This is something I've wondered about:
Is it practical to wire a ring circuit by taking a single cable from the CU a short distance to a junction box, then starting the ring (in both directions) from there?
Thanks.
This is something I've wondered about:
Is it practical to wire a ring circuit by taking a single cable from the CU a short distance to a junction box, then starting the ring (in both directions) from there?
Thanks.
If you used 4mm cable to run to the split point, it should be OK.
I wondered if that might be the case. It's not something I'm planning to do necessarily, just an approach I've wondered about. Thanks for the reply.
Bert
Its not a standard circuit, but in theory is doable. Its similar to taking a submain to a remote point and then wiring circuits from there.
I thought it might be: if you regard the single cable to the junction box as simply an extension to the output terminals on the CU, then the theory seems perfectly sound. Thanks.
Bert
I would have thought Ok as long as the junction box is inspectable, it's effectively a sub-CU that's fused at the supply end.
And, of course, has terminals big enough for 4+2.5+2.5 cable. That may be your biggest problem.
JGH
That's what I've done here:
Closed up:
It's one that I have done. I used the old 10mm shower cable for a loft conversion.
No idea what the regulations say but as long as the cable to the start of the ring is adequately sized to carry the total current in both arms of the ring I don?t see why not. Two of the rings in our house have earths wired like that (phase and neutral are rings from their respective MCBs but both earth rings are terminated in one terminal block from which a single earth cable runs back to the CU). This setup was recently tested and certified as part P compliant and passed all the earth impedance and disconnect tests.
Here's another point. Rings don't suit high loading near one end. I put two rings in a kitchen which was a long way from the CU. In this case, I ran each end back separately to the CU in a conventional circuit arrangement. This means the load is all near the centre of the ring because there are no wiring accessories connected near the ends of the ring, which is ideal for balanced ring loading.
That's not a generic problem with rings, its the half baked ones where the cable is too small if all/most of the current goes one way which it can if the path is a significantly higher resistance (e.g. length) one way.
Anyway if 4 mm T&E cable is used to the split then the earth may be too small as the earth wire in 4 mm T&E cable isn't very big. It would be much larger if it were 3 core SWA using one of the cores for instance.
Many thanks to everyone who responded. Much appreciated.
Bert
HomeOwnersHub website is not affiliated with any of the manufacturers or service providers discussed here. All logos and trade names are the property of their respective owners.