I can't find any data on Danfoss's site (as an example).

As a general rule, is the microswitch in a zone vale suitable for switching a pump directly, or is a relay advised?

Ta - Tim

PS - can anyone recommend a simple UFH mixer/pump unit for 2 UFH circuits? Dumb as possible (no wiring centre) as I'll be controlling it from an external system.

Reply to
Tim Watts
Loading thread data ...

Absolutely normal practice to switch pump and gas valve directly. I think they are rated at 10A

Reply to
Graham.

They're good for several amps - AC (less for DC). They can easily switch a pump and boiler demand without additional relays.

Bear in mind that the entire CH system is usually protected by a 3A fuse, so nothing takes all that much current.

Reply to
Roger Mills

Thanks Roger, and yes I know about the 3A. However, pumps do have a significant of a switch on surge (well, used to - not sure if any of the electronic ones are softer?) - some 6-10 x nominal for an induction motor, albeit only for a few cycles.

That's what I was worried about. I have one Z-Wave switch that explicitly says "do not control a pump directly" as its relay is reckoned to suffer.

Reply to
Tim Watts

formatting link

???

Yup.

switched live via timer to Thermostat(s) to zone valve(s) to neutral

Wire OR those to a relay and the UFH pump/reducer

Switched live to relay SC, NO terminal to boiler (pump) in parallel with normal CH motorised valve output. Boiler pump to neutral

Important to have relay to make UFH independent of CH

Reply to
The Natural Philosopher

I don't think there are any relays in my S-Plan system; just a chock-block connector. So I guess the thermostats and valve switches must be switching the pump directly.

Reply to
Caecilius

You need a relay when you have a separate pump for UFH.

Otherwise the standard CH will always make the UFH come on

Reply to
The Natural Philosopher

Understood - relays for logic. I'll be doing that. I'm merely wondering if I can save relays by assuming UFH actuators and zone valves have switches that don't mind inductive loads.

My plan is to take the controls to the boiler, UFH pump, and 2 actuators from a gridswitch bank - each circuit runs through 2 switches:

Switch 1: Off vs "On demand"

Switch 2: "Auto" vs "Manual On"

Good for clearing the air, testing and if the automatics go wrong.

The input to the "auto" switch input would come from relays driven by programmers (the programmers would be an integrated Z Wave solution).

At least, when it goes wrong, I'll be able to force various part sof the system on, or off.

Reply to
Tim Watts

Depends how it's wired. My roomstat switches on my UFH pump in parallel with the motor of its zone valve - and the zone valve's auxiliary contacts switch on the boiler and main pump - just like those for the other zones. I don't have any relays.

Reply to
Roger Mills

Snap.

Actually I do have relays for the rest of the house, but that is only because I wanted to run all those thermostats on 12Vac, as I have timer/stats and motorised valves for each room and (at least until each room was due for redecorating) I wanted to run stats off alarm cable surface run up the edge of door frames for neatness.

A useful side-effect was that I could have a timer/stat in the bathroom due to the 12Vac and isolating transformer.

SteveW

Reply to
Steve Walker

Blimey. You run a pump off the stat contacts?

Reply to
The Natural Philosopher

OK - that was my initial thoughts, hence the question...

Right, I think, given the lack of data on some of the microswitches, probably best to shove relays in everywhere. Just got to browse the Omron section in RS and find a nice beefy DIN mount one, but not silly beefy :)

Reply to
Tim Watts

Room stats will easily switch domestic pumps. Modern programmable stats use a relay anyway so why bother with making the system less reliable by using more?

Reply to
dennis

my boiler control (internal) operates the pump. This allows the pump to continue running for a short period after the demand has ceased. This allows the heat to be taken away from the boiler thus preventing the overheat thermostat from closing down then boiler. My bolier is nearly 30 years old, so it's not a new idea. Someone had to add a similar facilty to our village hall boiler as long ago as the 1970s.

Reply to
charles

I was asking about the microswitches in zone valves (and later UFH actuators).

Also, the Horstmann Z-Wave boiler relay explicitly will not switch a pump directly.

I need relays anyway to mix several signals down (2 UFH actuators, OR'ed to the blender pump, then that OR'ed with the main radiator demand relay to signal the boiler. So a couple more won't matter.

Reply to
Tim Watts
8<

I can't see where it says that in the manual.

It must work with motors as zone valves are motors.

Reply to
dennis

Why not? That was how a tradition gravity HW, pumped CH system worked.

Reply to
Roger Mills

It was in the Heatgenius literature (they use that part in their system).