Hopefully this is the last set of questions!
1) My current installation is PME with the following differences from the diagram in the OSG:All the conductors (supply and main equipotential) are 6mm2 (diameter is
4.4mm so it's either 6mm with .8mm insulation, or 10mm with .4mm - 6mm sounds more likely!)As far as I can tell, the gas pipe is not directly bonded to the main earthing terminal. The water pipe is, and then there is a second wire running away from the water pipe, which I believe connects to the gas pipe.
There is no separate main earthing terminal - it's more of an integrated one. The CU earth connects to a terminal at the side of the supply fuse, as does the water bond. I don't see any more terminals for adding a third (gas) bond there.
meter tails are 16mm2 (as are the fuse-meter conductors)
When I put the new CU in, I will provide 25mm tails and a 16mm CU earth for the supplier to reconnect (I assume I'm not allowed to touch anything on their board so they will want to do this bit). Is there any chance that they will refuse to reconnect me because my main bonding conductors aren't up to scratch? As I understand it 6mm2 is OK, just doesn't comply - there's even an example PIR in Appendix 7 illustrating this precise case - TN-C-S with 6mm earth. However, I don't (yet) understand why TN systems require a higher main bonding csa than TT, and things I don't understand bother me!
2) Is there anyway of testing the continuity of the main bonding without using a long test lead? There is no neutral to use on a gas pipe.... Would it be acceptable to temporarily run a second lead, calibrate its resistance and deduce R2?Thanks!