-

Reply to
Bud--

Gentlemen

Thank you for your responses. I think I understand most of what you are saying ... maybe !! I'll swap out the GFCI and see if that fixes it. Failing that I'll do my best to look for a common neutral, but that may be difficult because the wiring is not accessible. If I have no luck with that I'll replace the AFCI with a regular circuit breaker. Did I get it right?

All my best and thank you

Reply to
scbody

formatting link

Bud Thanks. I learned something new.